User: Mr. Pickle, Location: Rogers MN
Asked on: Monday, September 9, 2024 at 1:09 pm EDT
Answered on: Thursday, March 6, 2025 at 2:12 am EST
Question: Wondering if this is a violation of the required 30" working space width. See attached image. Both Enclosure 1 and 2 are electrical equipment. Enclosure 2 is deeper than enclosure 1. The distance to the wall from enclosure 2 is only 26". Working space width can overlap enclosure enclosures, but does this apply if one of the enclosures is deeper than the other? Is there a violation here with the 30" working space rule for enclosure 1?
Yes, there likely is a violation of the 30" working space width requirement in this scenario. Here's why: NEC Requirement
The National Electrical Code (NEC) requires a minimum working space width of 30 inches in front of electrical equipment that is likely to require examination, adjustment, servicing, or maintenance while energized. This is to provide a safe and accessible area for electricians to perform their work.
Obstruction
Enclosure 2, because it is deeper, creates an obstruction that reduces the working space in front of Enclosure 1. Even though working space can overlap other equipment, the actual depth available is what matters in this situation.
Effective Width
The effective working width is measured based on the furthest protruding object. Since Enclosure 2 is deeper, it effectively dictates the available working width. The distance from Enclosure 2 to the wall (26") is less than the required 30".
Overlapping Working Space
While it's true that working space can overlap other equipment, this generally applies when the equipment is alongside the primary equipment, not in front of it, effectively reducing the depth of the required working space.
Therefore, because Enclosure 2 reduces the working space depth in front of Enclosure 1 to 26 inches, there is a violation of the NEC's 30-inch minimum working space width requirement.Recommendation
To correct this violation, one or more of the following actions should be taken:1.
Relocate Enclosure 2
The ideal solution is to move Enclosure 2 further away from the wall to provide at least 30 inches of clear working space.2.
Relocate Enclosure 1
Move Enclosure 1 so that its working space is not obstructed by Enclosure 2. This may require rearranging the layout of the electrical room.
3.
Use a Smaller Enclosure 2
If possible, replace Enclosure 2 with a smaller enclosure that doesn't protrude as far, allowing for the required 30 inches of working space in front of Enclosure 1.4.
Seek an Exception
In some very specific and limited circumstances, a local electrical inspector might grant an exception. However, this is highly unlikely in this scenario as it directly impacts safety. Do not rely on this.5.
De-energize when working
If the equipment can be easily de-energized, and that is an acceptable procedure, then while working, de-energize the panel and tagout the panel.
Important Note: This analysis is based on the provided information and the general requirements of the NEC. Always consult with a qualified and licensed electrician or electrical inspector for a definitive assessment and to ensure compliance with local codes and regulations. They can consider the specific details of the installation and provide tailored recommendations. Flag for review