Topic: Can we use 40A backfeed breaker with Powerwall3?

User: permitdesign161, Location: USA

Asked on: Thursday, September 12, 2024 at 3:42 pm EDT
Answered on: Thursday, March 6, 2025 at 2:22 am EST

Question: In Tesla Powerwall3 if we do the PCS @31.7A than can we use 40A backfeed breaker in MSP to stay within 120% rule for PG&E in San Francisco?

Let's break down the 120% rule and how it applies to your Tesla Powerwall 3 situation with PG&E in San Francisco.

Understanding the 120% Rule

The 120% rule is a guideline often used by utilities like PG&E to ensure the busbar of your main service panel (MSP) is protected from overcurrent. It essentially limits the sum of the main breaker and the backfed breaker (from the solar/battery inverter) to no more than 120% of the busbar rating. Busbar Rating

This is the maximum current the busbar in your MSP is designed to handle safely. It's usually printed on the panel's label.


Main Breaker

The main breaker protects your entire house from overcurrent conditions.

Backfed Breaker

This breaker is dedicated to feeding power back into the grid from your solar/battery system (in your case, the Powerwall 3).

The 120% Rule Formula
`(Main Breaker Ampacity + Backfed Breaker Ampacity) <= (Busbar Rating 1.20)`Your Specific Scenario: Tesla Powerwall 3 and 40A Backfeed

You're asking if a 40A backfed breaker is acceptable when your Powerwall 3's PCS (Power Conversion System) operates at 31.7A in a PG&E service area in San Francisco. Let's analyze this.
1. Powerwall 3 PCS Current

The 31.7A represents the maximum continuous output current of the Powerwall 3's inverter. This is the key number we'll use for calculations.
2.


NEC 705.12 (B) Rule (The 120% Rule)

The
NEC (National Electrical Code) Section 705.12(B) details the requirements for backfeeding power into a service panel. This is where the 120% rule is formally addressed.3.

Applying the 120% Rule



Busbar Rating is Critical

We

need to know the busbar rating
of your main service panel. Let's assume a common busbar rating of 200A for example. Let's say you have a 200A main breaker as well. Using the 120% rule with our example numbers:`(200A (Main Breaker) + 40A (Backfed Breaker)) <= (200A (Busbar) 1.20)``240A <= 240A`In this hypothetical case, the 40A backfeed would be acceptable. Important Considerations



Continuous Current

The NEC requires that overcurrent protection devices be rated at least 125% of the continuous current. This applies to the backfed breaker. 31.7A 1.25 = 39.625A. A 40A breaker would satisfy this condition.

San Francisco and PG&E Requirements

San Francisco (and PG&E specifically) may have additional requirements or interpretations of the NEC. It is best to check with your local authority having jurisdiction (AHJ), and/or PG&E.

Why the Powerwall 3 PCS Current Matters
The 31.7A is the actual continuous output current of the Powerwall 3's inverter. While you might use a 40A breaker, the continuous load on the breaker will be limited by the Powerwall's capabilities. The breaker's purpose is to protect the wiring and the Powerwall from overcurrent faults (short circuits, etc.).

Important Steps Before Proceeding1. Identify Busbar Rating

This is the most important step. Locate the busbar rating on your MSP.2.

Verify Main Breaker Size

Confirm the ampacity of your main breaker.3.

Calculate Using the 120% Rule

Plug your actual values into the 120% rule formula: `(Main Breaker + Backfed Breaker) <= (Busbar Rating 1.20)`.
4.


Consult PG&E and Your Electrical Inspector

Contact PG&E's interconnection department and your local electrical inspector
before installing the Powerwall. They can provide specific guidance based on San Francisco's regulations and your particular installation. This is crucial.5.

Licensed Electrician

Have a licensed electrician perform the installation. They are trained to comply with all applicable codes and regulations and will ensure the system is installed safely and correctly.6.

Overcurrent Protection

Remember that the breaker is sized based on 125% of the continuous current.

In Conclusion


While a 40A backfed breaker
might be acceptable based on the Powerwall 3's 31.7A continuous current and the 120% rule, you must* verify the busbar rating of your MSP and consult with PG&E and your electrical inspector. Do not proceed without their approval. Safety and compliance are paramount. Flag for review