User: tortuga, Location: Oregon

Asked on: Tuesday, September 10, 2024 at 3:22 pm EDT
Answered on: Thursday, March 6, 2025 at 2:15 am EST

Question: Greetings all I came across a pole mounted pump service that has a manual generator interlock,the original installer used what appears to be a #6 SJO hard service cord with a cord cap as the 'inlet' for a 50A generator.Since a portable generator would be used it meets article 400 as its purpose is to "Connection of utilization equipment to facilitate frequent interchange".however since I typically see a piece of conduit to a 3R box with an 'inlet' I am wondering if any other code sections prohibit this or is this common in other areas?My plan is to replace the service and leave everything else as is, unless its a code violation to leave the cord?Thanks in advance

You've identified a situation that, while potentially meeting the letter of a few codes, raises significant safety concerns. Let's break it down

Arguments for it technically being allowed (but not recommended):
Article 400 (Flexible Cords and Cables)

As you pointed out, Section 400.7(A)(6) allows flexible cords for the "connection of utilization equipment to facilitate frequent interchange." A portable generator arguably falls under this definition. SJOOW is a type of flexible cord permitted by Article 400.


50A Compatibility

#6 SJOOW is theoretically rated for 50 amps in some situations, depending on the specifics of the cord and the temperature rating. However, its often rated closer to 45 Amps.

Manual Interlock

The presence of a manual interlock is crucial. This prevents backfeeding the utility grid when the generator is connected, a critical safety feature.

Reasons why this installation is
highly questionable and problematic


Misapplication of SJOOW for Stationary Wiring

While Article 400 permits flexible cords for portable equipment,
this installation isn't portable. The pump and the interlock are permanent parts of the electrical system. Using flexible cord as a substitute for permanent wiring methods like conduit is generally a violation of the spirit (and often the letter) of the NEC.2.

Durability and Environmental Exposure

SJOOW, while robust, isn't designed for continuous outdoor exposure, UV radiation, and potential physical damage. Conduit and proper enclosures provide far superior protection for the wiring and connections. Think about the longevity of the cord in direct sunlight, rain, snow, etc. It will degrade much faster than wiring in conduit.3.

Potential for Damage to the Cord

The cord is likely to be left exposed, creating a tripping hazard and subject to damage from lawn equipment, animals, weather, etc.4.

Strain Relief Issues

How is the cord secured to the pole and the interlock? Improper strain relief can lead to stress on the conductors and eventual failure.5.

Potential for Mismatched Cord Cap/Receptacle

Is the cord cap and receptacle (the "inlet") rated for outdoor use and appropriately weather resistant? Improper connections can lead to corrosion and electrical hazards.6.

Amperage issue

While #6 SJOOW may technically be rated for 50A in some conditions, its not a common or ideal installation. It is far more typical to see 6 AWG ran for 40/45 Amps.

Code Sections that are Potentially Violated



NEC 110.3(B) (Installation and Use)

Equipment must be installed and used according to its listing and labeling. The SJOOW cord is likely not listed for this type of permanent installation.

NEC 300.3(A) (Completeness of Circuit)

All conductors of a circuit, including the grounding conductor, must be contained within the same raceway, cable, or enclosure. It's unclear if the grounding conductor is properly protected and installed in this scenario.


NEC 300.4 (Protection Against Physical Damage)

Wiring methods must be protected from physical damage. An exposed SJOOW cord is vulnerable.

NEC 310.15 (Ampacity)

Ensure the ampacity of the cord is adequate for the load and generator size, considering environmental factors.


NEC 400.8 (Uses Not Permitted)

This section specifically prohibits using flexible cords:

(1)
As a substitute for the fixed wiring of a structure. (5) Where attached to building surfaces. (6) Concealed behind building walls, ceilings, or floors. Article 314 (Outlet, Device, Pull, and Junction Boxes; Conduit Bodies; Fittings; and Manholes)

If junction boxes are used, they need to be appropriate for the environment (3R rated, etc.).

Recommendation



Do NOT simply replace the service and leave the generator connection as is.
This installation needs to be corrected for safety and code compliance.Here's what I recommend:1. Install a proper weatherproof (3R) enclosure/junction box near the interlock.2. Run conduit (rigid metal conduit (RMC), intermediate metal conduit (IMC), or PVC conduit if permitted by local codes and soil conditions) from the enclosure to the interlock.3. Use appropriate listed conductors (THHN/THWN) inside the conduit, sized appropriately for the 50A generator. Ensure you have a properly sized grounding conductor.4. Install a listed and labeled inlet (generator receptacle) inside the enclosure. This should be a proper generator inlet, not just a random receptacle. Ensure its NEMA configuration is appropriate for the 50A generator (e.g., NEMA L14-50 for a 125/250V generator).

In summary: replace the SJOOW cord with a proper wiring method using conduit and listed conductors. This is the safe and code-compliant solution. This isn't just about following the letter of the code; it's about ensuring the safety of the installation and preventing potential hazards. Consult with a qualified electrician if you're unsure about any aspect of this work. Flag for review