Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Multiple HVAC split system load calculation

User: 2l84me1, Location: Florida

Asked on: Friday, September 13, 2024 at 9:56 pm EDT
Answered on: Thursday, March 6, 2025 at 2:26 am EST

Question: I have 11 condensers (RLA 25.6) and 11 AHU (FLA 6.1)Do I take 1.25x 25.6 + the sum of the other condensers + the sum of all FLA on the AHUs to get 355.1 amps?

Yes, your calculation method is generally correct according to the National Electrical Code (NEC) for determining the minimum ampacity of the conductors. Here's the breakdown and some considerations

Your Calculation:
Largest Motor (Condenser)

25.6 RLA
1.25 = 32 Amps

Remaining Condensers

25.6 RLA
10 = 256 Amps

AHUs

6.1 FLA
11 = 67.1 Amps

Total

32 + 256 + 67.1 = 355.1 Amps

NEC Considerations and Refinements


NEC 440.33(A)

This section usually dictates the calculation for air-conditioning and refrigeration equipment. You take 125% of the
largest motor-compressor and add the sum of the full-load currents of all other motors (compressors, fans, etc.) and other loads. You've correctly identified the largest motor and applied the 125% factor.2.

RLA vs. FLA



RLA (Rated Load Amperes)

This is the current a compressor draws under specific rated conditions. This is the value to use for your compressor motors.

FLA (Full Load Amperes)

This is the current an electric motor draws when producing its rated horsepower at rated voltage and frequency. This is the value to use for your AHU motors.You've used RLA for condensers and FLA for AHUs, which is correct.3.

Short-Circuit and Ground-Fault Protection

This calculation provides the
minimum ampacity for your conductors. You'll also need to determine the appropriate size and type of overcurrent protection (circuit breakers or fuses). NEC Article 440 covers this in detail. It's critical to coordinate the overcurrent protection with the motor characteristics to allow starting current without nuisance tripping, while still providing adequate short-circuit and ground-fault protection.

Do not use this calculated amperage alone to size your overcurrent protection.
4. Service Factor

If any of your motors have a service factor greater than 1.15, you might need to adjust the FLA used in your calculation slightly. (Refer to NEC 430.32). Typically, the FLA is used directly.
5.


Voltage Drop

This calculation ensures adequate current-carrying capacity. You
also need to calculate voltage drop, especially for longer conductor runs. Excessive voltage drop can cause equipment malfunction and reduced lifespan.6.

Conductor Type and Ampacity Tables

You need to select the correct conductor type (e.g., THHN, XHHW) based on the environment and application, and then use the appropriate ampacity tables in the NEC (Table 310.16 and others) to determine the minimum wire gauge that can safely carry the calculated current. Derating factors (NEC 310.15) may apply if you have multiple conductors in a conduit, high ambient temperatures, etc.
7.


Neutral Conductor Sizing

Determine if the calculated load is balanced. If you have unbalanced single phase or three phase loads, you might need to increase the size of your neutral conductor.

Example (Simplified)

Let's say after considering all derating factors, your calculations show you need a conductor with a minimum ampacity of 355.1 Amps. You might find, after looking at the appropriate NEC table (e.g., Table 310.16, assuming THHN copper conductors in a conduit at 30°C), that you need a 500 kcmil conductor (which has an ampacity of 380 Amps).

Important Considerations



Licensed Electrician

This type of work must be performed by a qualified and licensed electrician. Electrical codes are complex and constantly evolving. Incorrect wiring can lead to fire, electrocution, and equipment damage.

Local Codes

Local electrical codes may be more stringent than the NEC. Always check with your local authority having jurisdiction (AHJ).


Equipment Nameplates

Always refer to the equipment nameplates for the most accurate electrical information. If a piece of equipment contains more than one motor, look for minimum circuit ampacity (MCA) and maximum overcurrent protection (MOCP) values.

Complete Load Calculation

This calculation addresses the air conditioning and AHU equipment. You will need to perform a complete load calculation for the entire building or system to account for all other electrical loads (lighting, receptacles, etc.) to determine the overall service entrance size.


Future Expansion

It is often wise to design for future expansion. Consider increasing the service entrance size to account for potential future load growth.*

Power Factor

Low power factor (especially with a large number of motors) will increase current demand. Power factor correction capacitors are sometimes installed to improve power factor and reduce overall current draw.

In summary, your initial calculation is a good starting point, but it's critical to consult the NEC, local codes, and a qualified electrician to ensure a safe and compliant installation.
Flag for review

Previous Question Next Question