User: confused123, Location: USA
Asked on: Monday, September 9, 2024 at 4:02 pm EDT
Answered on: Thursday, March 6, 2025 at 2:12 am EST
Question: We have a 4000A ATS that is about 150 feet away from our switchboard, it's located on the same pad as the gensets and the utility transformer. Per NEC 250.122 we need a 500 kcmil EGC. We are using (11) 4" conduit to run (33) 500 kcmil conductors, we don't use the neutral for any loads so we are omitting it after the service entrance at the ATS. With this setup we will need a 500 kcmil EGC in each conduit, so we will be running (11) 500 kcmil EGCs.My question is if anybody knows of an expectation in the NEC where we don't need an 500 kcmil EGC in each conduit or if someone has another idea how to make this 150 foot run more efficiently?
You've accurately identified the requirement for a 500 kcmil EGC based on the 4000A overcurrent protection device per NEC 250.122. Let's analyze the situation and explore potential solutions for a more efficient installation
Understanding the NEC Requirements:
250.122(B)
This is the key section. It states that when conductors are installed in parallel, the EGC shall be increased in proportion to the increase in phase conductors. The phrase "increased in proportion" is the reason you're running a full-sized EGC in each conduit. Since you've divided the phase conductors across 11 conduits, you must divide the required EGC proportionally.
250.122(F)
This section allows for the EGC to be run outside of the raceway under certain conditions. However, those conditions require the EGC to be installed with the phase conductors, and the total EGC cross-sectional area must equal or exceed the required size per 250.122(B). This doesn't offer a cost or material savings in your situation.
Why You're Running So Many EGCs
The reason you need so many EGCs is the parallel conductor configuration combined with the full-size requirement of 250.122(B).
Potential Solutions and Considerations
Single Raceway for Phase Conductors
The most direct and cost-effective solution, if possible
If physically and practically feasible, can you combine all phase conductors into a single, large raceway (or fewer raceways)? For instance, could you use a large bus duct or a concrete-encased duct bank? If you were able to run all phase conductors within one raceway, you would only need one 500 kcmil EGC within that raceway.
Feasibility Considerations
This likely involves a significant redesign of the physical layout. Consider available space, bending radii for large conduits, support structures, and the increased cost of a very large raceway versus multiple smaller ones.2.
Grounding Busbar at the ATS and Switchboard
Grounding at Each End
Ensure you have a robust grounding busbar at both the ATS and the switchboard. This helps equalize ground potential and provides a low-impedance path to ground.
Still Need the Full-Sized EGC
This doesn't eliminate the need for the 500 kcmil EGCs in each conduit, but it reinforces the overall grounding system.3.
Aluminum EGC
Consider Aluminum
Aluminum conductors have a lower cost than copper conductors for the same ampacity. In some cases, using aluminum for your EGC's can save you money overall.
Proper Terminations
Ensure you use connectors rated for aluminum-to-copper connections. Aluminum requires proper termination to prevent oxidation and loose connections.
Sizing
When using Aluminum, the EGC must be sized differently than if using copper. See NEC Table 250.122. In this situation, a 750 kcmil Aluminum EGC is required.
4.
Consult with a Qualified Electrical Engineer
The best advice
A licensed and experienced electrical engineer can thoroughly review your entire system design and explore all possible code-compliant solutions. They can assess the practicality, safety, and cost-effectiveness of each option and provide a stamped engineered drawing.
Important Considerations
Voltage Drop
A 150-foot run with that much current can have significant voltage drop. Make sure your 500 kcmil conductors are adequately sized for voltage drop, not just ampacity.
Ampacity
Verify the ampacity rating of your 500 kcmil conductors based on the specific insulation type, installation conditions (temperature, derating factors), and termination temperature ratings.
Coordination Study
A proper coordination study is crucial to ensure that your overcurrent protective devices (breakers, fuses) are correctly sized and coordinated to protect the entire system and minimize downtime.
Local Amendments
Always check for local electrical code amendments or interpretations, as these can vary by jurisdiction.
In Summary:
Your analysis of the NEC requirements is correct. The most efficient solution likely involves minimizing the number of parallel raceways as much as possible. A thorough review by a qualified electrical engineer is highly recommended to ensure a safe, code-compliant, and cost-effective installation. Flag for review