Question: Hi, I’m putting in a remote sub panel for my well tanks and wanted to confirm I understand the grounding requirements correctly. I’ve installed a few before but never in a remote location.The panel will be 30a 220v and have both 110v and 220v circuits. The conduit to the panel is pvc not metal and I am pulling 8awg for the L1/L2 and N, I was going to pull 10awg for the egc. I also had 2 grounding plates put in by the remote panel when the conduit was installed.As I understand it the EGC from the main building and the grounding plates will both be connected into the sub panel ground bar which is bonded to the enclosure, the Neutral will be isolated from the ground on this remote sub panel similar to the sub panels in the main building.Do I understand this correctly?Thank you!
You're on the right track, but let's refine a few points to ensure your remote subpanel grounding is safe and code-compliant
Here's a breakdown and confirmation of your understanding:
1. Power Feed and Conductor Sizes
L1, L2 (Hot)
8 AWG is likely acceptable for a 30A circuit, but you need to confirm it's appropriate for the load you're anticipating. Calculate the total expected load on the subpanel to ensure 30A is sufficient, and that 8 AWG copper is rated to carry that current safely within the specific wiring method (e.g., conduit fill, temperature rating of the conductors).
Neutral (N)
8 AWG is typically correct, matching the hot conductor size for a balanced load.
Equipment Grounding Conductor (EGC)
This is where we need to be precise. You mentioned using 10 AWG for the EGC. The NEC (National Electrical Code) dictates the size of the EGC based on the overcurrent protective device (breaker) protecting the circuit. Since you have a 30A breaker feeding the subpanel,
NEC Table 250.122 requires a minimum of 10 AWG copper for the EGC. So, 10 AWG is the minimum. If in doubt, going up a size (to 8 AWG to match the hots and neutral) is always a safer bet.2. Grounding Electrodes (Grounding Plates)
You had two grounding plates installed at the remote subpanel location. This is excellent. These plates constitute your
grounding electrode system at the remote location. You must connect these grounding plates together to form the grounding electrode system. This is usually done with a copper conductor of appropriate size, typically run underground or in a protected manner. You'll need to consult NEC Section 250 for the exact sizing requirements of the grounding electrode conductor, but typically it's determined by the size of the service conductors. However, 6 AWG copper is often used for rod and plate electrodes, regardless of service entrance size. Crucially, these grounding plates/electrodes DO NOT replace the need for an EGC running back to the main panel. They are supplementary to it.3. Subpanel Connections
EGC Termination
The 10 AWG (or 8 AWG) EGC from the main panel will terminate on the ground bar in the remote subpanel.
Grounding Electrode Conductor (GEC) Termination
The conductor connecting your grounding plates together will also terminate on the ground bar in the remote subpanel.
Neutral Isolation
You are absolutely correct:
The neutral bar in the remote subpanel must be isolated from the enclosure and the ground bar. This is critical to prevent objectionable neutral current from flowing through the grounding system. The neutral bar should only be connected to the neutral conductor coming from the main panel.4. Enclosure Bonding
The subpanel enclosure must be bonded to the ground bar. This is usually accomplished by a bonding screw or strap that is already installed in the panel.
In Summary - To Confirm Your Understanding
Correct
You'll have an EGC (10 AWG or 8 AWG) running with the feed conductors from the main panel to the remote subpanel.
Correct
You'll have a separate grounding electrode system at the remote location (your grounding plates).
Correct
The EGC from the main panel and the grounding electrode conductor from the grounding plates both connect to the ground bar in the remote subpanel.
Correct
The ground bar is bonded to the enclosure of the subpanel.
Correct
The neutral bar in the remote subpanel is isolated from the enclosure and the ground bar.
Correct
The conduit is PVC so no need for the conduit to be used as an equipment ground
Important Considerations and Recommendations
Local Codes
Always check with your local electrical inspector or building department for any local amendments or requirements that may supersede the NEC. They have the final say.
Inspection
Absolutely schedule an electrical inspection before you energize the subpanel. This is crucial for safety and compliance.
Torque Specifications
Use a torque screwdriver or wrench to tighten all connections to the manufacturer's specified torque. Loose connections are a major cause of electrical problems.
Conduit Fill
Ensure you are not exceeding the maximum conduit fill allowed by the NEC for your type and size of conduit. This can lead to overheating and damage.
Voltage Drop
For long runs, consider checking voltage drop to ensure adequate voltage at the remote panel. A larger conductor size might be necessary. You can use online voltage drop calculators for this purpose.
GFCI Protection
Consider GFCI protection for any 120V circuits serving outdoor receptacles or equipment, as required by the NEC.*
Disconnect
Install a suitable disconnect at the remote panel for safety during maintenance and repairs.
Example Connection Scenario:1. Run your 8 AWG L1, L2, and N wires, and your 10 AWG (minimum - consider 8 AWG) EGC through the PVC conduit from the main panel to the remote subpanel.
2. Connect the grounding plates together with an appropriately sized grounding electrode conductor (likely 6 AWG copper).3. Terminate the L1, L2, and N wires on the appropriate lugs/breakers in the subpanel.
4. Terminate the EGC from the main panel AND the grounding electrode conductor from the grounding plates on the ground bar in the subpanel.5. Ensure the neutral bar is isolated from the enclosure.
6. Ensure the subpanel enclosure is bonded to the ground bar (usually pre-done).7. Check all connections for tightness and proper torque.By following these guidelines and consulting with your local electrical inspector, you can ensure a safe and code-compliant installation for your remote subpanel. Good luck! Flag for review