Topic: Fire Alarm devices for machine-less elevator and machine room elevator

User: Cartoon1, Location: Florida

Asked on: Thursday, September 12, 2024 at 11:48 am EDT
Answered on: Thursday, March 6, 2025 at 2:21 am EST

Question: My understanding for fire alarm devices for elevators. (excluding special cases). Scenario below is for 2 or 3 levels elevator.Machine-less elevator (no equipment room, equipment in hoist-way):Smoke detectors outside each elevator lobby floor for recall protocol.Smoke detector in the hoist-way for recall and flash helmet in elevator.Heat detector within 2 feet if there is a sprinkler in the hoist-way for shunt trip.Elevator with machine room:Smoke detectors outside each elevator lobby floor for recall protocol.Smoke detector in the elevator equipment room for recall and flash helmet in elevator.Heat detector in the elevator equipment room and hoist-way if sprinkler is there for shunt trip.---------------------My question isWhen are heat detectors required outside elevator lobby at different floors instead of smoke? Because i know i have seen heat detectors outside elevator lobby on different floors instead of smoke before.Is smoke detector required in the hoist-way of an hydraulic elevator with a machine room? if the elevator machine room has a smoke detector there.Thank you

You've got a good grasp of the basics of elevator recall and shutdown. Let's clarify the points you raised

When are heat detectors required outside elevator lobby at different floors instead of smoke?
Environmental Factors

Heat detectors are often chosen over smoke detectors in environments where smoke detectors are prone to false alarms. These environments might include:


Dusty areas

Construction sites, industrial areas, or even lobbies near loading docks.

High humidity

Locations near pools, spas, or in climates with consistently high humidity.


Areas prone to steam or cooking fumes

Near commercial kitchens, cafeterias, or break rooms.

Air turbulence

high wind/draft areas.


Code Variations & Local Amendments

While smoke detectors are the typical requirement, some local building codes or amendments might permit or even require heat detectors in specific lobby areas, depending on the building's occupancy and use. It's crucial to consult your local Authority Having Jurisdiction (AHJ) and the applicable building codes.

Specific Occupancies

Certain occupancies, due to their nature, may benefit from a change from smoke detector to heat detector.


Tampering Resistance

In area where there is public access, heat detectors are less prone to vandalism since there is no sampling chamber for someone to put trash or other objects into to cause alarm.

Is a smoke detector required in the hoist-way of a hydraulic elevator with a machine room if the elevator machine room has a smoke detector there?
Code Requirements and Interpretation

The requirement for a smoke detector in the hoistway of a hydraulic elevator, even with a machine room that is equipped with a smoke detector, is again largely dependent on the adopted building codes (IBC, NFPA, etc.) and local AHJ interpretations.


Machine Room Coverage

The presence of a smoke detector in the elevator machine room might satisfy the code requirements, if the AHJ deems it sufficient to detect fire within the elevator system. However, a fire in the hoistway itself could develop without immediately affecting the machine room, so it is important to assess the risk.

Hydraulic Fluid

Hydraulic elevators use oil, which presents a fire hazard. A leak in the hoistway could lead to a fire that a machine room detector might not quickly detect.


Best Practice

As a best practice, and to err on the side of safety, including a smoke detector in the hoistway is generally recommended, even for hydraulic elevators with machine rooms, unless the AHJ specifically allows an exception.

In summary



Always consult the applicable building codes and your local AHJ.
They have the final say. Consider environmental factors when choosing between smoke and heat detectors. For hydraulic elevators, even with machine room detection, consider the safety benefits of also installing a smoke detector in the hoistway.Important Considerations



Early Detection

Smoke detectors are generally preferred for early fire detection. Heat detectors require a significant temperature rise before activation.

Placement

Detector placement is critical. Follow the manufacturer's recommendations and the requirements of NFPA 72 (National Fire Alarm and Signaling Code) for spacing and location.


Maintenance

Ensure that all fire alarm devices are properly maintained and tested according to code requirements.*

Documentation:
Keep thorough documentation of all fire alarm system design decisions, including the reasons for choosing specific types of detectors.By considering these factors and working closely with your AHJ, you can ensure that the fire alarm system in and around the elevators is appropriate for the specific building and its occupants. Flag for review