Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: 600 amp service entrance design to be submitted to POCO, looking for input.

User: Tyler55, Location: Glenwood, NM

Asked on: Friday, September 6, 2024 at 7:27 pm EDT
Answered on: Thursday, March 6, 2025 at 2:08 am EST

Question: Hello everyone,Happy Friday. I have designed a service entrance for my shop using off the shelf equipment that is affordable and available for purchase. On Monday I will submit the drawing along with the cutout sheets for the various equipment that I am proposing to use. I am still unsure if my POCO uses bar type CT's... I'll find out on Monday when I speak to the Meter Supervisor at the POCO.Anyway, does this design look any good? Does it look fairly doable from an electricians point of view?It will likely need some modifications from the engineers as far as conduit size, the purpose here is to get the equipment approved by the POCO so it can be ordered.Any input is appreciated.Thanks to everyone who has helped me to get this far,

Okay, I understand you're looking for feedback on your proposed service entrance design for your shop, keeping in mind practicality, cost, and POCO approval. Since I can't see your drawing and cut sheets, I'll provide a general checklist and some points to consider. This will help you anticipate questions and potentially improve your design before you submit it.

General Considerations (Things You Should Definitely Include in Your Submission)



One-Line Diagram

A clear, single-line diagram is absolutely essential. It should show:


POCO Connection Point

Where does your service connect to the utility's system? Is it underground or overhead? Specify the voltage and phase configuration (e.g., 120/240V single-phase, 208Y/120V three-phase, 480Y/277V three-phase).

Metering

Location of CTs (if required), meter socket, and meter itself.


Service Entrance Conductors (SEC)

Size, type, and number of conductors. Specify the material (copper or aluminum). Include grounding and neutral conductor information.

Service Disconnect

Type (e.g., fused disconnect, circuit breaker), amperage rating, and interrupting rating (AIC). Location is also important.


Grounding Electrode System

Details about your grounding electrodes (ground rods, water pipe connection, ground ring, concrete encased electrode). Show the grounding electrode conductor (GEC) size and connection points. Indicate if supplemental electrodes are required.

Main Distribution Panel (MDP)

Ampere rating, voltage, number of spaces, and AIC rating. Show the connection from the service disconnect to the MDP.


Any Subpanels

If you have subpanels, show their location, ampere rating, and the feeder size and type from the MDP.

Equipment Grounding Conductor (EGC)

Indicate how equipment grounding is handled throughout the system.


Cut Sheets (Spec Sheets)

Include manufacturer's cut sheets for every piece of equipment you're proposing: Meter Socket CTs (if applicable) Service Disconnect Main Distribution Panel (MDP) Any Subpanels Any Surge Protective Devices (SPDs) Conduit bodies (LB's, pull boxes, etc.)

Calculations

Show your calculations for:

Service Entrance Conductor Size

Based on the anticipated load. This is critical. Use Article 220 of the NEC.


Grounding Electrode Conductor (GEC) Size

Based on the size of the service entrance conductors (Table 250.66 in the NEC).

Equipment Grounding Conductor (EGC) Size

Based on the size of the overcurrent protective device (Table 250.122 in the NEC).


Voltage Drop

Calculate voltage drop to critical loads, especially if you have long runs.

Short-Circuit Current Availability

Estimate the available fault current at the service entrance. This is important to ensure your equipment has a sufficient interrupting rating (AIC).


Physical Layout

A drawing showing the physical location of the equipment within your shop is helpful.

Conduit and Wiring Methods

Specify the type of conduit you plan to use (e.g., EMT, rigid, PVC) and the wiring method (e.g., THHN/THWN, XHHW).


NEC Code References

Cite the relevant NEC (National Electrical Code) sections that support your design choices. This shows that you've done your homework.

Specific Questions to Consider and Answer (For Yourself and the POCO)



Load Calculation

Have you accurately calculated the total load for your shop? Consider all equipment, lighting, receptacles, and future expansion. Be realistic! Undersizing the service is a common and costly mistake. Are you accounting for demand factors where applicable?


POCO Requirements

What are the specific requirements of your POCO? They often have their own rules that go beyond the NEC. Find out about: Acceptable Meter Sockets CT Requirements (if applicable) Clearance Requirements around the Meter and Service Disconnect Grounding Requirements (they may have specific grounding electrode requirements) Disconnect Requirements (location, type, etc.) Overcurrent Protection Requirements Inspection Procedures

Interrupting Rating (AIC)

Have you determined the available fault current at your service entrance? The service disconnect and distribution panel must have an interrupting rating (AIC) equal to or greater than the available fault current. This is a critical safety issue.

Accessibility

Is the service disconnect readily accessible? Can the meter be easily read and accessed by the utility?


Working Space

Is there sufficient working space around the electrical equipment as required by the NEC? (See Article 110)

Future Expansion

Have you considered future expansion? It's often wise to oversize the service slightly to accommodate future needs.


Coordination

Does your proposed equipment work well together? For example, does the meter socket properly accommodate the CTs (if required)?

Grounding

Is your grounding system properly designed and installed? This is crucial for safety.


Surge Protection

Are you including surge protection? It's highly recommended to protect sensitive electronic equipment.

Arc Flash

While this might be more in-depth than required for POCO approval, consider the arc flash hazard associated with your equipment. Higher voltage and current levels increase the risk.


Local Codes and Permits

Make sure you are aware of all local codes and permit requirements.

Electrician's Perspective - Things That Make a Design "Doable"



Clear and Complete Documentation

The easier it is for the electrician to understand the design, the smoother the installation will go.


Standard and Readily Available Materials

Using common materials reduces costs and makes the project easier to complete.

Adequate Working Space

Sufficient space to work safely and efficiently is essential.


Logical Layout

A well-organized layout makes the installation and future maintenance easier.

Good Grounding

A properly designed and installed grounding system is crucial for safety.


Accessibility for Maintenance

Consider how the equipment will be accessed for future maintenance and repairs.

Before Submitting



Double-Check Everything

Review your drawings, calculations, and cut sheets carefully for errors.


Consider a Consultation

If you're unsure about any aspect of your design, consider consulting with a licensed electrical engineer or a qualified electrician.

Talk to the POCO

As you mentioned, talking to the Meter Supervisor at the POCO is crucial. Get their feedback
before* you submit the final design.

Good luck!
Providing as much detail as possible upfront will save you time and headaches in the long run. Be prepared to answer questions and make revisions as needed. Remember, the POCO's primary concern is safety and reliability of their system. Flag for review

Previous Question Next Question