Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: URD In Conduit sizing

User: Mdsparky, Location: massachusetts

Asked on: Friday, September 13, 2024 at 8:50 am EDT
Answered on: Thursday, March 6, 2025 at 2:24 am EST

Question: I am trying to size a PVC conduit Schd 80 for two sets of 250 kcmil -3conductor URD . Would I treat each cable as 1 conductor ? or are they to be treated as six conductors ? I seem to remember cables being treated as 1 conductor using the diameter to find the area of each cable? I'm in the 2023 and it's been changed a bit . Any help would be appreciated.

You are correct; each cable assembly is treated as a single conductor.Here's the breakdown for sizing PVC conduit Schedule 80 for your application, according to the 2023 NEC, focusing on the key sections and changes you mentioned

1. Understanding the Rule:
Chapter 9, Note 9

A cable containing two or more conductors shall be treated as a single conductor for calculating percentage conduit fill area. This is the core rule that allows you to treat the URD cable as one conductor.

2. Gathering Information



URD Cable Specifications

You must obtain the actual outside diameter (OD) of the 250 kcmil, 3-conductor URD cable from the manufacturer's data sheet. Do not assume a size. URD cable dimensions can vary significantly between manufacturers.

3. Calculating the Area of the Cable

Once you have the OD, calculate the cross-sectional area of one URD cable using the formula for the area of a circle: Area = π (radius)^2. Remember radius = OD/2. Convert the area to square inches.

4. Calculating Total Conductor Area

Since you have two URD cables, multiply the area of one cable by 2.

5. Conduit Fill Percentage



Table 1, Chapter 9

For more than two conductors, the maximum conduit fill is 40%.

6. Sizing the Conduit (PVC Schedule 80)



Table 4, Chapter 9

This table provides the "Dimensions and Percent Area of Conduit and Tubing" for various conduit types and sizes, including PVC Schedule 80.

Find the Correct Table

Ensure you are looking at the
PVC Schedule 80 table.

Lookup

Locate the column for "40% Fill Area" in the PVC Schedule 80 table.

Selection

Select the smallest conduit size where the "40% Fill Area" is
greater than or equal to the total area of your two URD cables (calculated in step 4).

Example (Illustrative -
YOU MUST USE ACTUAL CABLE DIMENSIONS)

Let's
assume (for illustration only) that the 250 kcmil 3-conductor URD cable has an outside diameter (OD) of 1.5 inches.
1.


Area of One Cable

Radius = 1.5 in / 2 = 0.75 in Area = π (0.75 in)^2 = 1.767 sq. in. (approximately)2.

Total Area (Two Cables)

1. 767 sq. in. 2 = 3.534 sq. in.
3.


Consult Table 4 (Chapter 9) for PVC Schedule 80

(You need to physically look this up in the NEC). Let's say the table shows: 2" PVC Sch 80: 40% Fill Area = 2.10 sq. in. (Not enough) 2 1/2" PVC Sch 80: 40% Fill Area = 3.39 sq. in. (Not enough) 3" PVC Sch 80: 40% Fill Area = 5.02 sq. in. (Sufficient)4.

Conduit Size

You would need a 3" PVC Schedule 80 conduit in this
hypothetical example.

Important Considerations and 2023 NEC Reminders



Manufacturer's Data

I cannot stress enough: Always use the actual dimensions from the cable manufacturer's specification sheet. Do not guess.

Bends

If there are bends in the conduit run, you must follow the bending radius requirements in Chapter 3 of the NEC. This may necessitate a larger conduit size to facilitate pulling. (See Section 300.34 for raceway bends)


Pulling Lubricant

Using an approved pulling lubricant is essential, especially for long runs and multiple bends.

Derating

While conduit fill is the primary concern for sizing, don't forget to check conductor ampacity and apply derating factors if necessary (e.g., if the conductors are operating in a high-temperature environment). Although URD cable is often direct buried, running it through conduit can affect heat dissipation and require ampacity adjustments. The NEC article covering conductor ampacity adjustment for conduit fill is 310.15.


Fittings

Ensure that the fittings (couplings, connectors, etc.) are also rated for the conduit size and are suitable for the application.*

Local Codes

Always check with your local electrical inspector or authority having jurisdiction (AHJ). Local codes may have additional requirements or restrictions.

Summary:
1. Get the actual cable OD from the manufacturer.
2. Calculate the area of each cable.3. Multiply by the number of cables (2).
4. Consult Table 4 (Chapter 9) for PVC Schedule 80.5. Choose the smallest conduit size where the 40% fill area meets or exceeds your calculated total cable area.
6. Consider bends, pulling lubricant, ampacity derating, and local codes.This is a guide and not a substitute for professional electrical engineering advice. Always consult with a qualified electrical professional to ensure compliance with all applicable codes and regulations. I am an AI chatbot and cannot provide electrical code interpretations. Flag for review

Previous Question Next Question