User: Doc13067, Location: Bucks County/Philadelphia, PA USA
Asked on: Monday, September 9, 2024 at 8:21 am EDT
Answered on: Thursday, March 6, 2025 at 2:11 am EST
Question: I’m currently bidding a mobile home service with a 200 amp pedestal. I planned to run 4/0 aluminum feeder wire from the pedestal to the home and then I started second-guessing because the ampacity is 180 A. However, this is still allowed, even though it’s not the service because those wires are feeding the entire load, is that correct? I’m really hoping I don’t have to run 350. I’m still on the 2017 code so we aren’t doing outside disconnects or anything so I just haven’t encountered this a bunch.
You're right to double-check! It's a common situation, and understanding the nuances of feeder sizing vs. service conductor sizing is crucial. Here's the breakdown based on the 2017 NEC, confirming your understanding and addressing some key points
You are generally correct:
You can likely use 4/0 Aluminum for this application, assuming your calculated load allows it. The 180A ampacity doesn't automatically disqualify it because it's a feeder, not the service.
Here's the breakdown of the reasoning
Feeder vs. Service
The key is that these are feeder conductors, not service conductors. Service conductors, the conductors from the utility source to the service disconnecting means, have very specific (and generally more restrictive) sizing requirements. Feeders, on the other hand, are sized based on the calculated load.2.
NEC 310.15(B)(7) (2017 NEC)
This is where the "service conductor" sizing rules come from, and they only apply to service conductors for dwellings. It doesn't apply to feeders.3.
Feeder Sizing (NEC 220)
You must perform a load calculation according to NEC Article 220 to determine the actual ampacity required for the feeder to the mobile home. This includes:
General Lighting Load
Based on the square footage of the mobile home (3 VA per square foot).
Small Appliance Branch Circuits
Two 20-ampere circuits (1500 VA each).
Laundry Circuit
One 20-ampere circuit (1500 VA).
Fixed Appliances
Ranges, water heaters, air conditioners, furnaces, etc. Use nameplate ratings and apply the appropriate demand factors (e.g., Table 220.55 for ranges). Air conditioning and heating loads are handled in Article 440.
All other loads4. Apply Demand Factors
After calculating the total connected load, you can apply demand factors where permitted by Article 220. Demand factors acknowledge that not all loads will be operating at their maximum simultaneously. This will reduce the calculated load.
5.
Feeder Ampacity
After demand factors, the resulting calculated load in amperes is what you need to size the feeder conductors for.6.
Using 4/0 Aluminum
If your calculated load (after demand factors) is less than or equal to 180 amps, then 4/0 Aluminum is acceptable, even though the pedestal has a 200A breaker.
Important Considerations and Where You Might Need Larger Conductors
Large Electric Ranges or Ovens
These are often the biggest load in a mobile home. Table 220.55 allows significant demand factors for ranges, but if you have a very large or high-wattage range, it could push your calculated load up.
Electric Heat (Baseboard or Forced Air)
Electric resistance heat is a very heavy load and has a high demand factor (usually 100%). This can dramatically increase the required feeder size.
Air Conditioning
Consider the locked rotor amperage (LRA) and running load amps (RLA) of the AC unit when calculating.
Future Load
Consider whether the homeowner might add additional loads in the future (e.g., a hot tub, another AC unit). It might be wise to upsize the feeder slightly to accommodate potential future needs. It's always better to be slightly oversized than undersized.
Voltage Drop
Longer runs of feeder conductors can experience significant voltage drop. Check your voltage drop calculation to ensure it is within acceptable limits (typically 3% for feeders). If voltage drop is excessive, you'll need to increase conductor size. For a 200A load on 4/0 Al, you'll have issues if the run is over 100' or so.
Example (Simplified)
Let's say after your load calculation (including demand factors), you arrive at a calculated load of 150 amps. In this case, 4/0 Aluminum (rated for 180 amps) would be sufficient.
What To Do
Perform a complete load calculation according to Article 220 of the 2017 NEC.2. Consider future loads.3. Check voltage drop.4. Based on the calculated load, select the appropriate conductor size.In summary, don't just assume 4/0 Al is okay. You must do the load calculation! If the calculation reveals that you need more than 180 amps, then yes, you'll need to use a larger conductor (like 350 kcmil Al).Disclaimer: This information is for educational purposes only and should not be considered a substitute for professional electrical advice. Consult a qualified electrician or electrical inspector to ensure that your installation complies with all applicable codes and regulations. Flag for review