User: AlxLnv, Location: Florida
Asked on: Sunday, September 8, 2024 at 12:15 pm EDT
Answered on: Thursday, March 6, 2025 at 2:10 am EST
Question: There is the question which is a little unclear, are the tankless water heaters or the steamers a continuous load or not? According to the Mike Holt forum thread, the answer was it is not, which question was closed by the Moderator in 2020. Now I met the same question.I finished the New Jersey Ocean County Vocational School with Electrical Apprentice certificate in 2008. Since 2008 the NEC got charged several times. If in 2002 the tankless water heaters were not popular, today they are on sales in Home Depot.If calculate non-continuous load it would be less OCDP rating and smaller wire size. With Continuous load the 125% add breaker rating and wire size. For example, 69 Amp nameplate refer that the wire may be AWG 6 of THHN or exual from 90°C for 75 ampacity instead of AWG 4 in case of continuous load, that will need to increase Ampacity to 95 amp, and breaker to 90 Amp.I remember that in my sister's house they changed their water tank into tankless and when they turn on the hot water the kitchen lights were blinking.Theoretically, the water heater MAY BE WORKING FOR THREE HOURS and longer. The relatives are visiting house and taking shower one after another one.By the life experience it may be very unusual.The old forum do not clear out if it is NON-CONTINUOUS or it is CONTINUOUS load. I think the new NEC should have the stipulations about.
You've hit on a tricky point that often leads to confusion and debate in the electrical world. Let's break down why the determination of whether a tankless water heater is a continuous load or not is nuanced and why you're seeing conflicting opinions.
Understanding Continuous Load
First, let's clarify the definition of a continuous load according to the NEC.
Article 100 defines a continuous load as:"A load where the maximum current is expected to continue for 3 hours or more."This is the KEY phrase that dictates whether the 125% derating factor applies for overcurrent protection (OCPD) and conductor sizing.
The Tankless Water Heater Dilemma
Here's why it's not always a straightforward yes or no answer:
Manufacturer Instructions
You always need to follow the manufacturer's installation instructions first. Some manufacturers may specifically state whether their tankless water heaters are to be considered continuous loads and designed accordingly.
Intermittent vs. Continuous Use
Tankless water heaters are designed for intermittent use. The heater only activates when hot water is called for. However, usage patterns can transform an intermittent design into a continuous load scenario.
Shower-Shower-Shower Scenario
As you mentioned, with multiple people showering back-to-back, or someone taking an exceptionally long shower, it's entirely possible for a tankless water heater to draw its maximum current for 3 hours or more.
Flow Rate and Incoming Water Temperature
The higher the flow rate of hot water demand, and the colder the incoming water temperature, the harder the tankless heater has to work and the longer it will be running to maintain the desired hot water temperature.
Why the Debate and Past Forum Discussions?
Older discussions and forum threads (like the one you mentioned) may have leaned towards "non-continuous" because: Assumptions about Typical Use
There was an assumption that tankless heaters wouldn't be used for such extended periods in a normal residential setting.
Older Technology
Older models might have been less efficient or had lower maximum outputs, potentially making the 3-hour threshold less likely to be reached.
Lack of Clear NEC Guidance
The NEC's stance on this specific appliance has historically been somewhat ambiguous, leading to interpretations based on local inspector discretion and engineering judgment.
NEC Guidance and Current Best Practices
While the NEC doesn't have a specific rule explicitly stating that all tankless water heaters must be treated as continuous loads, here's how you should approach the situation:1.
Manufacturer's Instructions
This is paramount. If the manufacturer designates it as continuous, you must comply.2.
Load Calculation and Application
Article 220 outlines the procedure for calculating branch circuit, feeder, and service loads. For tankless water heaters, you would use Article 220.53 to determine the demand factor for the water heater. Important
Even if you use a demand factor from 220.53, you still need to evaluate whether the heater could realistically operate at its maximum current for 3 hours or more. If there's a reasonable possibility of continuous operation (back-to-back showers, high hot water demand), treat it as a continuous load. Err on the side of caution.3.
Local Inspector's Interpretation
Check with your local electrical inspector. They may have specific requirements or interpretations for tankless water heaters in your area.4.
Engineering Judgement
This is where your experience and knowledge come in. Consider the following factors:
Size of the Dwelling
A large house with multiple bathrooms is more likely to have higher hot water demand.
Number of Occupants
More occupants mean a greater potential for continuous use.
Lifestyle
Consider the habits of the occupants. Do they tend to take long showers, use multiple hot water appliances simultaneously, or frequently have guests?
Addressing Your Concerns
Blinking Lights
The blinking lights in your sister's house likely indicate a voltage drop caused by the high inrush current of the tankless water heater. This could be due to:
Undersized wiring
If the wiring is too small, it can't handle the load without a significant voltage drop.
Weak electrical service
The service to the house might be inadequate for the increased load.
Loose connections
Loose connections can exacerbate voltage drop. Treating as a continuous load with correctly sized conductors and OCPD will help.
69 Amp Example
You're correct about the difference in conductor sizing based on continuous vs. non-continuous. If you treat a 69A load as non-continuous, you could potentially use #6 AWG THHN (90°C column, derated to 75°C termination rating, 55A, 125% of 55 is 69A). However, if it's continuous, you must use at least a #4 AWG THHN to handle the 125% (69A 1.25 = 86.25A) plus account for any other applicable derating factors for ambient temperature, conduit fill, etc.
New NEC
While the NEC continues to evolve, it's unlikely to make a blanket statement about all tankless water heaters being continuous loads. The diverse range of models and usage scenarios makes a one-size-fits-all approach impractical.
In summary, the best practice is to
Consult the manufacturer's installation instructions.2. Consider the likelihood of continuous use (3 hours or more) based on occupancy, lifestyle, and appliance specifications.3. Err on the side of caution and treat it as a continuous load if there's any doubt.4. Confirm with your local electrical inspector.
By following these steps, you'll ensure a safe and code-compliant installation. Flag for review