Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Multiple AC Units

User: xformer, Location: Dallas, Tx

Asked on: Monday, September 9, 2024 at 4:23 pm EDT
Answered on: Thursday, March 6, 2025 at 2:13 am EST

Question: I am looking for a code section that makes installing multiple AC units on one OCPD a violation. I am having a can't see the forest for the trees moment. Can anyone assist?

Okay, I understand. You're looking for a specific section in the NEC (National Electrical Code) that prohibits installing multiple AC units on a single overcurrent protective device (OCPD) (like a circuit breaker or fuse). This is a common misunderstanding, and it's important to clarify the requirements.The NEC doesn't have a single, direct statement that says, "You can't put multiple AC units on one OCPD." Instead, the prohibition arises from a combination of requirements related to:1. Overcurrent Protection

Each appliance has to be protected per its listing and nameplate.2.

Ampacity and Load Calculations

The circuit conductors must be sized to carry the load. If you overload the circuit, you violate this.3.

Individual Appliance Requirements

AC units often have specific circuit requirements.4.

Motor-Starting Current

AC units have a high inrush current when they start.Here's a breakdown of the NEC sections that, taken together, lead to the conclusion that you generally cannot run multiple AC units on a single circuit:

NEC 110.3(B) - Examination, Identification, Installation, and Use of Equipment

"Listed or labeled equipment shall be installed and used in accordance with any instructions included in the listing or labeling." This is the BIG one. AC units are listed appliances. The manufacturer's instructions almost always specify a dedicated circuit. You
must follow the manufacturer's instructions. Read the installation manual for any specific AC unit you are working with. You'll likely find language requiring a dedicated circuit.

NEC 440.3(A) - General. The provisions of this article shall apply to electric motor-driven air-conditioning and refrigeration equipment. Modifications to these provisions shall be permitted to provide improved safety and suitability where engineering evaluations so indicate."
Article 440 covers AC equipment NEC 440.22 - Application and Selection of Overload Relays

Overload protection is critical for motors. AC units use motors for compressors and fans.


NEC 440.6 - Ampacity Determination.
"For the purposes of selecting conductors, disconnect means, controllers, and branch-circuit short-circuit and ground-fault protective devices, the nameplate rated load current shall be used." This means you must use the AC unit's rated current for calculations. NEC 440.12(B) - Branch-Circuit Short-Circuit and Ground-Fault Protection. This section dictates how to protect AC equipment from short circuits and ground faults and often mandates specific breaker types or sizes. NEC 210.23 - Permissible Loads, Multiple-Outlet Branch Circuits

Although this section allows for multiple outlets on a circuit, it contains restrictions that will often preclude using it for AC units.


(A)(1)
says a 15 or 20 amp circuit shall supply lighting units, other utilization equipment, or combination of both. It can't exceed 80% of the branch circuit rating. (B)(2) says the total rating of any utilization equipment not fastened in place, shall not exceed 80% of the branch-circuit ampacity. (C) says on a 20 amp, individual branch circuit can supply any load for which it is rated.

How it Works in Practice1. Nameplate Data

Look at the AC unit's nameplate. It will state the minimum circuit ampacity (MCA) or maximum overcurrent protection (MOP). This is critical. The circuit must be rated to handle at least the MCA.2.

Load Calculation

Calculate the total load of all appliances you want to put on the circuit. Include everything, not just the AC units. Example: If each AC unit has an MCA of 10 amps, and you want to put two on a circuit, you're already at 20 amps before considering anything else on the circuit.3.

Inrush Current

AC units have a very high inrush current when the compressor starts. This inrush can be 3-7 times the running current, even briefly. Putting two AC units on the same circuit significantly increases the likelihood of tripping the breaker, especially if they try to start simultaneously.4.

Dedicated Circuits

Because of the load calculation, the inrush current, and the manufacturer's instructions, AC units
almost always require dedicated circuits. A dedicated circuit is one that serves only that appliance.

Why it's a Violation


Putting multiple AC units on a single circuit
violates the NEC because: It's very likely to overload the circuit conductors (NEC 210.19). It's very likely to exceed the OCPD's rating (NEC 240.3). It likely doesn't comply with the manufacturer's instructions (NEC 110.3(B)), which usually require a dedicated circuit. It can cause nuisance tripping of the breaker due to inrush current. It can potentially damage the AC units due to undervoltage during startup.

In Summary

While there isn't a single, simple statement, the NEC, in conjunction with the listing and labeling of the AC units, effectively prohibits putting multiple AC units on a single overcurrent protective device in most residential or commercial applications. The key is to look at the nameplate information for each AC unit and follow the manufacturer's installation instructions. If the nameplate specifies a dedicated circuit, you must provide one. Flag for review

Previous Question Next Question