Topic: Need help with failed insulation testing results

User: diebog, Location: California

Asked on: Friday, September 13, 2024 at 7:36 pm EDT
Answered on: Thursday, March 6, 2025 at 2:25 am EST

Question: Hi all, my name is Jeremy. I have some questions about what is considered a fail when it comes to insulation testing. Our company was asked to do some testing on the insulation of the feeders that supply a privately owned eye surgery center O.R. room. We have the Fluke 1587 FC (which I highly recommend its such an awesome meter), so we tested the feeders 1 minute @1,050v phase to phase, phase to ground and phase to neutral on 5 separate sub panels ( 3 phase 208) and all feeders on these 5 panels shot up to 2.2GΩ within seconds, so all passed with flying colors. We go to test the main 400 amp feeders that route from the generator backup transfer switch (in the P.G.E utility room) to the main distribution panel (at other end of the building) During our testing, phase to ground, Phase A comes in at 2.2GΩ, Phase C at 2.2GΩ, but here is the kicker, phase B starts very low and after a minute the reading only goes up to 127MΩ. Now this test was phase to ground, but when testing Phase B to the other phases and Phase B to neutral the reading is normal and quickly goes up to 2.2GΩ. The issue is only Phase B to ground.The feeder in question is 500mcm copper, about 150ft long (rough guess). This wire is rated at 600v and we are testing for 1 minute @ 1,050v. From what I understand a min reading is 100MΩ for 600v rated wire. So just barely up at 127MΩ, is that a Pass or Fail? Ive never seen a reading on feeders so different from one another. Because Phase B is so much lower, I was thinking maybe there is a small nick in the insulation somewhere to cause the irregular reading. But is the reading low enough to warrant replacement? From what I understand this facility has never had the wire insulation test done and its been there sense the 2000's.I appreciate all your help. ThanksJeremy

Hi Jeremy,Okay, that's a good, thorough description of the problem. Let's break it down and address your questions.

Your Initial Tests

You're right, the results from the subpanels are excellent. The 2.2GΩ readings indicate very good insulation.

The Problematic 400A Feeder

This is where things get interesting. Here's how to approach this situation:

Understanding Pass/Fail Criteria



Your Understanding is Correct

For 600V-rated wire, a common rule of thumb is 1 megohm per 1000 volts of test voltage, plus 1 megohm. So for your 1050V test, 2.15MΩ is the minimum acceptable resistance. This is often used as a general guideline, but it's not the whole story.


Industry Standards

The IEEE 43-2000 (Recommended Practice for Testing Insulation Resistance of Rotating Machinery) is sometimes referenced, though it applies directly to rotating machinery windings. However, it offers valuable insights:

Polarization Index (PI) or Dielectric Absorption Ratio (DAR)

These are more sophisticated insulation tests that involve taking readings at different times and calculating the ratio. They provide a better indication of insulation quality over time, rather than just a single snapshot. Your Fluke 1587 FC can perform these.


Temperature Correction

Insulation resistance is highly temperature-dependent. Higher temperatures significantly reduce insulation resistance. So, knowing the conductor temperature during the test is crucial.

Is 127 MΩ a Pass or Fail?
Strictly Applying the Rule of Thumb

On the surface, and according to common guidelines, 127MΩ
should be a pass because its above the bare minimum of 100MΩ, and significantly higher then the 2.15MΩ calculated by the IEEE standards.

However

The significant difference between Phase B and the other phases raises serious concerns. It suggests a localized weakness in the insulation of Phase B.

Why is Phase B So Different? Possible Explanations


Localized Insulation Degradation

As you suspect, there could be a small nick, crack, moisture ingress, or area of contamination on the insulation of Phase B where it contacts ground. This could be: A point where the wire is bent sharply around a conduit fitting. A section where the wire is rubbing against the conduit. A splice (though hopefully there are no splices in a run like this). A damaged cable jacket exposing the insulation.2.

