Question: I manage controls in my plant and we hired local electricians to do a project for us.The project consists of 3 sections of heat tape that heat piping to move oil from a tanker to storage. We need the oil to be around 110 degrees to move around, but I can’t let it go beyond 140 degrees or the chemistry starts breaking down.I will preface this with the fact the electricians ran the power for the heat tape (220) to one location that’s about 400’ from the pipe inlet. I did show them a location for 220 where the piping begins, but for whatever reason the didn’t tap off of it. Unfortunately there was no formal scope, so I had to work with what they ran. There are three sections of heat tape, two of them are daisy chained.To control this I bought 3 Solo 4848 ( Manual ) process controllers. I am running a VFD through one controller, and heat tape through the other two ( Rough Sketch ).Controller 1Powerflex 525 may not be allowed to start unless the temperature setpoint is met. RTD run = 50’ (outdoors).Controller 2L1 of heat tape runs through a NC contact on the controller. This controllers sensor will be close to the sensor that controls the PF525. If the temperature exceeds 140’, the heat tape will lose L1 - power is cut to heat tape - which will also prevent PF525 from starting if conditions aren’t met. RTD = 400’ (outdoors)Controller 3L1 of heat tape runs through NC contact on controller. This controller is indoors, and will cut power to the last section of heat tape. RTD=50’ (indoors).What I’m afraid of is signal loss with the long run of RTD wire that goes outside. Am I right to be concerned? Is there anything I can do to avoid signal loss?
You're absolutely right to be concerned about the long RTD run for Controller 2. A 400-foot run, especially outdoors, is highly susceptible to signal degradation and noise interference. Here's a breakdown of the issues and potential solutions
Why You're Concerned (and Why You Should Be):
Resistance
RTDs rely on measuring changes in resistance. A long wire, especially if it's not a low-resistance type or if the connections are not perfect, adds significant resistance to the circuit. This added resistance can be misinterpreted by the controller as a lower temperature, leading to over-heating.
Noise Interference
Electrical noise from nearby equipment (motors, wiring, etc.) can be picked up by the long wire, corrupting the signal. This can cause erratic readings and unpredictable control behavior.
Voltage Drop
If you're using a 2-wire RTD configuration, the voltage drop across the long wire can significantly affect the accuracy of the temperature measurement.
Environmental Factors
Temperature changes, moisture, and corrosion can all affect the resistance of the wire and connections, further impacting accuracy.
RTD Wire Gauge
The gauge of the RTD wire also has an effect on resistance. Typically, RTD wire is small (22-24 AWG).
Solutions to Mitigate Signal Loss and Noise
Here's a prioritized list of solutions, from most recommended to less ideal:1.
Best Solution: Convert to 4-20mA Transmitter at the Source
How it works
Install an RTD-to-4-20mA transmitter near the RTD (at the pipe). The transmitter converts the RTD's resistance signal into a robust 4-20mA current signal. You then run the 4-20mA signal the 400 feet back to your controller.
Why it's best
4-20mA signals are much more immune to noise and voltage drop than resistance signals. The current is consistent, and the controller is just interpreting amperage. The current loop design automatically compensates for resistance changes in the wire. It's a standard industrial signal designed for long-distance transmission.
Implementation
You'll need to purchase an appropriate transmitter (loop-powered is ideal) and ensure your controller can accept a 4-20mA input (most can). You will also need an additional power supply to power the transmitter.
Wiring
The transmitter is wired to the RTD and the power supply, and a two-wire cable is run from the transmitter to the controller.
Considerations
More expensive upfront, but the accuracy and reliability gains are well worth it, especially given the critical nature of your temperature control. It's also easier to troubleshoot a 4-20mA loop.2.
Good Solution: Use Shielded Twisted Pair RTD Cable
How it works
Replace the existing RTD wire with shielded twisted pair cable specifically designed for RTD signals. The twisting helps cancel out common-mode noise, and the shielding protects the signal from external interference.
Why it's good
Significantly reduces noise and interference compared to unshielded wire. Twisted pair cable will help alleviate inductive noise. Shielded cable is more reliable for the application.
Implementation
Ensure the shield is properly grounded at one end only (typically the controller end). Grounding at both ends can create a ground loop and introduce noise.
Wiring
Use the twisted pair for the RTD signal wires. Connect the shield to ground.
Considerations
This is a good and recommended basic practice even if you implement other solutions. It won't completely eliminate noise, but it helps considerably.3.
Better Cable Management and Routing
How it works
Ensure the RTD wiring is physically separated from high-voltage power cables and other sources of electrical noise. Avoid running the RTD wire parallel to power cables. Cross them at right angles if necessary.
Why it's good
Minimizes the amount of noise that can be coupled into the RTD signal.
Implementation
Reroute the cable if possible. Use conduit to separate the RTD cable from power cables.
Considerations
Simple and relatively inexpensive, but may not be sufficient on its own for a 400-foot run in an electrically noisy environment.4.
Consider a 3-Wire or 4-Wire RTD Configuration (If Not Already Using)
How it works
3-wire and 4-wire RTD configurations compensate for lead wire resistance. The controller measures the resistance of the lead wires and subtracts it from the total resistance reading.
Why it's good
Improves accuracy by eliminating the effect of lead wire resistance.
Implementation
Ensure your controller supports 3-wire or 4-wire RTD input. Connect the RTD according to the controller's wiring diagram.
Considerations
Only works if your RTD and controller support these configurations. Doesn't eliminate noise, but improves accuracy by compensating for lead wire resistance.
Important
If you have a 4-wire RTD but are only using 2 wires, you are not getting accurate data, because there's nothing compensating for resistance in the wires.5.
Lower Value RTD
How it works
Most RTDs are PT100, meaning they have a resistance of 100 ohms at 0 degrees Celsius. RTDs can go as high as 1000 ohms at 0 degrees Celsius. By using this type of RTD, you are effectively increasing the signal strength.
Why it’s good
More signal allows for increased noise resistance.
Implementation
Ensure the RTD is compatible with your controller, as the controller will need to be configured properly.6.
(Less Ideal) Software Filtering in the Controller
How it works
Many process controllers have built-in filtering options (e.g., averaging, moving average filters). These filters can smooth out noisy readings.
Why it's less ideal
Filtering can introduce a delay in the temperature reading, which can affect the controller's response time and potentially lead to oscillations or overshooting. It's a band-aid solution, not a fix for the underlying problem.
Implementation
Consult your controller's manual for instructions on how to configure the filtering options.
Considerations
Use filtering sparingly and only after trying the other solutions. Too much filtering can make the system sluggish and unresponsive.
Addressing the Electricians' Wiring Choice
The fact that the electricians didn't use the closer 220V source is a problem. While you have to work with what you have, consider the following:
Voltage Drop on the 220V Run
A 400-foot run of 220V cable can experience significant voltage drop, especially under load. This could affect the performance of the heat tape and VFD. Have an electrician measure the voltage at the far end of the run under load to ensure it's within acceptable limits.*
Future Projects
Emphasize the importance of following agreed-upon plans and consulting with you before deviating. Clear communication and documentation are essential.
Recommendations
Implement a 4-20mA transmitter at the source of RTD 2.2. Use shielded twisted pair cable for ALL RTD runs, especially the long one.
3. Ensure proper grounding of the cable shield at the controller end only.4. Inspect and improve cable routing to minimize proximity to power cables.
5. Verify the voltage drop on the 220V run.6. Document everything! Keep detailed records of the wiring, settings, and any modifications made.By implementing these measures, you'll significantly improve the accuracy, reliability, and safety of your heat tracing system. Flag for review