Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: voltage drop question, residential

User: Stevenfyeager, Location: United States, Indiana

Asked on: Thursday, September 12, 2024 at 9:08 pm EDT
Answered on: Thursday, March 6, 2025 at 2:22 am EST

Question: Most of my jobs requiring wire sizing due to voltage drop are a single cable going to a single load, such as a distant sub panel. My workers asked me about a lighting branch circuit in a very large house. Should we add all the lengths of NM cables on that circuit and if it totals say 150 - 200' or more, do we need to calculate the voltage drop like we do for single runs ? The lighting load is spread out, not like at the very end of a single run. Any advice ? Thank you.

Yes, you definitely need to consider voltage drop on lighting branch circuits, especially in large houses with long runs. Here's a breakdown of why and how to approach the calculation for a circuit with multiple loads

Why Voltage Drop Matters on Lighting Branch Circuits
Dimming Lights

Insufficient voltage causes lights to dim, especially incandescent bulbs. This is annoying and can shorten bulb life. LED lights are generally more tolerant but still have performance limits.


Reduced Appliance Performance

While your example is lighting, remember that receptacles on lighting circuits might be used for other loads. Low voltage can damage sensitive electronics or reduce the efficiency of motors.

Code Compliance

The NEC (National Electrical Code) has recommendations (not strict mandates) for voltage drop. While not always
required by inspection, good practice dictates keeping voltage drop within reasonable limits.

Long-Term Reliability

Consistently undervolting equipment puts a strain on it, leading to premature failure.

Calculating Voltage Drop for Multiple Loads on a Branch Circuit


The key difference from a single-load calculation is that the current is not constant throughout the entire circuit. Here's how to approach it:1. Circuit Layout and Load Identification

Carefully map the branch circuit, noting the location of each light fixture (or receptacle and expected load). A hand-drawn diagram is fine. Determine the wattage (or amperage) of each load. Be realistic. Don't just assume the maximum allowed. LEDs, for example, often use significantly less than the maximum rating of the fixture. Note the distance from the panel to the first load. Then, the distance from the first load to the second load, and so on.2.

Segment the Circuit

Divide the circuit into segments. Each segment runs between the panel and the first load, then between each subsequent load.3.

Calculate Current in Each Segment

Start at the end of the circuit (the last load). The current in the last segment is simply the current draw of that last load. Use the formula: `I = P / V` (Current = Power / Voltage) Where: `I` is current in amps `P` is power in watts `V` is voltage (typically 120V) For the second to last segment, add the current of the last load to the current of the second to last load. Continue working backward towards the panel, adding the current of each load along the way. The segment closest to the panel will have the highest current.4.

Calculate Voltage Drop in Each Segment

Use a voltage drop formula or calculator for each segment. A simplified formula for copper conductors at 75 degrees C is: `VD = (2 K I L) / CM` Where: `VD` is the voltage drop in that segment `K` is the DC resistance of copper per foot at the operating temperature. A common value is 12.9 ohms per circular mil foot for copper. `I` is the current in amps in that segment (calculated in step 3) `L` is the one-way length of the segment in feet (from the panel to the first load, or from one load to the next) `CM` is the circular mils of the conductor. For example, #14 AWG is 2080 CM, #12 AWG is 6530 CM. Many online voltage drop calculators are available. They often allow you to input the wire size, current, distance, and conductor material, and they calculate the voltage drop. They also account for temperature. Search for "voltage drop calculator NEC".5.

Calculate Total Voltage Drop

Add the voltage drop calculated for each segment to get the total voltage drop from the panel to the farthest load.6.

Calculate Percentage Voltage Drop

Divide the total voltage drop by the source voltage (e.g., 120V) and multiply by 100 to get the percentage voltage drop. `Percentage Voltage Drop = (Total Voltage Drop / Source Voltage) 100`7.

Assess Acceptability

The NEC recommends a maximum of 3% voltage drop for branch circuits and 5% total (from service entrance to the farthest load). This is a recommendation, not a hard requirement, but it's a good target. More importantly, consider the actual performance of the equipment. If the farthest light is noticeably dim, or an appliance struggles to operate, the voltage drop is too high.

Example (Simplified)


Let's say you have a circuit with three LED light fixtures: Fixture 1: 10W, 20 feet from the panel Fixture 2: 10W, 50 feet from Fixture 1 Fixture 3: 10W, 30 feet from Fixture 2Assume 120V and using #14 AWG copper wire (2080 CM).1. Currents

Fixture 3: I = 10W / 120V = 0.083A Segment 2 (Fixture 2 to Fixture 3): I = 0.083A Segment 1 (Fixture 1 to Fixture 2): I = 0.083A Segment 0 (Panel to Fixture 1): I = .083 + .083 + .083 = 0.25A2.

Voltage Drops (using the simplified formula)

Segment 0: VD = (2 12.9 0.25 20) / 2080 = 0.062 V Segment 1: VD = (2 12.9 0.083 50) / 2080 = 0.061 V Segment 2: VD = (2 12.9 0.083 30) / 2080 = 0.031 V3.

Total Voltage Drop

Total VD = 0.062 + 0.061 + 0.031 = 0.154 V4.

Percentage Voltage Drop

%VD = (0.154 / 120) 100 = 0.128%In this simplified example, the voltage drop is very low. However, if the distances were much longer or the loads much higher, it could become a problem.

Practical Considerations
Use a Spreadsheet

Set up a spreadsheet to automate the calculations. This makes it easy to change wire sizes or load values and see the impact on voltage drop.


"Worst Case" Scenario

Design for the "worst case" scenario – all lights on at their maximum wattage.

Consider Upsizing

If the calculations show you're close to the limit, it's usually best to upsize the wire one size. The cost difference is often minimal compared to the problems caused by excessive voltage drop. Going from #14 to #12 is a common and relatively inexpensive upgrade that significantly reduces voltage drop.


Split Circuits

For very large areas, consider splitting the lighting into multiple branch circuits. This reduces the current in each circuit, which in turn reduces voltage drop.

Home Runs

Running separate "home runs" from the panel to strategic locations can help distribute the load and reduce the overall length of individual branch circuits.


Verify with Measurement

After installation, use a multimeter to measure the voltage at the farthest fixture with the circuit fully loaded. This verifies your calculations.*

Software

There are electrical design software packages that automate voltage drop calculations, short circuit calculations, and other aspects of electrical design. These can be helpful for complex projects.

In summary, for large houses with long lighting branch circuits, it is crucial to perform voltage drop calculations to ensure proper performance and avoid problems. Segmenting the circuit and calculating the current in each segment is the key to accurate results.
Flag for review

Previous Question Next Question