Question: Optical Fiber Nonconductive Riser is being used a several locations at this site but the data sheet does not show a UL Listing… the vendor is stating the OFNR makes it UL listedDoes anyone have experience with this issue?
You're right to question this. Here's the breakdown: OFNR IS NOT a UL Listing. OFNR stands for Optical Fiber Nonconductive Riser. It's a type of cable that's been tested to meet specific flammability standards suitable for use in vertical runs (risers) within buildings. It's a performance rating. UL Listing IS a specific certification from Underwriters Laboratories (UL). UL independently tests and certifies products to meet their safety standards. A UL Listing is a mark that signifies the product has passed those tests and meets those standards. OFNR is a Requirement that helps meet UL Listing OFNR is a cable rating designed to help the cable itself adhere to the UL regulations OFNR Doesn't Guarantee UL Listing
Just because a cable is OFNR does not automatically mean it is UL Listed. The manufacturer still needs to submit the cable to UL for testing and certification.
Confusing Terminology
Sometimes vendors use the terms loosely, or they might assume because the cable meets OFNR requirements, it's automatically UL Listed. This is incorrect.
Here's what you need to do
Demand Proof
Tell the vendor that you need to see the actual UL Listing for the specific cable they're providing. This should include a UL file number and/or a UL mark directly on the cable jacket.2.
Check the Cable Jacket
Examine the cable jacket itself very closely. A UL Listed cable will typically have the UL logo (usually a small circle with "UL" inside) and a file number printed on the jacket. It should also specify the cable type (e.g., OFNR) and other relevant information.3.
Search the UL Database
If the vendor provides a UL file number, you can search the UL Product iQ database (productiq.ul.com) to verify the listing. This will tell you exactly what standards the cable is certified to meet.
Why This Matters
Safety
UL Listings are critical for building safety. They ensure that electrical and optical cables meet minimum flammability and safety requirements, minimizing the risk of fire and smoke propagation.
Code Compliance
Building codes (like the National Electrical Code - NEC) often require or highly recommend UL Listed products for certain applications. Using a non-listed cable where a listed cable is required can result in code violations and potential fines.
Insurance
Your building's insurance policy might require UL Listed products to be used in the electrical and data infrastructure. Using non-listed products could jeopardize your coverage in the event of a fire or other incident.
In Summary:
Do not accept the vendor's claim that OFNR "makes it UL Listed." Demand proof of UL Listing. If they can't provide it, find a different cable that has proper UL certification. Flag for review