Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Sauna trailer

User: FlatStanley, Location: Portland Oregon

Asked on: Monday, September 16, 2024 at 1:13 am EDT
Answered on: Thursday, March 6, 2025 at 2:29 am EST

Question: Hi everyone. This might be long. I have a friend who built a sauna on a 20 something foot flatbed trailer. Built out of wood with a suana and a hang out room, shower. Decent size. He asked me to do his electrical. The actual sauna is wood stove, so I don't have to worry about that. I added some plugs, a water heater and lights for him. I'm installing a outdoor 100 amp panel, with a 50 amp inlet using 6/3 romex. He's planning on using a portable generator to run everything. I have over 3 years of residential experience but have never done anything like this. So I have a few questions. How would grounding work in a situation like this? The trailer will be possibly moving around. How would I make sure everything is grounded and safe? Do i need to run ground rods or bond all the electrical to the metal? Would the panel be considered a sub since its fed from a generator? Do I need the panel to a main breaker or can I use a main lug. I know its a lot of questions, but it just becomes more confusing the more I think about it. I have little understanding on generators work. Thanks in advance.

Okay, this is a fun and slightly unusual project! Let's break it down and address your questions with safety and code considerations in mind. It's important to emphasize that this advice is based on common electrical practices and general interpretations of the NEC (National Electrical Code), but you MUST verify everything with your local electrical inspector before starting any work. They will have the final say on what's acceptable in your jurisdiction, and they are there to help ensure the installation is safe.Here's a breakdown of the key considerations

1. Grounding (This is the most important part):

This is where things get a bit tricky and why talking to your inspector is critical. The goal

The primary purpose of grounding is to provide a low-resistance path for fault current to return to the source (the generator), allowing the breaker to trip and prevent electrocution hazards.


Option 1: Trailer Frame as Grounding Electrode (Potentially problematic, check with your inspector)

In some vehicle-like situations, the metal frame can be used as the grounding electrode. However, this has specific requirements that this trailer may not meet, and there are HUGE caveats for a sauna (moisture!).

Requirements (highly likely not met with a wooden sauna on top of it)

The frame must be reliably connected to earth. This is tricky because it moves. Also, it needs to be in contact with earth. Having it on rubber tires defeats the purpose of it being the grounding electrode. Also, you can not ground anything that is not a metal frame.


How it might work (IF approved by inspector)



Bonding

The electrical panel's grounding bus (where the ground wires are connected) must be
securely bonded to the metal frame of the trailer. Use heavy gauge copper wire (at least #6 AWG) for this bond. The connection must be robust and protected from corrosion.

Reliance on Generator Grounding

The system would rely primarily on the generator's grounding. The generator must have a properly connected grounding electrode system (ground rod) when it's operating. The ground rod needs to be driven into the earth near the generator's location and connected to the generator's grounding terminal. This means the generator owner needs to be diligent about setting up the ground rod every single time the generator is used.



Important considerations if you use the trailer as the grounding electrode



Frame Integrity

The frame must be continuous and electrically conductive. Any rust, paint, or non-conductive coatings at connection points must be removed to ensure good electrical contact.

Moisture and Corrosion

A sauna on a trailer will have significant moisture. This makes corrosion a HUGE concern. All connections must be meticulously protected against corrosion with anti-oxidant compound and potentially sealed enclosures.


Safety Risks

If the generator is not grounded properly, or if the frame connection is poor, the metal parts of the sauna could become energized in the event of a fault, posing a serious shock hazard.

Option 2: Ground Rods at Each Location (Recommended and Likely Required)

This is the safer and more reliable approach.


How it works



Two Ground Rods

Install
two ground rods at least 8 feet apart at each location where the trailer will be used. These should be standard 8-foot copper or copper-clad steel ground rods.

Connect to Panel

Run a #6 AWG or larger copper wire from the ground rods to the grounding bus in the 100 amp panel on the trailer.

Generator Grounding

The generator
still needs to be grounded with a separate ground rod connected to the generator's grounding terminal.

