User: mehdi1351, Location: New Zealand
Asked on: Friday, September 6, 2024 at 7:32 pm EDT
Answered on: Thursday, March 6, 2025 at 2:09 am EST
Question: Hello all,I am currently dealing with Texas POCO (Swepco) to order 2 transformers. What they asked me was only limited to the load list and last week they already ordered the transformers. I am a bit concern on why the transformers got ordered without and sizing/adequacy check criteria checked by myself (as a user of the device).Is that quite normal in US?As far as I know, there are 2 adequacy check on the transformers that should be part of the transformer sizing documentation, but seems like the POCO got all the responsibilities in this area, rather than sending the design/calculation document to me for review/approval prior to order the transformers?Any thoughts?
Your concern is understandable. It's unusual, but not entirely unheard of, for a utility (POCO) to order transformers solely based on a load list without further design review from the end user. Here's a breakdown of the situation and things to consider
Why This Might Happen:
Simplified/Standardized Service
If you're a relatively small customer with a fairly standard load profile, SWEPCO might have pre-engineered solutions and transformer sizes that they regularly deploy. They might feel the load list is sufficient to fall within these established parameters.
Efficiency for the POCO
Ordering transformers in bulk based on common needs streamlines their procurement and deployment processes.
Trust in Load List
SWEPCO might be relying heavily on the accuracy of the load list you provided. They assume it accurately reflects your peak demand and future expansion plans.
Ownership and Responsibility
In some cases, the utility owns and maintains the transformer, so they take full responsibility for its sizing.
Why Your Concern is Valid (Adequacy Checks)
As you correctly pointed out, two critical adequacy checks should ideally be performed:1.
Load Capacity Adequacy
Ensuring the transformer can handle your calculated peak load (including future growth). This involves calculating your total kVA demand, accounting for diversity factors (the likelihood of all equipment running at full load simultaneously), and adding some safety margin.2.
Short-Circuit Withstand Capability
Confirming the transformer can withstand the available fault current (short-circuit current) at its location. If the available fault current exceeds the transformer's withstand rating, it could be damaged or even explode during a fault.
Possible Explanations and Next Steps
Ask for Clarification
The most important step is to contact your SWEPCO representative immediately. Explain your concerns and specifically ask: "What transformer sizes did you order?" "Can I see the design calculations used to determine those sizes?" "How was the available fault current taken into consideration?" "What is the short-circuit withstand rating of the transformers ordered?" "What is the estimated life of the transformer at the max load I provided?" "What is the estimated inrush current of the transformer that you have ordered?"2.
Review Your Load List
Double-check the load list you provided to ensure it's accurate and includes: All expected equipment and their ratings (kVA or kW, voltage, phase). Any future expansion plans. Diversity factors that you applied (if any) and the reasoning behind them. Consider also including the inrush current from any equipment that require high inrush.3.
Independent Calculation (Optional)
Consider running your own load calculations independently (or hiring a consulting engineer) to compare your results with SWEPCO's assumed load.4.
Short-Circuit Study (If Necessary)
If you're concerned about fault current, or if the transformer is serving a critical load, you may need to commission a short-circuit study. This will determine the available fault current at the transformer location. SWEPCO likely has this information as well.5.
Written Documentation
Make sure you have written documentation from SWEPCO about the transformer specifications, sizing calculations (or at least the assumptions they used), and fault current considerations.
Typical US Practices
Utilities have varying levels of involvement
Some utilities provide detailed design reviews and collaborate closely with the customer. Others take a more hands-off approach, relying on the customer's load list.
Customer Responsibility
Generally, the customer is responsible for providing accurate load information.*
Shared Responsibility (Ideal)
The best practice is a shared responsibility where the customer provides the load list and the utility performs the sizing calculations, then shares the results with the customer for review and approval.
Key Takeaway:
Don't assume everything is fine. Be proactive in getting the information you need from SWEPCO to ensure the transformers are properly sized and safe for your application. Document all your communication with SWEPCO in writing. If you still have concerns after talking to them, consider seeking advice from a qualified electrical engineer. Flag for review