User: James Williams, Location: Fairmont, WV, USA
Asked on: Sunday, September 15, 2024 at 10:08 am EDT
Answered on: Thursday, March 6, 2025 at 2:28 am EST
Question: I've got a UL listed 200A 1ø meter socket I will use in a feeder to an art studio building fed from my house. The feed will be #2 AL URD. It has a 100A rating at 90°C and I want to feed it from a 100A breaker.The meter socket label is not marked with a temp rating for the terminals, and the terminals (ILSCO D3845) are not marked with a rating either. The cut sheet and instructions from Siemens have no temp rating listed. I googled and found several POCOs that specify 90°C as part of their meter socket specifications. Googling ILSCO D3845 produces no relevant response.Is it OK to assume a 90°C rating?I also assume that most everything POCO-related is 90°C anyway.
You're right to be cautious and investigate this further. You're dealing with a critical part of the electrical system, and safety is paramount. Here's a breakdown of the situation and how to approach it
The Issue: Terminal Temperature Ratings
The National Electrical Code (NEC) is clear on conductor ampacity and terminal temperature ratings. NEC 110.14(C) (1) and (2) are the most relevant: (1) Equipment Provisions. The determination of equipment terminal ratings shall be based on the termination provisions of the equipment. (2) Conductor Ampacity. The ampacity of conductors shall be determined by 310.16 through 310.21 and 310.
60.However, If the terminal temperature limitations are not identified for the equipment, the following shall apply:(a) Equipment labeled for use with 14 AWG through 1 AWG conductors shall be used with conductors rated for 75°C (167°F).(b) Equipment labeled for use with conductors larger than 1 AWG shall be used with conductors rated for 75°C (167°F).Exception No. 1: Equipment listed and marked for use with a higher temperature-rated conductor shall be permitted to be used with conductors rated at the higher temperature.Exception No. 2: Conductor ampacities greater than those specified in the 75°C (167°F) column of Table 310.16 shall be permitted to be used, provided all of the following conditions are met:(1) The equipment is listed and marked for use with the higher temperature-rated conductors.(2) The ampacity of the conductors is limited to the ampacity of conductors rated for the temperature listed on the equipment.(3) The equipment is installed such that the heat generated within the equipment is dissipated.
Why You Can't Simply Assume 90°C NEC Requirement
As you can see in NEC 110.14(C)(1) & (2), In the absence of explicit marking on the equipment (meter socket and the terminals), the NEC defaults to the 75°C column in Table 310.16 for conductors larger than #1 AWG.
UL Listing Doesn't Guarantee It
A UL listing means the complete assembled device meets UL standards for safety. It doesn't automatically mean every component is rated for 90°C, especially if those components are field-installed (like the terminals). The UL listing applies to the device with specific, tested components. Substituting other terminals, even those that look similar, voids that listing.
POCO Practices Aren't Law
While many power companies might specify 90°C meter sockets, their internal standards don't supersede the NEC or your local electrical codes. They likely use sockets specifically marked for 90°C.
Steps to Take1. Contact Siemens Directly
This is the most important step. Call their technical support line. Have the model number of the meter socket handy. Ask specifically about the terminal temperature rating for use with conductors in that socket. Ask for documentation (a letter, a spec sheet, etc.) stating the rating. Explain the specific terminals you are using (ILSCO D3845) and ask if those are acceptable for use with the meter socket and a 90°C rated conductor at its full ampacity. Keep a record of your conversation (date, time, name of the person you spoke with).2.
Contact ILSCO
If Siemens is unable to answer, or if there are compatibility concerns, contact ILSCO directly. They should be able to provide data sheets or documentation for the D3845 terminal, if it exists. If you can't find data on the D3845, you may have the wrong part number. Confirm the part number, and contact ILSCO directly.3.
Consult Your Local Electrical Inspector
This is always a good idea for unusual situations. Show them your research and the responses you've gotten from Siemens and/or ILSCO. They have the final authority to approve the installation.4.
Consider Your Options if No 90°C Rating is Confirmed
Use 75°C Ampacity
This is the safest and most straightforward option. Derate the #2 AL URD conductor to its 75°C ampacity (typically 90A). You would then protect the feeder with a 90A breaker.
Find a 90°C Rated Meter Socket and Terminals
Look for a meter socket that is clearly and explicitly marked for 90°C terminals. The terminals themselves must also be marked or have documentation showing their 90°C rating. This option will likely cost more, but provides the desired 100A capacity.
Upgrade Conductor Size
If you really need 100A at 90°C, and can't confirm the terminal rating, you could upsize the conductors to a size that has a 75°C ampacity of 100A or greater. This is generally not a cost-effective solution.
Important Considerations Documentation is Key
Don't rely on assumptions or hearsay. You need written documentation from the manufacturer (Siemens, ILSCO) to support a 90°C rating.
Safety First: When in doubt, err on the side of caution. Using the 75°C ampacity is always a safe bet.In summary, don't assume a 90°C rating. Do your homework, get documentation, and consult with the manufacturer and your local electrical inspector. Good luck! Flag for review