Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Another fundamental grounding/bonding question.

User: Isaiah, Location: Baton Rouge

Asked on: Sunday, September 15, 2024 at 9:40 am EDT
Answered on: Thursday, March 6, 2025 at 2:27 am EST

Question: We have a 480V switchgear feeding a MCC (MCB) with a 3/C 500kCMIL plus ground.The SWGR has a GEC that is routed from the SWGR grd bus to a ground rod/test well just outside the building.Does the MCC ground bus also need to be bonded directly to a grounding electrode or does the feeder with an EGC from the SWGR ground bus accomplish this?

You're asking a very common and important question about grounding and bonding. Here's the breakdown based on the NEC (National Electrical Code) and how it applies to your situation

Key Principles:
Equipment Grounding Conductor (EGC)

The 3/C 500 kCMIL plus ground is your EGC. It provides a low-impedance fault current path back to the source (the switchgear) to facilitate the operation of overcurrent protective devices (OCPDs) like breakers.


Grounding Electrode Conductor (GEC)

The GEC connects the electrical system (typically the neutral bus, but in your case, the switchgear's ground bus) to a grounding electrode (ground rod, water pipe, etc.). Its primary purpose is to stabilize the voltage to earth during normal operation and to provide a path for lightning or other transient voltage events.

Bonding

Bonding ensures all non-current-carrying metallic parts (enclosures, conduit, etc.) are electrically connected to create a low-impedance path.


Separately Derived System Considerations

A MCC is not considered a separately derived system.

Your Situation and the NEC

In your case, the feeder with an EGC from the switchgear ground bus

IS
sufficient to establish the required grounding for the MCC. The 3/C 500kCMIL feeder from the 480V switchgear IS NOT a separately derived system.

NEC Rationale

The EGC from the switchgear to the MCC is sized to handle fault currents, which is critical for safety. This connection is what ensures the OCPD will trip quickly in the event of a ground fault within the MCC.

Important Considerations



Adequate Sizing of EGC

Verify that the 500 kCMIL ground conductor is appropriately sized according to NEC Table 250.122, based on the size of the overcurrent protection device protecting the feeder.


Proper Connections

Ensure all connections are clean, tight, and properly made using listed connectors. Pay close attention to bonding the ground bus in the MCC to the enclosure.

Continuity

Verify the continuity of the grounding system from the MCC back to the switchgear.


Bonding Within the MCC

All non-current-carrying metallic parts within the MCC (enclosures, conduit, etc.) must be properly bonded to the MCC's ground bus.*

Local Amendments

Always check with your local Authority Having Jurisdiction (AHJ) for any local amendments to the NEC that might affect your grounding requirements. Some jurisdictions may have stricter requirements.

In summary:


You do not need an additional GEC from the MCC's ground bus directly to a grounding electrode. The feeder's EGC from the switchgear, along with proper bonding within the MCC, is sufficient to meet the NEC requirements for grounding your MCC in this scenario.Always consult the latest edition of the NEC and local codes for the most accurate and up-to-date information. When in doubt, consult with a qualified electrical engineer. Flag for review

Previous Question Next Question