Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Breaker Sizing UL508A

User: Mehdi, Location: United States

Asked on: Tuesday, September 10, 2024 at 10:47 am EDT
Answered on: Thursday, March 6, 2025 at 2:14 am EST

Question: I have control transformer 1000VA, 208/120. I want to know if my breaker sizes are correct as per UL508A. Primary side, 1000/208 *250/100=12A. What should be the size of breaker 10A or 15A on primary side? On secondary side, 1000/120 * 125/100=10A. Is 10A breaker ok on secondary side? Thank you,

Okay, let's break down the breaker sizing for your control transformer according to UL 508A, keeping in mind the nuances of this standard.

Understanding UL 508A and Transformer Protection

UL 508A is the standard for industrial control panels. It provides guidelines for protecting components within the panel, including transformers. The goal is to protect the transformer from overcurrent situations (overloads and short circuits) while allowing for the inrush current that transformers experience upon energization.

Primary Side (208V)

You correctly calculated the primary current.

Full Load Current (FLA) Calculation

`1000 VA / 208 V = 4.8 A`


Your Primary Calculation

`(1000/208)250/100 = 12A`

UL 508A Overcurrent Protection Requirements


According to UL 508A, Section 33.4:
Control power transformer primary protection shall comply with Table 33.1 Table 33.1 states that primary side may be protected at 300% for transformer current ratings of 9 amps or less, or 167% for transformer current ratings greater than 9 amps Based on the above table, the 208V transformer requires primary protection at 300% FLA. Therefore, . Therefore, 4.8A 3 = 14.4 Amps. The next standard size breaker is 15 Amps.

Primary Breaker Selection



15 Amp Breaker: Yes
. A 15 Amp breaker is appropriate for the primary side.

Secondary Side (120V)

You correctly calculated the secondary current.

Full Load Current (FLA) Calculation

`1000 VA / 120 V = 8.3 A`


Your Secondary Calculation

`(1000/120)125/100 = 10.4A`

Secondary Breaker Selection

According to UL 508A, Section 33.4:
Control power transformer secondary protection shall comply with Table 33.2 Table 33.2 states that secondary side may be protected at 167% of the secondary rated current.

Based on the above table, the 120V transformer requires secondary protection at 167% FLA. Therefore, 8.3A 1.67 = 13.8 Amps
. The next standard size breaker is 15 Amps.

Secondary Breaker Selection



15 Amp Breaker: Yes
. A 15 Amp breaker is appropriate for the secondary side.

Important Considerations and Best Practices



Verify with Manufacturer Data

Always refer to the transformer manufacturer's documentation. They may specify recommended fuse or breaker sizes, which supersede the general guidelines.


Type of Breaker

Consider using a circuit breaker designed for transformer applications. These are often "high inrush" or "instantaneous trip" breakers designed to handle the initial surge without nuisance tripping. Standard thermal-magnetic breakers can work, but you might have to go up a size if you experience nuisance tripping on startup.

Downstream Load

Your final breaker selection will depend on the nature of the load connected to the secondary side. Make sure the breaker adequately protects both the transformer
and the wiring and equipment downstream. The secondary overcurrent protection devices are intended to protect the transformer as well as the downstream circuits, so they must be suitable for the application.

Short Circuit Current Rating (SCCR)

Ensure the control panel, including the transformer and overcurrent devices, has an adequate SCCR for the available fault current at the installation location. This is a critical safety requirement.

Local Codes

Always comply with all applicable local electrical codes and regulations. These may have requirements that go beyond UL 508A.


Professional Review

It's always a good idea to have your control panel design reviewed by a qualified electrical engineer or experienced control panel builder. This helps ensure safety, compliance, and optimal performance.

In Summary



Primary (208V)

15 Amp Breaker (Recommended)


Secondary (120V):
15 Amp Breaker (Recommended)Remember to double-check the manufacturer's data and consider the nature of the load connected to the secondary before making a final decision. Always prioritize safety and compliance with relevant codes and standards. Flag for review

Previous Question Next Question