Topic: reducing of motor wire size

User: malachi constant, Location: Minneapolis

Asked on: Wednesday, September 11, 2024 at 1:57 pm EDT
Answered on: Thursday, March 6, 2025 at 2:18 am EST

Question: Hi all, we have a motor being replaced with a smaller unit. The existing unit was fed with #8s from a 40A breaker. The new unit is smaller and the contractor proposes reusing the breaker and wire, with a new disconnect fused at 15A being installed at the motor. I don't have detailed information on motor size. Assuming the 40A breaker is too large of OCPD for the motor, is it legal to fuse down like that at the motor? This strikes me as a "tap rule" crossed with "motor rules", both of which are out of my wheelhouse beyond the basics, and confound me.It was our suggestion that they swap out the 40A breaker with a smaller 15A breaker, but the contractor states the panel is older and they do not think they can find a replacement breaker in a timely manner. (I bring that up to head off the common sense suggestion.)

Okay, let's break this down. Your instincts are right; this is a bit of a tricky situation that requires understanding the intent behind the code, not just the letter.

The Situation & Potential Problems



Existing

#8 AWG conductors protected by a 40A breaker feeding a motor.


Proposed

Replace the motor with a smaller one, keep the #8 AWG and 40A breaker, and install a 15A fused disconnect at the motor.

Concern

The 40A breaker is likely too large for the
overload protection of the smaller motor.

Relevant NEC Considerations


Motor Branch Circuit Protection (430.52)

This section deals with the
short-circuit and ground-fault protection of the motor branch circuit. The 40A breaker is likely sized based on this, allowing for inrush current on motor starts for the original motor. The breaker primarily protects the conductors from faults, not the motor from overloads.2.

Motor Overload Protection (430.31 & 430.32)

This section deals with
overload protection, which is designed to protect the motor from running at excessive current for extended periods. This is where a problem likely exists. The 15A fuse in your contractor's proposal is intended to provide this protection.3.

Tap Rules (240.21)

Tap rules allow you to reduce conductor size in certain circumstances, when the conductor is protected from faults. Your contractor's proposal
sounds a bit like a tap rule application, but for a motor application. Tap rules are generally for feeders, not branch circuits, though 240.21(B)(2) does have an exception for conductor runs of 25' or less for a 100A or less tap. This is not applicable in your situation because of the motor rules overriding the tap rules, and the 40A breaker being larger than 100A.
4.


Fused Disconnects (430.109)

This is fine for the motor, as it provides the means to disconnect. However, it does not replace the need for appropriate branch circuit protection (430.52) or overload protection (430.31/430.32).

Legality and Safety Analysis



Technical Legality

The biggest problem is that the 40A breaker is likely too large to provide adequate overload protection for the new, smaller motor. Overloads are not the same as short circuits, and can damage the motor even if the breaker doesn't trip. The 15A fuses in the disconnect are intended to provide that overload protection. The acceptability of the design depends on the specifics of the motor and how well the fused disconnect can truly act as an overload device.

Code Compliance

It's unlikely this setup fully complies with the spirit of the code, particularly 430.32, which deals with running overload protection. The 15A fuse is trying to function as the overload protection, which may or may not work as intended.


Practicality & Safety

The smaller motor could potentially run for a long time with a moderate overload, and the 40A breaker would never trip. The motor could overheat and fail, or in extreme cases, cause a fire. The 15A fuse may prevent this, but without knowing the motor specifics (FLA, Service Factor) it's hard to say for sure.

Why the Contractor's Suggestion is Problematic

The contractor is trying to avoid replacing the breaker. While the intent is good (provide overload protection with the fuses), the method is questionable, and potentially unsafe and not fully code-compliant.

Better Solutions (in order of preference)


Replace the 40A breaker with the correct size breaker

This is the best solution. Find a breaker that matches the panel, and size it according to NEC 430.52 based on the new motor's nameplate.
2.


Use a Motor Starter with Overloads

Replace the existing breaker with a correctly-sized breaker for the motor's branch circuit protection (short circuit/ground fault). Install a motor starter with properly sized overload relays. This is a more sophisticated and robust solution and can be a good choice for critical motors.3.

Carefully Analyze the Fused Disconnect

Get the new motor's nameplate data (Full Load Amps (FLA), Service Factor). Calculate the maximum allowable overload protection based on the motor's FLA and Service Factor (typically 115% to 125% of FLA, see NEC 430.32).

Verify
that a 15A fuse (or a smaller size) is appropriate for overload protection, based on the motor's FLA and Service Factor. Verify the interrupt capacity (AIC) of the fuses will handle a fault. Carefully document this analysis and keep it with the motor. If the 15A fuse is appropriate for overload protection, and you are comfortable with this solution, consider it. This is the least desirable option, because it is not fully code compliant, as there will be no means of overload protection at the supply end, as required by 430.32.

My Recommendation

Push back on the contractor's proposal. Explain your concerns about overload protection. Insist on Option #1 (replace the breaker) or Option #2 (motor starter). Offer to help source the correct breaker if needed. These are the safest and most code-compliant solutions. Only consider Option #3 if you've done your homework, understand the risks, and are willing to accept them. Have a qualified electrical engineer review your calculations.

In summary, while the contractor's proposal might
seem* like it addresses the immediate problem, it likely doesn't fully comply with the NEC or provide the best protection for the new motor.
You have a valid concern, and you should advocate for a safer and more code-compliant solution. Flag for review