Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Service Sizing for Golf Course Pump Station

User: PluggedIn66, Location: Sarasota, FL

Asked on: Wednesday, September 11, 2024 at 11:39 am EDT
Answered on: Thursday, March 6, 2025 at 2:17 am EST

Question: Hello everyone, long time reader and first time poster here.We are working on an upcoming project, where golf course is upgrading pump station for course irrigation. The pump station is prefabricated and UL listed with 405FLA stamped on nameplate). Pump station is 3PH 480V. The prefabbed station has a 600A fusible main disco built-in (with 600A dual element, RK5 fuses) , and we will also be installing a service entrance rated 600A fusible disco/manual transfer switch ahead of the pump station.. There is an existing 3PH 480V 400A service, fed with parallel 4/0 AWG THWN-2 Cu feeders in (1) 3" PVC conduit feeding previous pump station. Existing self contained meter can is 400/320A rated.QUESTION: Can I replace the 400/320A meter can with a 600/480A can, and RE-USE the existing feeders? According to my calcs (and using the 90*C column for derating purposes), these parallel feeders are rated for a max of 416A (260A+260A*0.8), which is above the 405A FLA.The prefabbed equipment with 600A disconnect is making me question whether we need to provide a true 600A to equipment. Other issues throwing me off (which may be a moot point due to UL listing of equipment?)...The pump station contains (4) 75HP motors, (1) 30HP motor, and (1) 5HP motor, all at 480V. My FLA calcs are higher than what is listed (96Ax4 + 40A + 7.6A), or 431.6A. At this point, the existing service feeders would not be adequate.These pump stations are state of the art for the market, and contain VFD's for all motors...so maybe that is where they are able to decrease the FLA calcs...not sure on this one, or that it even matters.Anyhow, I appreciate everyone/anyone's time and help on this one!

Okay, this is a good, practical question with a few layers to unpack. Here's a breakdown of my thoughts and how I'd approach this

Key Considerations:
UL Listing and Prefabrication

This is HUGE. The fact that the pump station is UL listed and prefabricated significantly changes the game. This means the manufacturer has already gone through rigorous testing and design to ensure the entire system (pumps, VFDs, controls, and disconnect) operates safely and within the specified ratings.


VFDs and Reduced FLA

You are correct that the use of VFDs drastically reduces the inrush current and overall demand compared to across-the-line starting. This is likely the primary reason the manufacturer is able to use a lower FLA rating on the nameplate than what you'd calculate based on the motor HP alone.

NEC 430 (Motors, Motor Circuits, and Controllers)

This is the section of the NEC that governs motor installations. However,
because the entire pump station is UL listed, NEC 430 requirements for individual motor branch circuits might be superseded by the UL listing requirements for the entire assembly. This needs to be confirmed.

Feeder Ampacity vs. Load

You need to ensure the feeders feeding the pump station are adequately sized for the load, considering the UL-listed FLA and any potential future load growth.

Coordination and Utility Requirements

Always coordinate with the utility company. They will have requirements for the meter can, service entrance, and possibly protection.

Analysis and Recommendations


Manufacturer's Documentation is King



Obtain the UL Listing Report

This is crucial. The UL listing report will detail the specific testing and requirements the pump station meets. It will also specify the maximum overcurrent protection (OCPD) and conductor size the unit is designed for. The UL report is the governing document.

Review the Manufacturer's Installation Instructions

These instructions
must be followed. They will specify the required feeder size, OCPD, grounding, and other critical installation details.

Contact the Manufacturer

If anything is unclear, contact the manufacturer's technical support. Ask them specifically about the discrepancies between your calculated FLA and the nameplate FLA, and whether your existing feeder size is adequate.2.

Address Your Specific Questions



Can you re-use the existing feeders and just upgrade the meter can?
Maybe, but not likely. Meter Can

You definitely need to upgrade the meter can to a 600/480A rated unit to match the service disconnect.

Feeders

The 405A FLA on the nameplate is the limiting factor. Your existing parallel 4/0 feeders
technically have an ampacity of 416A after derating (based on your calculations). This appears to be adequate for the pump station. However, the local AHJ may consider this inadequate, as it only provides for a 2.7% difference, so do confirm with them.

Important Considerations



NEC 310.15(B)(7)

If this is a dwelling unit service, you might be able to use the ampacity reduction allowed by this section, but it doesn't sound like it is.


Future Load Growth

Is there any possibility of adding more equipment or expanding the system in the future? If so, consider upsizing the feeders now to avoid costly upgrades later.

Voltage Drop

Even if the ampacity is sufficient, check the voltage drop under full load. Long feeder runs can result in excessive voltage drop, which can damage the equipment.


AHJ Approval

Ultimately, the local Authority Having Jurisdiction (AHJ) has the final say. Discuss your plans with them early in the process.

The 600A Disconnect

The 600A disconnect is there primarily for
fault current protection and system isolation. It doesn't necessarily mean the system requires 600A of continuous current. The manufacturer likely chose a 600A disconnect to provide adequate interrupting capacity for potential faults. This size disconnect is also likely a standard offering for them, which may result in a lower purchase price for the equipment.

Motor FLA Calculation Discrepancy

The manufacturer's reduced FLA is almost certainly due to the VFDs. VFDs control the motor's voltage and frequency, allowing them to start and operate at lower currents. Trust the manufacturer's nameplate FLA.3.

NEC Requirements to Consider



NEC 230 (Services)

Make sure the entire service entrance complies with NEC 230, including proper grounding, bonding, and overcurrent protection.


NEC 250 (Grounding and Bonding)

Proper grounding and bonding are critical for safety. Ensure the grounding electrode system is adequate and that all equipment is properly bonded.*

NEC 110.3(B)

This is the most important! "Listed or labeled equipment shall be installed and used in accordance with any instructions included in the listing or labeling."

Action Plan


Obtain and Review the UL Listing Report and Manufacturer's Installation Instructions.
2. Contact the Manufacturer's Technical Support. Discuss your concerns and confirm that your existing feeder size is acceptable given the UL listing and VFDs.3. Perform Voltage Drop Calculations.4. Consult with the Local AHJ. Present your plans and the manufacturer's documentation for approval.5. Upgrade the Meter Can to a 600A Rated Unit.6. Follow All Manufacturer's Instructions and NEC Requirements.7. Document Everything. Keep a record of all communications, calculations, and approvals.

In Summary:

The UL listing of the pump station is the most important factor here. It simplifies the process significantly. You need to confirm the existing feeders are appropriate for the load and the manufacturer's instructions allow you to use them. Prioritize communication with the manufacturer and the AHJ. Good luck! Flag for review

Previous Question Next Question