User: dhalleron, Location: Louisville, KY
Asked on: Sunday, September 15, 2024 at 4:26 pm EDT
Answered on: Thursday, March 6, 2025 at 2:28 am EST
Question: I'm a licensed Master and haven't posted here for quite a while. I only did electrical work part-time for the past 33 years. I mostly do fire alarms.I am helping someone install a 50 amp underground feeder to a garage in Indiana. I understand they are still on 2008 NEC and we probably don't need a disconnect outside the building. We installed a main lug-only panel, so I decided on a disconnect anyway. The disconnect I had lying around was 60 amp, but it only had 2 terminal screws for the ground and no place to terminate the ground rod GEC or the neutral.I don't use a supply house much anymore, since I rarely do this work. I've been looking at Home Depot, Lowes, and Menards websites. They mostly don't show enough detail to tell if a particular disconnect is suitable for my use. Also, prices are all over the board from 20 bucks to 200 bucks.Am I thinking this through correctly? Suggestions anyone? Thanks.Dale
Okay, Dale, let's break this down and get you on the right track. You're right to be thorough, especially with older code cycles.
Confirming the 2008 NEC in Indiana (Important!)
While you believe Indiana is still on the 2008 NEC, it's absolutely crucial to officially confirm this with your local electrical inspector or building department before proceeding. States, cities, and counties sometimes adopt revisions to the NEC at different times or have local amendments. Relying on outdated information can lead to re-work and potentially fines. A quick phone call is all it takes.
Your Plan & Considerations
You are on the right track with these points: 50 Amp Underground Feeder
Solid starting point.
2008 NEC (Verify!): Under the 2008 NEC, you likely don't require an exterior disconnect, if the garage meets the conditions of 225.31 and 225.
32. (Easy access from within the house, etc.). MLO Panel
Using a main lug-only panel in the garage is fine, given the planned disconnect.
Disconnect
Installing a disconnect anyway is a good safety practice, even if not strictly required by code, and you should be commended for that.
Your Disconnect Issue (The Core Problem)
You've identified the critical issue: Inadequate Grounding/Bonding in Disconnect
The disconnect you have on hand lacks sufficient terminals for grounding and bonding. This is a problem, and you can't simply ignore it or fudge it.
Understanding Grounding/Bonding Requirements (NEC 2008 - Assuming it applies)
Here's what's needed for your situation, based on the 2008 NEC and assuming it applies to your project. The main thing that is tripping you up is that there is not a place for the grounded conductor to land. It would be best to find a product that has a place to land both the grounding and grounded conductor in this case. Feeder to a Separate Building (Garage)
You're dealing with a feeder running to a separate structure.
Grounding Electrode System (Ground Rod at Garage)
You will need a grounding electrode system at the garage (typically ground rod(s)).
Separately Derived System Rules NOT in play
Since this is a feeder and not a separately derived system, 250.32 applies.
Bonding Jumper
The enclosure of your disconnect needs to be bonded.
Solutions & Recommendations
Here's what to do:1. Purchase a Suitable Disconnect
Don't try to make the existing disconnect work. It's unsafe and will likely not pass inspection. Find a 60-amp disconnect that has 3 screws, 1 for the ground from the feeder, 1 for the grounding electrode conductor to the ground rods, and 1 to bond the enclosure.2.
Don't Overthink the Brand
Any reputable brand carried at Home Depot, Lowes, or Menards is likely fine (Square D, Siemens, Eaton/Cutler-Hammer). Focus on the features and ratings. You're primarily looking for:
Amperage Rating
60 amps is acceptable for a 50-amp feeder.
NEMA Rating
NEMA 3R (rainproof) is typical for outdoor disconnects.
Terminal Configuration
Critically important: Make sure it has the terminal screws as described above.3.
Look for "Neutral Bonding Strap"
Some disconnects come with a removable neutral bonding strap that bonds the neutral to the enclosure. This must be removed in your situation (feeder to a separate building), as you only want the neutral bonded back at the service.
Step-by-Step Wiring at the Disconnect
Here's how it should be wired with the correct disconnect:1. Incoming Feeder
Connect the ungrounded (hot) conductors to the disconnect's lugs. Connect the grounding conductor from the feeder to the appropriate grounding screw on the disconnect.2.
Grounding Electrode Conductor
Run a grounding electrode conductor (size based on NEC table 250.66) from the ground rod(s) to the other grounding screw in the disconnect enclosure.
3.
Bonding
Ensure that the enclosure of the disconnect is bonded. Usually, this is accomplished by tightening the grounding screw connected to the grounding electrode conductor.4.
Outgoing Feeders to the Panel
Connect the ungrounded (hot) conductors to the disconnect's load-side lugs. Connect the grounding conductor to the panel's ground bar. Connect the neutral conductor to the neutral bus bar in the panel.
Important Considerations
Conduit Fill
Ensure your conduit fill percentages are within code limits (both for the feeder and the grounding electrode conductor).
Ground Rod Installation
Proper installation of the ground rods is crucial (spacing, depth, etc.). Consult NEC 250.53.
Wire Sizing
Ensure the feeder conductors are properly sized for the 50-amp load, based on the ampacity tables in the NEC.
Overcurrent Protection
The breaker protecting the feeder at the house must be appropriately sized (50 amps or less).*
Local Amendments
Always double-check for any local amendments to the NEC that might affect your installation.
Don't Cut Corners
Grounding and bonding are not areas where you can afford to cut corners. Incorrect grounding can create dangerous conditions. Getting the right disconnect is the key to doing this safely and correctly.Good luck with the project! Flag for review