Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: MCP instantaneous setting

User: Space, Location: Kansas

Asked on: Friday, September 13, 2024 at 9:47 am EDT
Answered on: Thursday, March 6, 2025 at 2:24 am EST

Question: Hello all, we have several Allen Bradley MCC's that control many of the plants motors. We have a 1.6A FLC motor that needs connected to an MCC bucket, the bucket has an Allen Bradley 15A MCP (Motor Circuit Protector ie. Instantaneous Trip Circuit Breaker) with instantaneous settings between 45-150A. I initially thought this MCP was too large because of it lowest instantaneous trip setting (45A) being greater than the normally allowed value of 800% FLC for the short circuit/ground fault protective device (430.52(C)(3)(b)(1).However after reading 450.52(C)(3)(b)(3) it states if the FLC of the motor is 8 amps or less, an instantaneous trip circuit breaker (MCP) with continuous current rating of 15A or less shall be permitted to be increased to the value marked on the motor controller. I don't know exactly what that means, but it seems like they are saying you can use a 15A MCP and have the instantaneous setting at a value greater than the 800% max FLC for motors <8A FLC. I just don't fully comprehend what value marked on the motor controller means.Looking for interpretations or firsthand experience if anyone has worked with MCC's / Motor Circuit Protectors. Thanks.

You've correctly identified the relevant sections of the NEC (National Electrical Code) Article 430. Let's break this down

Understanding the Issue:
Normal Rule

Normally, you size a motor's short-circuit and ground-fault protection (like an MCP) to protect the motor and prevent nuisance tripping. 430.52(C)(3)(b)(1) typically limits the instantaneous trip setting to 800% of the motor's FLC (Full Load Current). For your 1.6A motor, that would be 8
1.6A = 12.8A. A 45A minimum trip setting seems way too high based on this rule.

Exception for Small Motors

430.52(C)(3)(b)(3) provides an
exception for small motors (FLC <= 8A) when using an instantaneous trip circuit breaker (MCP) with a continuous current rating of 15A or less. It allows you to exceed the 800% FLC limit.

What "Value Marked on the Motor Controller" Means

This is the crucial part. The "motor controller" in this case is likely the
combination motor starter in your MCC bucket. The manufacturer (Allen-Bradley in your case) might have tested and listed the combination of components in the bucket (specifically, the contactor, overload relay, and MCP) to be safely coordinated even with a higher instantaneous trip setting.

Here's how to interpret it


Look for a Listing/Marking

Examine the motor starter assembly (within the MCC bucket). There should be a label or nameplate that indicates it's a listed assembly. This listing would include the catalog number of the assembled unit.2.

Allen-Bradley Documentation

Once you have the catalog number, you will need to contact Allen-Bradley/Rockwell Automation. You'll need to find documentation (specifically,
coordination tables, short-circuit current ratings (SCCR), or application notes) that specifically address this combination of components. This documentation might:

Explicitly state
that the MCP's instantaneous trip setting is acceptable for motors down to a specific FLC. Provide a table that shows acceptable instantaneous trip settings for different motor sizes, given the components used in the bucket. List a maximum motor FLC acceptable for the specified MCP and instantaneous setting.3. Coordination Studies

In some cases, larger facilities perform coordination studies. These studies analyze the entire electrical system to ensure proper protection. If such a study exists for your system, it may provide the documentation you are looking for.

Why This Exception Exists

This exception is in the NEC because:

Small motors are less prone to catastrophic failures
from short circuits that require very fast tripping. Nuisance tripping is a significant concern. Very low instantaneous trip settings can lead to frequent (and unnecessary) tripping, especially in industrial environments with voltage dips or other disturbances. Listed Combination Motor Starters

Manufacturers design and test specific combinations of motor starters (contactors, overloads, and short-circuit protection). The listing is based on coordination tests performed by independent testing agencies like UL or CSA. They determine acceptable protection schemes. If an Allen-Bradley starter is listed with a 15A MCP and higher instantaneous settings, it's been proven safe for a specific range of motors.

Important Considerations



Do NOT Exceed the Marked Value

You cannot simply arbitrarily set the instantaneous trip to any value. It must be based on the manufacturer's listing for that specific combination motor starter.

Overload Protection is Crucial

Ensure that your motor is adequately protected against overloads using the overload relay in the motor starter. The overload relay is responsible for protecting the motor from sustained overcurrents that can cause overheating and damage.


Documentation is Key

You must have documented evidence from Allen-Bradley (or Rockwell Automation) or a qualified engineer (through a coordination study) to support the use of the 15A MCP with the higher instantaneous settings.

SCCR

Verify that the entire motor starter assembly has a Short-Circuit Current Rating (SCCR) adequate for the available fault current at that point in your system. The SCCR is the maximum fault current the equipment can safely withstand.


AHJ (Authority Having Jurisdiction)

Ultimately, the AHJ has the final say on the acceptability of your installation. Be prepared to provide documentation to justify your design.

In summary

While the 45A-150A instantaneous trip setting on the 15A MCP could be acceptable for your 1.6A motor, it is

entirely dependent
on the Allen-Bradley's listed assembly information for the combination motor starter in that MCC bucket. You must find the supporting documentation to prove that this configuration is safe and compliant with the NEC. If you cannot find this documentation, you are required to use an MCP with a lower instantaneous trip setting or provide additional protection as required by the NEC. If you can't find the information, the safest route is to replace the MCP with a properly sized one (or change out the bucket entirely). If you are unsure, consult with a qualified electrical engineer. Flag for review

Previous Question Next Question