Topic: Switchgear Question

User: charlie b, Location: Lockport, IL

Asked on: Tuesday, September 10, 2024 at 1:23 pm EDT
Answered on: Thursday, March 6, 2025 at 2:15 am EST

Question: I am reviewing a Design Analysis (DA) document written by a person who doesn't seem to understand the nature of switchgear. Or perhaps it is me who is missing something.It's for a military housing building, and the DA is calling for a 2000 amp main service switchgear with a 1500 amp MCB. I have already written a comment to the effect that this is overkill. But the DA description includes the statement that the breakers will all be molded case. Would that be, (A) perfectly normal, (B) unusual but not unheard of, or (C) absurd? I am inclined to say "C."Whatcha think?

You're right to question this. Let's break down why and classify it

The core issue: A 1500A MCB in 2000A Switchgear
Overkill

You're right; this is generally overkill. Unless there are VERY specific and unusual future expansion plans, a 2000A service switchgear for a load that's protected by a 1500A breaker is inefficient. You're paying for 500A of capacity you're not using.

Molded Case Breakers (MCBs) in Switchgear
General Use

MCBs are designed to be robust and reliable, and can serve for a wide range of current levels. However, at high current ratings (above ~800 Amps), other breaker types are usually used instead due to size and cost.

Air Circuit Breakers (ACBs)

Air circuit breakers (ACBs) are typically favored for high-ampacity switchgear applications. ACBs use air to extinguish the arc generated when a circuit is interrupted. They are physically larger and more complex than MCBs, but they offer higher interrupting ratings and are designed for frequent switching and maintenance.

Why MCBs at High Ampacity is Uncommon
Size

A 1500A molded case breaker would be huge. Space becomes a major constraint within the switchgear enclosure.

Cost

MCBs at those amperages tend to be more expensive than ACBs, which are more common in a switchgear.


Maintenance

ACBs are designed for maintenance and periodic inspection. MCBs are not.

Interrupting Rating

Although available, MCBs aren't generally known for high interrupting capacity. Depending on the available fault current from the utility, the interrupting rating of the breaker could be an issue.


Functionality

ACBs often have more sophisticated features like adjustable trip settings, remote operation capabilities, and advanced monitoring features, which are beneficial in a service entrance application.

Classification


Given the above, your classification of (C) Absurd is appropriate.

Here's a more nuanced way to put it

While technically possible to have a 1500A MCB in a 2000A service switchgear, it is highly unconventional, inefficient, and likely not the best solution. It raises significant questions about the designer's understanding of switchgear best practices.

What to do in your review


Specifically question the rationale

Don't just say "overkill." Ask: "What is the calculated or anticipated connected load of the building? Please provide the load calculations supporting the need for a 1500A breaker." "What are the future expansion plans that necessitate a 2000A switchgear? Please provide details." "Why was an MCB selected for the main breaker instead of an Air Circuit Breaker (ACB)? An ACB may offer a more cost-effective, maintainable, and space-efficient solution at this amperage." "What is the available fault current at the service entrance? Confirm that the interrupting rating of the 1500A MCB is adequate for the application."2.

Suggest alternatives

Recommend that they explore using a smaller switchgear (e.g., a 1600A) with a more appropriately sized ACB.3.

Consider the Military Housing aspect

Military specs often have requirements that drive up component sizes. Be sure you're aware of any specific military standards that might be influencing this design.

In summary, your intuition is correct. This design seems off. Force the designer to justify their choices with solid reasoning and calculations.
Flag for review