Question: For multi-family projects, we are seeing developers considering use of a combination units which are all in one washer / dryer. This is not a combo stacked unit but rather a single laundry appliance. Equipment datasheet indicates there is a heater internal to unit. A 5.0CuF unit power requirement is 120V, 12A. While Dwelling Unit load calculations requires laundry circuit load, it also requires a dryer circuit for an electric dryer, with minimum 5000VA or higher per nameplate rating. For projects using such combination washer/dryer, do we need to account for it as an electric dryer load (5000VA-220.54), or do we consider it as a Laundry Circuit load (220.52B) for the dwelling unit service calculation. While on a single int basis, it may not make much difference, for a good size multifamily buildings it is a significant difference in service ratings. Thoughts?
This is a great question and highlights a common point of interpretation with combo washer/dryer units. Here's my breakdown of the NEC requirements and how they apply, along with my recommendation
NEC Sections at Play:
220.52(B) Laundry Circuit Loads - Dwelling Unit(s)
This section requires a minimum 1500 VA laundry circuit for each dwelling unit. This is intended for the typical washer.
220.54 Electric Clothes Dryers – Dwelling Unit(s)
This section requires that you include the nameplate rating of the electric dryer load, but not less than 5000 VA.
Understanding the Intent
The intent of 220.54 is to account for the significant power draw of a traditional electric clothes dryer, which uses high heat for drying. The intent of 220.52(B) is to account for the electrical load of a washing machine, which is significantly lower than a dedicated electric dryer.
Analysis for the Combo Washer/Dryer
The crucial point is how the combo unit achieves drying. From your description, this sounds like a ventless heat pump dryer. Heat pump dryers use a much lower power heating element and generally draw significantly less power overall, and recycle the heat and moisture within the unit instead of venting outside.
Low-Power Drying
The 12A, 120V rating (1440 VA) suggests that the drying function does not rely on a traditional high-wattage electric resistance heater like those in standard dryers. The internal heater is likely for supplemental heating and is of a lower wattage than a traditional dryer heating element. This wattage aligns closer to a regular washing machine.
Recommendations
Given the specific characteristics of the combination washer/dryer you describe, I believe the most appropriate approach is to treat it as a
Laundry Circuit Load (220.52(B)).
Here's why:1. Lower Power Consumption
The 1440 VA power draw is closer to a standard washing machine than the 5000 VA+ demanded by 220.54 for a conventional dryer.
2.
Drying Method
The ventless heat pump drying method is fundamentally different and uses much less electricity compared to a traditional electric resistance dryer.3.
Avoiding Over-Sizing
Applying the 5000 VA rule for each dwelling unit in a multi-family building, when the actual load is much lower, will lead to significant oversizing of the service and distribution equipment. This will needlessly increase project costs.
Important Considerations and Caveats
Local AHJ Approval
This is crucial. The final decision rests with the Authority Having Jurisdiction (AHJ). Present your argument, backed by the unit's specifications, to the AHJ for their acceptance. Be prepared to provide documentation showing the drying mechanism and lower power consumption.
Nameplate Rating
If the nameplate requires a higher voltage or amperage (even if it doesn't seem accurate for the functionality), the AHJ may insist on using that value.
Future-Proofing
Consider the possibility of future residents replacing the combo unit with a traditional electric dryer. If that is the case, there would have to be either a 240v receptacle for the clothes dryer.
Steps to Take
Gather Documentation
Compile the complete specifications for the combo washer/dryer, including the power requirements, drying method (specifically highlighting the heat pump or other low-power technology), and any manufacturer documentation that supports your argument.2.
Contact the Manufacturer
Reach out to the manufacturer of the combo unit and ask them for their recommendations on how to calculate the load for electrical service sizing. They may have experience with this issue.3.
Consult with the AHJ
Schedule a meeting with the local electrical inspector or building official to discuss your proposed approach. Present your documentation and explain your rationale for treating the combo unit as a laundry circuit load.4.
Document the Agreement: Obtain written approval from the AHJ for your approach. This will protect you from future issues and ensure consistency throughout the project.By taking these steps and focusing on the actual power consumption of the combo unit, you can potentially save a significant amount of money on the electrical service for your multi-family project while still ensuring a safe and code-compliant installation. Good luck! Flag for review