Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: 250.136 bonding a steel switch rack

User: Isaiah, Location: Baton Rouge

Asked on: Friday, September 13, 2024 at 7:08 am EDT
Answered on: Thursday, March 6, 2025 at 2:23 am EST

Question: At this site, they are insisting the metal switchbacks must be bonded to an equipotential plane that is buried approximately 18” deep. Per 250.136,I’ve told them that if the rack is bonded via the EGC to the main disconnecting means there is no need to provide an additional bond from metal rack to the so called “grounding loop”.Am I missing something here?

You are likely correct. Here's a breakdown of why, referencing the NEC (specifically 2023, but principles generally apply across recent editions)

Your Assessment is Likely Correct:
250.136 Equipment Considered Effectively Grounded

This section is key. It states that exposed noncurrent-carrying metal parts of equipment are considered effectively grounded if they are connected to the equipment grounding conductor (EGC) of the circuit supplying that equipment.


EGC and the Main Disconnecting Means

If your metal switchbacks (which I assume you are using to mount solar modules?) are bonded to the EGC, and that EGC runs back to the service equipment where it is properly connected to the grounding electrode system (GES), then your argument holds water. You've created a low-impedance path back to the source for fault current.

Redundant Grounding (The Pitfalls)

Adding another connection to a "grounding loop" (buried conductor)
can introduce problems if not done very carefully. Here's why:

Potential Ground Loops

Connecting to multiple ground points can create ground loops, which can introduce noise and unwanted current flow in the grounding system. This can be detrimental to sensitive electronic equipment. The intent is to limit ground loops to avoid creating a path for current to flow outside of the wiring system.

Voltage Differences

Even if the loop is well-installed, there can be slight voltage differences between different points in the earth. Connecting to multiple points can then create a path for circulating current.

Why the Site Might Be Insisting (And Why They Are Likely Wrong)


Misunderstanding of Equipotential Bonding vs. Grounding

They may be confusing the concept of
equipotential bonding with grounding. Equipotential bonding aims to minimize voltage differences in a specific area to protect people during a fault. While grounding helps to provide a low impedance path for fault current. For PV systems, 690.43(B) is the one of the sections where it addresses the need for equipotential bonding.
2.


Local Codes or Interpretation

There is always the chance that the local AHJ has a unique interpretation of the code, has local amendments to the code that are stricter than the NEC. This could also be driven by the engineer of record.3.

Misapplication of Other Standards

They might be misapplying concepts from other standards (e.g., telecommunications grounding or industrial grounding) that aren't directly applicable to a PV system.

What You Should Do


Review the Specs

Double-check the project specifications, drawings, and any other documents. Look for specific requirements for grounding and bonding.2.

Communicate Clearly (And Get it in Writing)

Explain your reasoning, referencing NEC 250.136 and the potential problems with unnecessary redundant grounding. Emphasize that the EGC provides the necessary grounding path.

Most importantly, get their requirements in writing.
If they are requiring this additional bonding, ask them to specify which code section requires it and how it improves safety beyond the EGC.3. Involve the Authority Having Jurisdiction (AHJ)

If the site continues to insist and you believe it's not code-compliant or is potentially creating a safety issue, involve the AHJ (electrical inspector). They have the final say on code interpretation.4.

Consider a Grounding Electrode Conductor (GEC)

While the EGC connection is likely sufficient, if you
must add a connection to earth, consider running a separate grounding electrode conductor (GEC) from the metal racks directly to the GES (grounding electrode system) at the service or separately derived system. This is generally a more controlled and code-compliant approach than simply connecting to a buried "grounding loop". But even then, make sure it's in addition to, not instead of, the EGC. And consult with the AHJ beforehand.

Important Considerations for PV Systems



690.43(B) Bonding of Metal Racks and Enclosures

This section specifically addresses bonding of metal racks and enclosures in PV systems. Make sure you are meeting these requirements.

String Inverters and Transformerless Inverters

The type of inverter used can affect grounding requirements.

In Summary:


You are likely correct. Insisting on a separate connection to a buried "grounding loop"
in addition to the EGC, and without a clear code basis or specific engineering justification*, is likely unnecessary, potentially detrimental, and may violate the code. Get the requirement in writing, and if you disagree with the interpretation, involve the AHJ. Flag for review

Previous Question Next Question