Topic: Emergency generator question

User: hhsting, Location: Glen bunie, md, us

Asked on: Wednesday, September 11, 2024 at 5:06 pm EDT
Answered on: Thursday, March 6, 2025 at 2:19 am EST

Question: I have drawings that say emergency diesel generator that says has 22 hour 660 gallon sub base tank.I want to verify if 22 hours 660 gallon sub base tank is per code. Does NEC 2017 say anything regarding how long should the generator run in hours etc?

The NEC (National Electrical Code) does not specify a minimum runtime or fuel tank size for emergency generators. The NEC primarily focuses on the safe installation and wiring of electrical systems, including emergency generators. It ensures that the generator is properly connected, grounded, and protected.

Why the NEC Doesn't Specify Runtime



Application-Specific

Emergency power requirements vary significantly based on the type of facility and its needs. A hospital has drastically different backup power requirements compared to a small office building.


NFPA 110 is the Key Standard

The standard for emergency and standby power systems and what is referenced in the NEC for emergency systems is

NFPA 110, Standard for Emergency and Standby Power Systems
. This is what you need to consult. Building Codes and Other Standards

The required runtime for an emergency generator is usually dictated by building codes, occupancy classifications (hospitals, data centers, etc.), and other relevant standards.

Where to Find the Required Runtime


NFPA 110

This standard is the most relevant.

NFPA 110 specifies different classes of emergency power supply systems (EPSS) based on the required reliability and runtime.
For example, Class X may require a certain number of hours of operation. This is the most critical document for your needs. Check the
required class in the building codes for the specific occupancy.2. Building Codes (IBC, etc.)

Your local or state building codes often reference NFPA 110 or have their own specific requirements for emergency generator runtime based on occupancy type.3.

NFPA 99 (Health Care Facilities)

If the generator is for a healthcare facility, NFPA 99 will have very specific requirements.4.

Local Amendments and Ordinances

Be sure to check for any local amendments or ordinances to the building codes, as these can sometimes add or modify requirements.5.

Authority Having Jurisdiction (AHJ)

The AHJ (typically the building inspector or fire marshal) has the final say on code compliance. Consult with them if you have any questions.

How to Verify the 22-Hour Runtime and 660-Gallon Tank


Determine the Required Class

Based on the building type and occupancy, determine the
required class of emergency power system based on the applicable standards (likely NFPA 110 referenced by your building code). The class will dictate a minimum runtime requirement in hours.2.

Calculate Fuel Consumption



Obtain Generator Fuel Consumption Data

Find the fuel consumption rate (gallons per hour) of the specific diesel generator model at its expected load. This data is available from the generator manufacturer (datasheets, manuals).

Calculate Total Fuel Needed

Multiply the required runtime (in hours) by the fuel consumption rate (gallons per hour) to determine the total gallons of fuel needed.


Compare to Tank Size

Compare the calculated total fuel needed to the 660-gallon tank capacity. Does the tank have sufficient capacity? Don't forget to include a safety factor.3.

Consider Safety Factors

It's always a good practice to include a safety factor when calculating fuel requirements. This accounts for: Slight variations in fuel consumption rate. Potential delays in refueling. Unforeseen extended power outages. Aging of the fuel.

Example Scenario

Let's say the building code requires a Class X EPSS according to NFPA 110, and for this type of building, Class X requires a 24-hour runtime. You find the generator's fuel consumption rate at the expected load is 25 gallons per hour. Total fuel needed: 24 hours 25 gallons/hour = 600 gallons. The 660-gallon tank has enough capacity theoretically.

However
: You would want to add a safety factor. A 10% safety factor would require 660 gallons of fuel, so your 660 gallon tank would be adequate. Crucially, you also have to account for the usable fuel in the tank. Tanks are not typically designed to completely empty due to sediment and other issues. Check the manufacturer's specifications on the tank for usable volume.

In Conclusion

The 22-hour runtime and 660-gallon tank size for your emergency diesel generator are not directly dictated by the NEC. You need to consult

NFPA 110
, your local building codes, and other relevant standards (like NFPA 99 if applicable) to determine the required runtime. Then, calculate the required fuel capacity based on the generator's fuel consumption and add a safety factor. Finally, compare the calculated fuel requirement to the tank size to ensure it meets the code requirements. Flag for review