Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Dedicated space above a wall mounted transformer.

User: steve61, Location: Nebraska

Asked on: Wednesday, September 11, 2024 at 2:08 pm EDT
Answered on: Thursday, March 6, 2025 at 2:18 am EST

Question: I am mounting a 15 KVA transformer(single phase,460 to 208)on a concrete wall. According to 110.26(a)(3),The working clearance only needs to be 6.5' high or as high as the equipment, ,whichever is higher. According to 110.26(E)(1)(a) the dedicated space must extend 6' above the equipment. I want to mount the transformer 5' off of the floor. At this elevation, there will be a couple of conduits(unrelated to this installation) within the 6' distance, with the ceiling 5' above the top of the transformer. Can I mount the transformer there ,Or must I find a different location ? There are no other items above the transformer, such as sprinkler lines, water lines ,drain lines, etc. Am I getting working space confused with dedicated space ? They both seem to be the same thing in this instance. Thank You ,Steve Wiese.

You're right to be cautious and precise. Let's break this down and address the Code requirements.

You are correct in distinguishing between working space and dedicated equipment space. They are not the same thing, even though they are related to the equipment.

Here's the analysis based on the 2023 NEC (or whatever version your jurisdiction uses, though these concepts are fairly consistent): Working Space (110.26(A)): This is about providing enough room for a qualified person to safely operate and maintain the equipment while energized. Key points: Height (110.26(A)(3)): Yes, it is 6.5 feet high or the height of the equipment, whichever is greater. Your transformer will dictate the height requirement. Since the transformer is at least 18" tall, 6.5' will be sufficient. Depth (110.26(A)(1)): The depth (distance away from the wall) depends on the voltage to ground and conditions. Since your secondary voltage is 208V, the maximum voltage to ground will be 120V. Per 110.26(A)(1), you need at least 3 feet of clearance for Condition 1 (exposed live parts on one side and grounded parts on the other or no exposed live parts on either side). Width (110.26(A)(2)): The width must be the width of the equipment or 30 inches, whichever is greater. This space must be maintained clear and unobstructed, providing safe access for personnel. Dedicated Equipment Space (110.26(E)): This is about protecting the equipment itself from foreign interference not related to the electrical installation. Key points: Above the Equipment (110.26(E)(1)(a)): This is your problem area. 110.26(E)(1)(a) is clear: The dedicated space shall extend from the top of the equipment to a height of 6 ft above the equipment or to a structural ceiling, whichever is lower. The issue: The code prohibits foreign systems within this zone: The entire space directly above the transformer, extending to a height of 6' above or to the ceiling, shall be dedicated to the electrical installation. No piping, ducts, or other equipment foreign to the electrical equipment...shall be located in this zone. Enforcement: The 6' rule is strictly enforced by inspectors.

Your Situation and the Answer

You want to mount the transformer 5' off the floor. Let's assume the transformer itself is 2' tall for calculation purposes (you'll need to use the actual height).
The top of the transformer will be at 7' above the floor. The dedicated space extends 6' above the transformer, so to 13' above the floor. Your ceiling is only 5' above the top of the transformer, or 12' above the floor. The unrelated conduits are within that dedicated space.

Conclusion: No, you
cannot mount the transformer in that location as planned. The conduits violate the dedicated equipment space requirements. The ceiling height does not matter, as the height of the conduits is the determining factor.

Recommendations1. Relocate the Transformer

This is the most straightforward solution. Find a spot where there are no obstructions (conduits, pipes, etc.) within the 6' dedicated space.2.

Reroute the Conduits

If possible, have the conduits rerouted
outside of the dedicated space. This might be costly.3.

Elevate Transformer to a Higher Point

This does not help because the 6' dedicated space above will still be where the existing conduit is.

Important Notes
Local Amendments

Always check with your local electrical inspector or Authority Having Jurisdiction (AHJ) for any local amendments to the NEC. Some jurisdictions have specific interpretations or requirements.

Drawings

It's always a good idea to provide drawings to the inspector showing the proposed installation and demonstrating compliance with Code. This can prevent misunderstandings and potential delays.


Manufacturer's Instructions:
Always follow the transformer manufacturer's installation instructions as well.By carefully considering both working space and dedicated equipment space, and keeping your AHJ informed, you can ensure a safe and Code-compliant installation. Good luck! Flag for review

Previous Question Next Question