User: fjm, Location: NJ
Asked on: Tuesday, September 10, 2024 at 7:14 am EDT
Answered on: Thursday, March 6, 2025 at 2:14 am EST
Question: In 2020 NEC ....225.31 and 225.33 Disconnecting a feeder to a detached structure. MLO panel with six or less BC breakers or install a main/backed breaker tied down.What I don't know,, Is the code referring to the feeder or branch circuits when disconnecting the supply. Shouldn't I be able to control the live bus.Thanks in advance,
Okay, let's break down NEC 225.31 and 225.33 in the context of disconnecting a feeder to a detached structure and clarify the situation with MLO (Main Lug Only) panels and your question about controlling the live bus.
Understanding NEC 225.31 and 225.33
These sections of the NEC deal with the required disconnecting means for feeders supplying detached buildings or structures. The goal is to ensure that someone can safely disconnect all ungrounded conductors at the detached structure. 225.31 Disconnecting Means Required
This section states a disconnecting means shall be installed at the location described in 225.30 (accessible either outside or inside the building nearest the point of entrance of the conductors).
225.33 Maximum Number of Disconnects
This section addresses how many disconnecting means are allowed. There are two important parts to understand:
(A) General
The disconnecting means can consist of up to six switches or circuit breakers mounted in a single enclosure, on a switchboard, or in a panelboard.
(B) Single-Pole or Multiconductor
A multi-pole breaker is considered one disconnecting means.
Applying This to a Detached Structure with an MLO Panel
Here's where your question about MLO panels comes in. An MLO panel does not have a main breaker. This is perfectly acceptable but it needs to meet the requirements of 225.33.
1. The Six Disconnect Rule
If you are only feeding a few circuits
If your detached structure only needs a few branch circuits and you use an MLO panel, you can use up to six individual branch circuit breakers as the disconnecting means. This is permitted. Each breaker must be clearly labeled as a disconnecting means for the entire structure.2.
The Main Breaker (or Switch) Option
If you prefer or need a single disconnecting means
You can install a main breaker (or a fused disconnect switch) in the MLO panel. This would then become the disconnecting means required by 225.31.
Tie-Down Requirement
If you add a main breaker to an MLO panel, it typically needs to be "tied down." This means that the panelboard must be designed in such a way that the main breaker cannot be easily removed or bypassed. This ensures that the breaker is permanently available as the disconnecting means.
Addressing Your Specific Questions "Is the code referring to the feeder or branch circuits when disconnecting the supply?" The code is referring to the entire supply to the detached structure, which is the feeder. The disconnecting means must be able to disconnect all ungrounded conductors of the feeder at the structure. This can be accomplished with one main breaker for the entire feeder, or with individual branch circuit breakers if the total is six or less. "Shouldn't I be able to control the live bus?" Yes, you absolutely should be able to control the live bus at the detached structure. That's the entire purpose of the disconnecting means! The disconnecting means (whether it's a main breaker or a group of branch circuit breakers) must be able to de-energize the entire panelboard in the detached structure, making it safe for work.
In Summary
NEC 225.31 and 225.33 require a disconnecting means at a detached structure that can disconnect all ungrounded conductors of the feeder. You can use an MLO panel if it complies with the six-disconnect rule (six or fewer branch circuits) or if you install a main breaker (or switch) that serves as the disconnecting means. If a main breaker is installed, it may need to be "tied down" to prevent its removal. The disconnecting means is intended to allow you to de-energize the entire panelboard, effectively controlling the live bus for safety.
Important Considerations and Recommendations
Local Amendments
Always check with your local electrical inspector for any local amendments or interpretations of the NEC. They have the final say on what's acceptable in your area.
Panelboard Markings
Make sure the disconnecting means (whether it's a main breaker or individual branch circuit breakers) is clearly and permanently marked to indicate that it disconnects the entire structure.
Ease of Access
The disconnecting means must be readily accessible to those who need to use it.
Load Calculations: Make sure you perform proper load calculations to determine the appropriate size of the feeder, the disconnecting means, and the overcurrent protection.I hope this clears up your understanding of NEC 225.31 and 225.33 in the context of detached structures and MLO panels. Electrical work can be dangerous, so please consult with a qualified electrician if you have any doubts or are unsure about any aspect of the installation. Flag for review