Topic: Insulated wire like THHN XHHW on cable tray

User: eunji, Location: NC

Asked on: Tuesday, September 10, 2024 at 3:59 pm EDT
Answered on: Thursday, March 6, 2025 at 2:15 am EST

Question: Hi,When I reviewed the NEC 392 (Cable tray), there is restriction of single conductor to 1/0 and larger.Also, equipment grounding wire has to be bigger than 4AWG.In table 392.10 (A) Wiring Methods, I can't find the insualted single wire like type THHN, THWN and XHHW.My questions are1. Do I have to understand that insulated single wire has to be bigger than 1/0?2. Is there any way to use smaller size like 6AWG ground wire for circuit?Thank you!

You've raised good points about NEC 392 (Cable Trays) and wiring within them. Let's break down each of your questions

1. Do I have to understand that insulated single wire has to be bigger than 1/0?
Yes, but with qualifications. NEC 392.22(B) generally requires single conductor cables installed in cable tray to be 1/0 AWG or larger. However, there are exceptions. Here's the breakdown: 392.22(B) Single Conductors. Single conductors 1/0 AWG and larger shall be permitted to be installed in accordance with 392.22(B)(1) through (B)(3): (1) In industrial establishments only, where conditions of maintenance and supervision ensure that only qualified persons will service the installed cable tray system, single conductors shall be permitted to be installed in ladder, ventilated trough, or ventilated channel cable trays. (2) In ladder cable tray. (3) In ventilated trough cable tray. 392.22(C) Multiconductor Cables. Multiconductor cables, such as Type TC (Tray Cable), are permitted in cable trays regardless of conductor size, as long as they are listed for use in cable tray (have the "-TC" designation).This means that in a standard commercial application single conductors smaller than 1/0 AWG aren't permitted in cable tray.

Therefore, single conductor cables like THHN, THWN, and XHHW
can be used in cable tray, but generally only if they are 1/0 AWG or larger. The table 392.10(A) doesn't specifically list them because it's focused on wiring methods (complete systems). It assumes you know THHN, THWN, XHHW are approved wire types if properly installed within a compliant wiring method.

Exception: TC Cable

If you need smaller conductors in a cable tray, use Type TC (Tray Cable). TC cable is a multiconductor assembly specifically designed for cable tray use, and its individual conductors can be smaller than 1/0 AWG.

2. Is there any way to use smaller size like 6 AWG ground wire for a circuit?

Yes, absolutely! The 4 AWG requirement is
specifically for equipment grounding conductors within cable tray. The NEC has different rules for equipment grounding conductors (EGCs) run outside of cable tray, or inside cable tray as part of a cable assembly. 392.10(B)(1)(c) Equipment Grounding Conductors. Where cable tray is used as an equipment grounding conductor, provisions are made to comply with 392.7(A). Where the cable tray contains only metal-sheathed cable or metal-clad cable, the cable tray shall be permitted to serve as the equipment grounding conductor. Where the cable tray contains nonmetal-sheathed cable or nonmetal-clad cable, one or more equipment grounding conductors shall be installed to comply with 250.
134.
392.10(B)(1)(c)(1) Equipment Grounding Conductors in Cable Trays. Equipment grounding conductors (EGC) 4 AWG and larger where installed within cable trays, shall comply with 250.8(A) and 250.8(B).This section is stating that a cable tray is allowed to be used as an equipment grounding conductor if the cable tray and connections are designed to handle the ground fault current. 250.122 provides the rules for sizing EGCs. This is what you'll reference to determine the appropriate EGC size based on the overcurrent protection device. Generally speaking, a 6 AWG EGC is perfectly acceptable for many common circuits (e.g., 50A, 60A circuits). It just can't be a single conductor used as the sole EGC within the cable tray for conductors not within a cable assembly.

If the EGC is part of a cable assembly (like TC cable), then the EGC size within the cable is determined by the cable's listing and 250.122. You could have a TC cable with 6 AWG EGC running in a cable tray.

In Summary



Single Conductor Size in Cable Tray

Generally 1/0 AWG and larger, except within TC cable.

Equipment Grounding Conductor Size

4 AWG and larger for
single conductor EGCs in cable tray. Smaller sizes are permitted if the EGC is part of a cable assembly (like TC cable) or if the cable tray is not used as the ground.

Recommendations



For smaller conductors in cable tray

Use Type TC cable. This is the most common and compliant solution.

Refer to 250.122 for EGC sizing

This section provides the appropriate EGC size based on the overcurrent protection device.


Consult with a qualified electrician or electrical engineer: For complex installations or where you have any doubts about compliance, it's always best to seek professional advice.Always consult the latest edition of the NEC and local amendments for the most accurate and up-to-date information. Understanding the specific context of your installation is critical for ensuring compliance and safety. Flag for review