Question: I have a 400 ' run of 3/4' EMT. It will be a 460 VAC two wire circuit. There are 3 4" square boxes in the run. Do need to install bonding bushings in each of the three boxes?(one on each of the two fittings in each box) or just one bonding bushing at the main breaker panel and one at the panel that this circuit will be feeding? Thank You, Steve Wiese.
Okay, Steve, let's break down the bonding requirements for your 3/4" EMT run with 4" square boxes and a 460VAC two-wire circuit.
Understanding the Code Requirements (NEC Perspective)
The National Electrical Code (NEC) focuses on ensuring a low-impedance fault current path back to the source to facilitate the operation of overcurrent protective devices (circuit breakers or fuses) in the event of a ground fault. This is achieved through proper grounding and bonding.
Key Considerations for your situation
Equipment Grounding Conductor (EGC)
The primary method for providing the low-impedance fault path is the equipment grounding conductor (EGC). In your case, the EMT conduit itself can serve as the EGC, if all fittings are properly tightened and meet listing requirements. However, at 460V and with a 400' run, reliance solely on the EMT is often not considered best practice.2.
Voltage
The 460V is significant, especially for a long run. Higher voltages increase the potential for leakage currents and require more attention to bonding.3.
Length of Run
A 400-foot run of EMT introduces significant impedance. Even well-tightened EMT couplings have some resistance. This resistance can impede the fault current, potentially delaying or preventing the overcurrent device from tripping quickly.4.
Concentric or Eccentric Knockouts
This is critical. If you are using standard knockouts and not using listed grounding locknuts, you will need bonding bushings to insure a proper bond.5.
Over 250V to Ground
At 460VAC, you will be over 250V to ground, and per NEC 250.97, you'll likely require bonding bushings on your concentric/eccentric knockouts.
NEC requirements and best practices
NEC 250.4(A)(5): Effective Ground-Fault Current Path
This is the overarching requirement. All parts of the electrical system must be designed and installed to create a low-impedance fault path.
NEC 250.92(B): Methods of Bonding
This section covers the acceptable methods for bonding enclosures containing service conductors. While this specifically applies to service equipment, the principles apply broadly.
NEC 250.96(A): Bonding Other Enclosures
Metal raceways, cable trays, cables, cable armor, enclosures, frames, fittings, and other metal non–current-carrying parts that are to serve as grounding conductors, with or without the use of supplementary equipment grounding conductors, shall be effectively bonded where necessary to ensure electrical continuity and the capacity to conduct safely any fault current likely to be imposed on them. Any nonconductive paint, enamel, or similar coating shall be removed at threads, contact points, and contact surfaces or be so designed as to make such removal unnecessary.
NEC 250.97: Bonding for Over 250 Volts
In other than service equipment, where circuit voltage exceeds 250 volts to ground, and metal raceways or metal-armored cables are used, each metal raceway and cable shall have a grounding bushing or similar fitting installed on each end of the raceway or cable.
NEC 314.4 Hubs
A bonding-type locknut is required on a metal raceway terminated to an enclosure (box) where: The box has concentric or eccentric knockouts. The box has knockouts of other than a standard size. The box is not identified for grounding.
Here's a breakdown of my recommendation
Run a supplemental EGC (Green Wire)
This is the best practice, without question. Run an appropriately sized insulated equipment grounding conductor (green wire) inside the EMT for the entire length of the run. This wire should be sized according to NEC Table 250.122, based on the rating of the overcurrent protection device protecting the 460V circuit. Terminate this EGC to the ground bar in the panel feeding the circuit and to the ground bar in the panel/enclosure being fed. This becomes your primary EGC.2.
Bonding Bushings at Each Box
Assuming your boxes have concentric or eccentric knockouts: Install bonding bushings with jumpers at each point where the EMT enters and exits the 4" square boxes. The jumpers (short lengths of copper wire) should be sized appropriately (at least the same size as the supplemental EGC) and connected securely to the box using a listed grounding screw or other approved method.3.
Bonding at Panels
At the main breaker panel and at the panel being fed, use bonding locknuts or bonding bushings (again, with jumpers to the ground bar).
Why this approach? Redundancy
The supplemental EGC provides a dedicated, low-impedance path for fault current. The bonding bushings/locknuts and jumpers provide additional fault current paths.
Safety
High-voltage systems demand extra precautions. This approach ensures the best possible protection.
Code Compliance
This approach will generally satisfy the NEC requirements, especially in jurisdictions with strict interpretations.
Mitigation of Voltage Drop
The supplemental EGC can also help to mitigate voltage drop, which is always a concern over long distances.
In Summary:
While the EMT can be used as an EGC, given the length of your run, the voltage, and the presence of boxes, I strongly recommend running a supplemental EGC and using bonding bushings with jumpers at each box (assuming the boxes have concentric or eccentric knockouts). This provides the most reliable and safest installation.Remember to consult with a qualified electrical inspector in your jurisdiction to ensure compliance with local codes and interpretations. Electrical work can be dangerous, and it's always best to err on the side of caution. Flag for review