Question: I work on a lot of community solar projects that interconnect to overhead lines in the 15-35kV classes. The service usually comes with a grounded conductor as well. Typically the OH setup is as follows:Existing Utility Pole -> Utility Meter Pole -> Customer Service Disconnect Pole -> Customer Meter Pole -> Customer Recloser Pole -> Riser PoleMy partners and I were debating whether the Neutral-Ground bond in a customer owned transformer downstream of these poles is a Main Bonding Jumper or System Bonding Jumper. There is no question to me that this would be a System Bonding Jumper, and I was able to convince them that much.I went to Section 250 Part X to review bonding requirements for MV services, and I still have some questions on how it applies to OH equipment.1. 250.186(A) says the grounded conductor must be bonded to the disconnect enclosure, but if it is an overhead GOAB switch, does that even count as the enclosure? Does this section apply?2. I don't usually see an EGC being run with overhead conductors, but is it possible that this is technically required per 250.1803. Does the NEC have any blind spots for OH mounted equipment?Thanks!
Okay, let's break down these community solar overhead (OH) interconnection grounding questions according to the NEC (specifically 2023 edition, which is the most current generally adopted).
Understanding the Terminology and Context System Bonding Jumper (SBJ)
This is the connection between the grounded (neutral) conductor and the equipment grounding conductor (EGC) at the source of a separately derived system (SDS). In your case, the transformer on the customer side creates an SDS.
Main Bonding Jumper (MBJ)
This is the connection between the grounded conductor and the equipment grounding conductor at the service equipment. Your setup has the utility providing the service.
Equipment Grounding Conductor (EGC)
The conductor used to connect the non-current-carrying metal parts of equipment, raceways, and other enclosures to the system grounding electrode conductor at the service equipment or at the source of a separately derived system. It is the conductor that provides a low impedance path to ground for fault current to facilitate the operation of overcurrent protective devices.
Addressing Your Questions1. 250.186(A) and Overhead GOAB Switch
Yes, 250.186(A) applies. This section focuses on bonding the grounded conductor to the equipment.
GOAB Enclosure
The key is to consider the GOAB (Gang Operated Air Break) switch's enclosure. Even though it's mounted on a pole, it has a metallic structure that needs to be grounded/bonded. If the GOAB switch has an enclosure, and that is not inherently bonded to the grounded conductor, this section applies.
Practical Application
Often, the grounded conductor is simply bolted to the steel frame of the GOAB switch (which acts as the enclosure), effectively bonding them together. The method needs to provide a low-impedance path. A simple tap connection might not be sufficient if there's a significant resistance between the grounded conductor and the switch enclosure.
Compliance
You need to ensure that the grounded conductor and the metal portions of the gear (if metallic) are bonded together via a means approved for the purpose. This could be a listed lug or other device.2.
EGC and Overhead Conductors (250.180)
250.180 Considerations
This section gets into the grounding of the supply side of the service. While it often is the responsibility of the utility, it is ultimately up to the inspector/Authority Having Jurisdiction (AHJ) to determine who's responsible.
Required EGC?
250.180(B) states that a grounded conductor is permitted to ground non-current-carrying metal parts of equipment and raceways per 250.
184. If there are metal parts of equipment or raceways that aren't effectively bonded through other means (like a solid metal pole), then an EGC could be required.
Practical Considerations
Overhead conductors often lack a dedicated EGC because the metallic pole structure itself is often used as a ground path. However, the NEC does not specifically say that a pole is permitted to serve as an EGC.
Compliance
The EGC would only be required if the equipment is required to be grounded per Article 250 Part V. In addition, 250.4(A)(5) specifies that exposed metal parts must be connected to an equipment grounding conductor, which means this conductor must be present.
Important Considerations: Ensure that all metal parts of the overhead equipment (such as enclosures, hardware, and support structures) are properly connected to the grounding system. This grounding system should comply with the requirements of Article 250, including having a low impedance path to ground. If the existing overhead system does not meet these requirements, an equipment grounding conductor should be installed to ensure compliance with the NEC.3.
NEC Blind Spots for OH Mounted Equipment
Limited Specificity
The NEC is generally performance-based, not prescriptive. It outlines what needs to be achieved, but not always how to achieve it in every specific scenario. This is especially true for utility-owned or controlled equipment prior to the service point (typically the utility meter).
Practical Implications
This means the AHJ has significant discretion in interpreting the NEC and requiring specific grounding measures for OH equipment. What might pass in one jurisdiction could be rejected in another.
Areas Needing Attention
Bonding of Overhead Raceways
The NEC often assumes raceways are metallic and bonded. If you're using PVC or other non-metallic conduit for OH runs, you definitely need to ensure a proper EGC is installed within the conduit.
Corrosion
OH equipment is exposed to the elements. Ensure all grounding and bonding connections are corrosion-resistant and protected from the weather.
Mechanical Protection
Overhead conductors and grounding conductors need to be protected from physical damage (e.g., from tree limbs).
Accessibility
Grounding connections should be accessible for inspection and maintenance.
Working with the Utility
You will be working very closely with the utility, and they may have additional grounding and bonding requirements that are more stringent than the NEC. Defer to their requirements first.
Working with the AHJ
The AHJ will have the final say in enforcing the code. Discuss your grounding and bonding methods with them early in the design process to avoid surprises.
In summary: The transformer creates a separately derived system, so the neutral-ground bond at that transformer is a System Bonding Jumper. 250.186(A) applies to bonding the grounded conductor to any metallic enclosure associated with the GOAB switch. Whether an EGC is required along with the overhead conductors will depend on whether the utility and AHJ are using the pole as an EGC. The NEC isn't always perfectly clear about overhead equipment, so you need to work closely with the utility and the AHJ.Remember that local codes, utility requirements, and AHJ interpretations always supersede the NEC. Always consult with them for specific guidance. Flag for review