Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Do we really need kindorf for some installations?

User: Tainted, Location: New York

Asked on: Thursday, September 12, 2024 at 9:56 pm EDT
Answered on: Thursday, March 6, 2025 at 2:23 am EST

Question: Some electrical equipment is mounted and bolted directly onto the wall without kindorf.Sometimes a kindorf is used and mounted onto a wall and then the electrical equipment is mounted onto the kindorf...Can vertical wireways be mounted onto the wall without kindorf?When is kindorf really necessary for mounting electrical equipment on the wall?

Okay, let's break down the use of Kindorf (also known as Unistrut or strut channel) for mounting electrical equipment to walls.

Can vertical wireways be mounted directly to the wall without Kindorf? Yes, generally, vertical wireways can be mounted directly to the wall, provided they meet the support requirements outlined in the NEC (National Electrical Code) and the manufacturer's instructions. The code dictates how frequently wireways need to be supported based on their size, weight, and the weight of the conductors within them.

When is Kindorf really necessary for mounting electrical equipment on the wall?

Kindorf provides a flexible and robust mounting solution. It's typically chosen when the direct mounting isn't practical, safe, or compliant with codes and specifications. Here are scenarios where Kindorf is particularly useful or required:1. Heavy Equipment/Load

Kindorf provides a much stronger and more stable platform for supporting heavy equipment than simply bolting to drywall or other less robust wall surfaces. Heavy panels, large transformers, or multiple pieces of equipment clustered together often necessitate strut.2.

Uneven Wall Surface

If the wall surface is uneven, using Kindorf allows you to create a level mounting plane for your equipment. Shimming directly behind equipment can be difficult and less reliable.3.

Aesthetics/Alignment

Kindorf allows you to precisely align multiple pieces of equipment in a clean and organized manner. It provides a consistent mounting point for everything, ensuring a professional appearance.4.

Future Expansion/Modifications

One of Kindorf's greatest strengths is its flexibility. It allows you to easily add or move equipment in the future without having to drill new holes in the wall for every change. You can simply adjust or add new mounting hardware to the existing strut.5.

Vibration/Shock Mitigation

In environments where vibration or shock is a concern (e.g., near machinery), Kindorf can be used with vibration-damping mounts to help protect the equipment.6.

Code Requirements



Support Intervals

As mentioned, NEC articles covering specific equipment (e.g., raceways, cable trays, panels) will dictate the maximum spacing between supports. If the wall studs or existing mounting points don't align with these requirements, Kindorf can be used to create a support structure that
does meet the code.

Suitable Support

The NEC requires that equipment be "securely fastened" and "adequately supported." The interpretation of "adequately supported" can vary depending on the AHJ (Authority Having Jurisdiction), but Kindorf is generally accepted as a robust and reliable support method.7.

Wall Construction/Material



Drywall/Plaster

Mounting heavy equipment directly to drywall or plaster is generally
not recommended. The screws or anchors are likely to pull out over time. Kindorf allows you to span between studs and securely attach to them, distributing the load more effectively.

Concrete Block/Brick

While you can anchor directly into concrete block or brick, Kindorf can still be advantageous. It avoids multiple holes and allows for easier alignment.8.

Corrosive Environments

Kindorf is available in various finishes (e.g., galvanized, stainless steel) that are suitable for corrosive environments. Directly bolting equipment to a wall in such an environment could lead to corrosion of the equipment and the wall itself.

Specific Examples for Wireways



Small, lightweight wireways

If the wireway is small, lightweight, and the wires within it are not excessively heavy, it may be possible to mount it directly to the wall using appropriate anchors that can handle the weight and comply with the NEC's support requirements. The manufacturer's instructions must also be followed.

Large, heavy wireways, or wireways with many conductors

These
almost certainly require Kindorf (or a similar strut system) to provide adequate support at the required intervals. Especially if running vertical. The weight of the conductors themselves will add significant load.

Key Considerations



NEC and Local Codes

Always consult the NEC and local electrical codes to ensure your mounting methods are compliant. These codes will specify support requirements for different types of equipment and raceways.

Manufacturer's Instructions

The manufacturer of the electrical equipment and the wireway will provide specific mounting instructions that
must be followed. These instructions may dictate the need for specific types of supports or mounting hardware.

Weight and Load Calculations

Accurately estimate the weight of the equipment and the conductors it will contain. Use appropriate anchors and mounting hardware that are rated for the calculated load with a safety factor.*

AHJ (Authority Having Jurisdiction)

The AHJ has the final say in whether your installation is acceptable. If there's any doubt, consult with the AHJ before starting the project.

In Summary:


Direct mounting is possible in some situations, especially with lighter equipment and when the wall construction is suitable. However, Kindorf provides a superior and more versatile solution for many applications, particularly when dealing with heavier equipment, uneven walls, future modifications, or the need to meet stringent code requirements. When in doubt, it's generally safer and more professional to use Kindorf. Always prioritize safety, code compliance, and the manufacturer's instructions. Flag for review

Previous Question Next Question