Moisture

Moisture can significantly reduce insulation resistance, especially between a conductor and ground. Even a small amount of moisture trapped near a damaged area can cause a significant drop in resistance.3.

Contamination

Chemical contamination can also degrade insulation.4.

Previous Damage

The wire might have been damaged during installation or in the past, but it's only now becoming apparent.

What To Do Next: Recommendations
1. Visual Inspection

Carefully (with the circuit de-energized and locked out) inspect the entire run of Phase B from the transfer switch to the main distribution panel. Look for: Signs of physical damage to the insulation. Areas where the wire might be rubbing against conduit or other objects. Evidence of moisture or contamination. Proper support and strain relief. Conduit damage that could allow water ingress.2.

Temperature Measurement

Take the temperature of the conductors before the test. If you use the IEEE 43 standard, use the correction factor to bring your resistance readings to the standard of 40°C.3.

Repeat the Test

Repeat the insulation resistance test on Phase B to ground. See if the value changes significantly. If it does, it could indicate moisture or contamination that's migrating.4.

Dielectric Absorption Ratio (DAR) or Polarization Index (PI) Test

Use your Fluke 1587 FC to perform a DAR or PI test on Phase B. These tests can provide a more comprehensive assessment of the insulation's condition over time. A significantly lower DAR or PI on Phase B compared to the other phases would be a strong indicator of a problem. Consult the Fluke manual for guidance on interpreting the results. You can also find more detailed guides from cable manufacturers or IEEE.5.

Investigate Termination Points

Very carefully inspect the termination points of Phase B at both the transfer switch and the main distribution panel. Look for signs of corrosion, overheating, or improper connections.6.

Meggering in Sections (If Possible)

If the cable run is accessible enough, consider disconnecting Phase B at both ends and testing it in shorter sections. This can help isolate the location of the problem. This requires
extreme caution to ensure proper lockout/tagout and safe working practices.

Judgment Call: Replace or Monitor?


This is where it gets tricky. Even though you are technically passing according to IEEE 43 standards,
the significant difference between phases should give you pause.

My Recommendation

I would lean towards recommending replacement of Phase B, especially given the critical nature of the load (surgery center O.R. room). Here's why:

Risk Mitigation

The cost of replacing the wire is likely far less than the potential cost of a failure during surgery.


Long-Term Reliability

The fact that the resistance is significantly lower than the other phases indicates that the insulation is already compromised and will likely continue to degrade.

Peace of Mind

Replacing the wire will provide peace of mind to the facility operators knowing that they have addressed a potential problem.


Alternative (If Replacement is Absolutely Not Possible)

If replacement is truly impossible due to logistical or cost constraints, then:

Implement a Rigorous Monitoring Program

Conduct regular insulation resistance tests (e.g., every 3-6 months) on Phase B to ground. Track the results over time. If the resistance continues to decrease, replacement should become a priority.


Document Everything

Carefully document all test results, visual inspections, and recommendations. Make sure the facility operators understand the risks associated with not replacing the wire.

Consider a Cable Diagnostic Test

There are more advanced cable diagnostic tests, like Partial Discharge (PD) testing, that can detect insulation defects non-destructively. These tests are more expensive and require specialized equipment, but they can provide valuable insights.

Important Considerations



Safety First

Always prioritize safety when working with electrical equipment. Follow proper lockout/tagout procedures and use appropriate personal protective equipment (PPE).

Consult with a Qualified Engineer

If you're unsure about any aspect of this testing or the interpretation of the results, consult with a qualified electrical engineer. They can provide expert guidance and help you make informed decisions.


Document Everything

Keep detailed records of all tests, inspections, and recommendations. This documentation will be valuable for future maintenance and troubleshooting.

In summary: While 127MΩ technically might be considered a pass according to some standards, the discrepancy compared to the other phases, combined with the criticality of the load, warrants a very thorough investigation and strong consideration for replacement. If replacement isn't possible, a rigorous monitoring program is essential.Good luck, Jeremy. Be safe and thorough! Flag for review