Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: transfer switch

User: jabschc, Location: Louisiana

Asked on: Thursday, September 12, 2024 at 8:25 pm EDT
Answered on: Thursday, March 6, 2025 at 2:22 am EST

Question: I have a generac RXSW200A3 transfer switch. The customer wants it mounted inside, recessed in a 2x6 wall finished with sheetrock. It will protrude out a 1/2" from the sheetrock when finished to access cover. Inspector said this is not allowable because it does not have factory knockouts and a flush mount cover. The installation manual states it can be inside, but must be mounted vertically to a rigid structure. Closest I can find in code is 314.20 Flush Mounted installation...shall not be set back more than 1/4" , shall extend to finished surface or extend past. Figured it would come down to manufacturer listing, but nothing out right allows or prohibits it. 2020 code cycle. Thoughts?

Okay, let's break this down and figure out the best approach for your situation with the Generac RXSW200A3 transfer switch and the inspector's feedback.

Understanding the Inspector's Concerns and Code 314.20 (Flush Mounted)

The inspector's primary concern stems from NEC 314.20. This section dictates the requirements for boxes (or, in this case, an enclosure performing a similar function) that are flush-mounted. It states that when installed in a combustible surface, the front edge of the enclosure or fitting shall not be set back more than 1/4 inch from the finished surface. It should also extend to the finished surface, or project beyond it. The key here is the potential for fire hazard if there's a gap behind the enclosure.


Lack of Factory Knockouts & Flush Cover

The inspector's point about "factory knockouts" and "flush cover" is related to the intent of 314.20. Boxes designed for flush mounting typically have knockouts positioned so that wiring can be brought in behind the finished wall surface. A flush cover eliminates the gap mentioned in 314.20. The absence of these things on your transfer switch is what's raising flags.

Why the Inspector's Interpretation is (Likely) Valid


While the Generac manual might not explicitly prohibit recessed mounting, here's why the inspector's interpretation is probably correct and safe to follow:1. Listing and Intended Use

The RXSW200A3 is likely

not listed
for flush mounting. The listing would be in a documentation provided by the manufacturer and the standards authority (UL, ETL, etc) that they use to test equipment. If it's not listed as suitable for flush mounting, you can't install it that way. The manual stating it can be inside is different from it being flush-mounted. Inside just means not outdoors.2. Fire Safety

Recessing a metal enclosure like the RXSW200A3 into a combustible wall cavity without the proper design features (knockouts positioned for recessed wiring, a close-fitting cover, etc.) creates a potential fire hazard. If an arcing fault occurs inside the enclosure, the heat and potential flames could ignite the wall framing.3.

Enclosure Type

Transfer switches are generally designed as surface-mounted enclosures, not recessed enclosures.

Possible Solutions and Approaches


Here's what you can do to address the situation:1. Verify Listing Information with Generac

Contact Generac's technical support. Ask specifically if the RXSW200A3 is listed for flush mounting or recessing. Get this in writing (email is fine) if possible. If they provide documentation saying it IS listed, present that to the inspector.2.

Surface Mount It (Best Option)

The simplest and safest approach is to surface-mount the transfer switch as the manufacturer intended. You might need to reroute the wiring slightly. If aesthetics are a major concern, consider:

Aesthetic Cover

Build a simple, paintable box around the transfer switch to improve its appearance. This is often easier and cheaper than trying to force a flush-mount.


Location

Choose a more discreet location for the switch.3.

Recessed Box (Less Desirable, Requires Major Modifications)

This is not recommended, but if you're really committed to a recessed look, it would involve A LOT of work and likely still fail inspection:

Remove the switch from the Generac enclosure.
This will void the UL listing. Mount the switch into a UL-listed recessed box. This must be installed so that any arc flash will be contained within the box. Ensure proper ventilation. The switch may be rated for free-air installation and could overheat when enclosed.

Key Takeaways
Follow the Listing

Always install electrical equipment according to its listing and the manufacturer's instructions.

Prioritize Safety

The NEC and the inspector's concerns are about safety. Don't compromise safety for aesthetics.


Communicate with the Inspector:
If you have questions or believe there's a misunderstanding, discuss it with the inspector. They are there to ensure a safe installation.In short, avoid the flush-mount installation. Surface mounting is the safest, easiest, and most code-compliant solution. If you must try something else, get written confirmation from Generac and be prepared to make significant modifications while ensuring all safety aspects are fully addressed. Flag for review

Previous Question Next Question