Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: MI (mineral insulated) Cable in building stairwell

User: Grouch1980, Location: New York, NY

Asked on: Sunday, September 15, 2024 at 2:04 pm EDT
Answered on: Thursday, March 6, 2025 at 2:28 am EST

Question: Hi,I'm aware the building code in NYC (and many other jurisdictions) prohibits conduit / wiring in an egress stairwell without being enclosed in a 2 hour fire rated enclosure, unless the circuits are for loads specifically within the stairwell.If you route MI cable in the stairwell, which has a 2 hour fire rating, would this free you from needing the 2 hour rated enclosure?

You're correct about the general rule regarding electrical wiring in egress stairwells in NYC and other jurisdictions following model codes like the IBC. The intent is to prevent the spread of fire and ensure the continued functionality of critical life safety systems during a fire.Regarding MI cable in a 2-hour rated stairwell: Yes, MI cable generally is considered a fire-rated wiring method and would typically negate the requirement for an additional 2-hour enclosure.

Here's why:1. Fire Resistance

MI cable's construction (copper conductors insulated with mineral insulation, encased in a copper or stainless steel sheath) inherently provides excellent fire resistance. It is specifically designed to withstand very high temperatures and maintain circuit integrity during a fire.2.

Code Acceptance

Building codes (like the IBC) and electrical codes (like the NEC) recognize MI cable as a fire-rated wiring method. It's often listed as an acceptable alternative where other wiring methods require fire-rated enclosures. The NEC, in particular, calls out MI cable as a wiring method capable of maintaining circuit integrity under fire conditions.3.

Exception for Stairwell Loads

As you mentioned, the building code allows wiring
without a 2-hour enclosure if the circuits serve equipment solely within the stairwell (e.g., stairwell lighting, fire alarm devices within the stairwell, ventilation fans for stairwell pressurization). However, if the loads are not exclusive to the stairwell, a fire-rated wiring method or enclosure is needed.4.

Local AHJ is Key

Always confirm with the local Authority Having Jurisdiction (AHJ) (e.g., NYC Department of Buildings) to get their specific interpretation and acceptance. While MI cable is generally accepted, they may have specific requirements or interpretations. Get it in writing if possible.

Important Considerations



Proper Installation

MI cable must be installed according to the manufacturer's instructions and the NEC (National Electrical Code). Proper terminations are crucial for maintaining the fire resistance.

Support

The supports for the MI cable within the stairwell must also be fire-rated or suitable for the environment to prevent failure during a fire event. This might mean using fire-rated straps or supports designed to withstand high temperatures.


Penetrations

Any penetrations through the fire-rated stairwell walls or floors must be properly firestopped with a listed firestopping system that maintains the fire-resistance rating of the assembly.

NYC Amendments

Always consult the NYC Building Code, which may have amendments or specific requirements beyond the base IBC or NEC.

In summary:
Using MI cable in a 2-hour fire-rated stairwell generally eliminates the need for an additional 2-hour enclosure for circuits not serving stairwell-exclusive loads. However, you must* verify this with the NYC Department of Buildings or the relevant AHJ and ensure the installation meets all applicable codes and manufacturer's specifications, especially regarding support and firestopping. Don't assume; confirm. Flag for review

Previous Question Next Question