User: mdlueck, Location: Michigan, USA
Asked on: Thursday, September 12, 2024 at 4:51 pm EDT
Answered on: Thursday, March 6, 2025 at 2:22 am EST
Question: Greetings,In Saint Joseph, MI.... the old downtown part of town I observe an unusual transformer configuration. They have AEP as their utility provider.I see two sets of secondary on the poles. One is clearly USA standard 120/240.The second set I would assume to be three phase delta 240v. However the transformer powering that bus has only a single connection to the primary, and four secondary connections. The middle two of the secondary are bonded together. Then a total of three wires connect to the bus it powers.I would suspect three phase open delta. But I am puzzled at how the utility could make three phase anything with only a single primary connection!We are in Consumers Energy territory of Michigan, and here the utility utilizes two standard 120/240 tubs to deliver three phase open delta. That configuration makes sense to me.So is the AEP configuration even delivering a type of old three phase.... or a totally different output?I am thankful,Michael Lueck
Hello Michael,That's a very interesting observation in downtown St. Joseph! Let's break down what's likely happening, considering the constraints you've observed. You're right to be skeptical of a true three-phase configuration with only a single primary connection to the transformer.
Understanding the Configuration Dual Secondaries
You're correct that the standard 120/240V secondary is providing single-phase power for most residential and small commercial needs.
Single Primary Connection
This is the key to the puzzle. A single primary connection strongly suggests that this transformer is NOT a standard three-phase transformer. Three-phase transformers inherently require at least two, and typically three, primary connections.
Four Secondary Connections with Bonded Midpoint
This is an unusual but telling detail. A standard single-phase transformer has three secondary connections: two hots and a neutral (center tap). The fact that the middle two are bonded together and then only three wires are used on the "three phase" bus implies a derived three phase circuit.
Three Wires to the "Three-Phase" Bus
This is consistent with a three-phase open delta system.
What's Likely Happening: Modified Single-Phase to Open Delta
Given your observations, here's the most plausible scenario:1. The transformer IS single-phase
Despite the apparent three-phase output, the transformer itself is fundamentally a single-phase transformer.2.
Phase Conversion Circuitry
The most plausible explanation is the single-phase transformer is serving as the feed to a phase conversion circuit. It is possible the utility may house the phase conversion circuitry local to the transformer, on the pole. There are multiple vendors of such equipment. Phase-a-matic and Ronk are but two possible suppliers.3.
Open Delta Configuration
The output side is configured as an open delta (or sometimes called a "V" configuration). One leg of the open delta is sourced directly from the converted input. The second leg, will be "X" degrees out of phase in relation to the first leg.
Why AEP Might Do This Legacy System
This configuration likely dates back to a time when three-phase power was required for specific industrial equipment in the area, but the overall demand didn't justify a full-blown three-phase distribution system.
Cost Savings
Installing a single-phase transformer and phase conversion unit is less expensive than running a full three-phase line and using dedicated three-phase transformers.
Load Balancing
Depending on the setup, the phase conversion unit could help AEP balance the load on the single-phase distribution line.
Important Considerations and Cautions Voltage Imbalance
Open delta systems inherently have a higher voltage imbalance than closed delta systems. This can be problematic for sensitive three-phase equipment.
Limited Capacity
Open delta systems are less efficient at using the available transformer capacity compared to closed delta systems.
Single-Phasing Issues
If one of the phases is lost, the system will single-phase, potentially damaging three-phase motors.
Not a True Three-Phase Source
It's crucial to remember this is NOT a true three-phase source. It's a derived three-phase source.
Further Investigation
To confirm this hypothesis, you could: Use a multimeter
Measure the voltage between each pair of wires on the "three-phase" bus. You should see three voltages, all in the 200-240 volt range and separated by approx 120 degrees. If you measure the voltage from each wire to the "neutral" ground reference, you might see something unusual. With an open delta, that neutral only references the single phase of the transformer, it doesn't reference the derived phase at all.
Use a phase rotation meter
This will confirm if the "three-phase" output is rotating in the correct sequence (A-B-C) and whether the phase angles are roughly correct (ideally 120 degrees apart).
Contact AEP: Explain your observation to AEP's engineering department. They should be able to confirm the configuration and its purpose. However, be prepared for the possibility that the person you speak with might not be familiar with this older system.I hope this detailed explanation helps! It's a fascinating electrical mystery, and I commend your keen observation skills. Flag for review