Question: Using a portable generator for backfeed the house when we lost power, Using a interlock and a 50 amp twist cord,what we have to do with the generator?most of the generator are bounded, I understand what code is saying regarding of first means of disconnect,I have 3 different type of gen all bounded, I never took out the jumper betwen ground and neutral on generator and everything work fine, all afci,gfci work good, spoke with multiple electricians most of them are not touching the gen,

You're right, this is a common and often confusing topic. Let's break down the issues with using a bonded neutral generator with an interlock kit and what might be happening in your setup.

Understanding the Problem: Bonded vs. Floating Neutrals Bonded Neutral (Typical Portable Generators)

In most portable generators, the neutral conductor is
bonded (connected) to the generator's frame and grounding conductor at the generator itself. This creates a single point of grounding.

Floating Neutral (Required for Code Compliance with Interlocks)

When you're using a transfer switch or interlock kit to backfeed your house, your house's main panel becomes the primary grounding point. You only want one neutral-to-ground bond in the system. If the generator's neutral is also bonded, you create a parallel neutral path.

Why Parallel Neutral Paths are a Problem
1. Circulating Current

Current will flow through both the intended neutral path (through the utility transformer) and the ground path back to the generator.2.

Nuisance Tripping

This circulating current in the ground wire can cause: GFCI outlets and breakers to trip unexpectedly. AFCI breakers to trip unexpectedly.3.

Safety Hazard

The ground path is not designed to carry significant current continuously. It can overheat, potentially creating a fire hazard. Also, metal enclosures might become energized.4.

Incorrect Voltage Readings

Some electrical devices might not function correctly due to incorrect or unstable voltage readings.

Why Your System Seems to Work (But Might Be Dangerous)


You said everything seems to be working, but AFCI and GFCI outlets are all okay. There are a few reasons why this might be happening, even though it's generally not safe or code-compliant: Low Generator Load

If you're running a very light load on the generator, the circulating current in the ground path might be small enough not to immediately cause problems.


Short Runs/Good Connections

If the wiring between the generator and the house is short, and all connections are tight and clean, the resistance in the ground path might be low enough that the circulating current is somewhat limited (but still present).

Tolerance of Devices

Some GFCI and AFCI devices have tolerances, and the circulating current might be just below the threshold that causes them to trip. This is not a guarantee of safety.


Luck

You might simply be getting lucky, and a combination of factors is preventing immediate issues. However, the potential for problems remains.

What You Should Do (The Safe and Compliant Approach)
1. Determine if Your Generator is Truly Bonded



Consult the Owner's Manual

The generator's manual should explicitly state whether the neutral is bonded to the frame.


Visual Inspection (If You're Comfortable and Know What You're Doing)

Locate the neutral terminal inside the generator's outlet box. See if there's a wire connecting it directly to the frame.

Continuity Test (Recommended)

Use a multimeter to test for continuity between the neutral terminal and the generator frame. If you have continuity, the neutral is bonded. Make sure the generator is OFF and unplugged when performing this test.2.

If the Neutral is Bonded, You
Should Float the Neutral (Remove the Bond)



Important Note

This is the most critical step, and it must be done correctly.

Consult the Owner's Manual

Many generator manuals have instructions on how to disconnect the neutral-to-frame bond. Look for a specific procedure.


Typical Procedure (If No Specific Instructions)



Disconnect the Generator

Turn it off and unplug it completely.


Locate the Bond

Open the generator's control panel. The bond is usually a wire (often green or bare) connecting the neutral terminal to the generator frame.

Disconnect the Bond

Carefully disconnect the wire from either the neutral terminal or the frame. Insulate the disconnected end(s) of the wire with electrical tape.


Verify

Use a multimeter to verify that there is no continuity between the neutral terminal and the generator frame after disconnecting the bond.3.

Use a Grounding Rod (Recommended for Portable Generators)

Even with a floating neutral, it's good practice to drive a grounding rod near the generator and connect the generator's grounding terminal to the grounding rod. This provides a direct path to earth for fault currents, improving safety. You can purchase grounding rod kits at most hardware stores.

Why Electricians Avoid Generator Connections


Electricians often avoid working on generator connections for several reasons:
Liability

Generator connections can be complex, and if something is done incorrectly, it can create a significant safety hazard and potential liability for the electrician.

Code Changes

The National Electrical Code (NEC) has changed over the years regarding generator connections, and some electricians may not be up-to-date on the latest requirements.


Unknowns

The electrician may not know the specifics of your generator model or the quality of the wiring in your home.

Important Safety Considerations
Carbon Monoxide (CO)

Generators produce deadly carbon monoxide.
Never run a generator indoors or in an enclosed space. Place the generator outdoors in a well-ventilated area, away from windows and doors. Install carbon monoxide detectors in your home and test them regularly.

Fuel Storage

Store gasoline safely in approved containers, away from heat sources and living areas.

Overloading

Do not overload the generator. Know the generator's rated wattage and only connect appliances and devices that are within that limit.

In Summary

While your system
might* seem to be working now, using a bonded neutral generator with an interlock kit is generally not safe or code-compliant. The safest and most reliable approach is to:1.

Determine if your generator has a bonded neutral.
2. If it does, disconnect the neutral-to-frame bond (float the neutral).3. Consider using a grounding rod for the generator.Disclaimer: I am an AI chatbot and cannot provide professional electrical advice. Consult with a qualified and licensed electrician for any electrical work. Electrical work can be dangerous, and improper wiring can lead to fire, shock, or electrocution. Flag for review