Topic: Non tray rated cables in Cable tray

User: Isaiah, Location: Baton Rouge

Asked on: Saturday, September 7, 2024 at 10:53 am EDT
Answered on: Thursday, March 6, 2025 at 2:09 am EST

Question: Construction installed many thousands of feet of multi conductor cable in cable tray that is not CT Tray Rated. They’re telling me it doesn’t matter since the tray is installed indoors and not exposed to UV rays

You're right to question this. Here's a breakdown of why it matters, even indoors, and how to approach the situation

Why CT Rating Matters, Even Indoors
Code Compliance

The National Electrical Code (NEC) typically requires cable used in cable tray to be specifically identified for the purpose. That usually means having a "CT" or "tray cable" rating. Even without direct sunlight, the requirements in the NEC are still applicable indoors.


Mechanical Protection

CT-rated cables are designed to withstand the rigors of installation, flexing, and potential abrasion within a cable tray. The trays themselves can be sharp. Standard cables may have thinner jackets or less robust construction, making them more vulnerable to damage.

Fire Propagation

CT-rated cables are designed to limit the spread of fire within the cable tray. They typically have a higher degree of flame resistance. This is critical in a tray system, which can act like a chimney if a fire starts.


Weight and Support

CT-rated cables are often built to handle the cumulative weight of many cables bundled together in a tray and supported over long spans. Non-CT-rated cables might sag or have insulation damage over time.

Chemical Resistance

Cable trays may be in industrial environments with chemicals or cleaning agents that could degrade standard cable jackets. CT-rated cables often have better chemical resistance.

The UV Argument (and Why It's Usually Irrelevant Here)


While the installer is correct that UV resistance is a
factor in some cable ratings, it's not the only reason for using CT-rated cable. The UV argument is a red herring in this scenario, and does not negate the required performance of the cable.

What To Do1. Consult the NEC

Review Articles 318 and 392 of the NEC (National Electrical Code) regarding cable trays and cable installation requirements. Verify the specific requirements based on your local jurisdiction's adoption of the code.2.

Review the Cable Specifications

Document the cables: Get the exact manufacturer and part number of the cable installed. Check the markings: Carefully inspect the cable jacket for any markings that might indicate suitability for cable tray use (e.g., "TC," "CT," or equivalent). Obtain the cable's cut sheet: Get the manufacturer's specification sheet for the cable. This will state the cable's intended applications and any relevant ratings.3.

Communicate with the Contractor

Have a professional conversation with the electrical contractor. Explain your concerns and point out the relevant NEC requirements.4.

Consult with an Electrical Engineer or Inspector

This is a critical step. An electrical engineer or inspector can: Provide an authoritative interpretation of the code. Assess the specific installation and determine if there are any alternative methods that might be acceptable (though unlikely). Advise on the best course of action to bring the installation into compliance.5.

Document Everything

Keep detailed records of all communication, inspections, and decisions. This is essential for liability protection.6.

Possible Remediation (Unfortunately Expensive)



Replacement

The most straightforward solution is to replace the non-CT-rated cable with properly rated cable. This is the most expensive option but guarantees compliance.

Derate

According to 392.80, “the ampacities of cables installed in cable trays shall be calculated in accordance with 310.14 and all applicable notes to Table 310.
16." This will likely mean you need to use larger gauge wiring.


Alternative Methods (Highly Unlikely)

It's highly unlikely that the authority having jurisdiction (AHJ) would approve an alternative method if the code specifically requires CT-rated cable. However, it might be possible if you can demonstrate an equivalent level of safety and performance.7.

Inspection

A thorough inspection by the Authority Having Jurisdiction (AHJ) is critical. They will have the final say on whether the installation is acceptable.

In Summary


Don't accept the argument that UV exposure is the only reason for CT-rated cable. Code compliance, mechanical protection, and fire safety are all important considerations.Document everything and get professional guidance from an electrical engineer or inspector. It's far better to address this issue proactively than to face potential problems, liabilities, or rejection during an inspection. Flag for review