Neutral-Ground Bond

Within the 100A panel on the trailer, you will bond the neutral and ground buses together. This creates the required single point of grounding for the system.

Why this is better

It provides a consistent and reliable ground path regardless of the trailer's location. It reduces the risk of relying on a potentially unreliable connection to the trailer frame.

Which Grounding Method to Use

Again,

talk to your inspector. They will likely prefer the ground rod method for its reliability and safety, especially given the presence of the sauna.2. Panel Configuration



Sub-Panel

Yes, the 100A panel on the trailer is considered a sub-panel because it's being fed from a generator.

Main Breaker vs. Main Lug

A main breaker is generally preferred in a sub-panel because it provides a convenient way to disconnect power to the entire trailer. It's a good safety feature. However, a main lug panel
may be acceptable if the generator has its own overcurrent protection (breaker) sized appropriately for the 50A inlet. Again, ask your inspector.

Neutral-Ground Separation (Important for Sub-Panels)

As mentioned earlier, you BOND the neutral and ground buses together in the 100A panel on the trailer.

3. Generator Considerations



Grounding

The generator MUST be properly grounded with a ground rod whenever it's in use. This is not optional.


Size and Capacity

Make sure the generator is appropriately sized for the load. Add up the wattage of all the devices that could be running simultaneously (water heater, lights, outlets with potential loads). The generator should have enough capacity to handle the peak load without being overloaded. A 50 amp inlet at 240 volts is 12,000 watts.

GFCI Protection

Consider adding GFCI protection to all 120V circuits, especially in areas where water is present (shower, sauna area).

4. Wiring and Materials



Outdoor Rated

All wiring, boxes, and fittings must be rated for outdoor use (UV resistant, waterproof).

Proper Support

Securely support all wiring runs to the trailer frame to prevent strain and damage.


Flexible Conduit

Use flexible conduit (e.g., liquidtight flexible metal conduit, LFMC) where wiring needs to flex due to movement.

Weatherproof Connections

Ensure all connections are weatherproof and protected from corrosion.

5. Safety Features



Smoke Detectors and CO Detectors

Install smoke detectors and carbon monoxide detectors inside the sauna and hangout area. These are critical for safety, especially with a wood-burning stove and potential generator exhaust.

Clearly Labeled Disconnect

The 50A inlet should be clearly labeled with a warning to disconnect power before moving the trailer.


Emergency Shut-Off

Consider an emergency shut-off switch that can quickly disconnect power to the entire trailer in case of a problem.

Summary of Steps


Consult with your local electrical inspector. Discuss the project in detail and get their approval on the grounding method, panel configuration, and any other specific requirements.2.

Choose a Grounding Method (with inspector approval). Most likely, the best and safest method is two ground rods connected to the panel grounding bus on the trailer.3.

Install the 100A Outdoor Panel

Mount the panel securely to the trailer.4.

Wire the 50A Inlet

Use 6/3 Romex (or THHN in conduit if preferred) to connect the 50A inlet to the main breaker or lugs in the panel.5.

Install Branch Circuits

Wire the plugs, lights, and water heater according to code requirements. Use appropriate wire gauge and overcurrent protection for each circuit.6.

Grounding

Connect the ground wires from all branch circuits to the grounding bus in the panel. Bond the neutral and ground bus in the panel together.7.

Ground Rods (if using)

Install two ground rods and connect them to the grounding bus in the panel.8.

Test and Verify

Once everything is wired, test all circuits to ensure they are working correctly and that the grounding system is properly connected.9.

Labeling

Label all circuits in the panel clearly.10.

Final Inspection

Call your electrical inspector for a final inspection to ensure the installation meets all code requirements.

Important Considerations



Moisture

Saunas are notoriously humid environments. Pay extra attention to protecting all electrical components from moisture and corrosion. Use outdoor-rated boxes and fittings, and consider using waterproof sealants.


Movement

The trailer will be moving, so ensure all wiring is securely supported and protected from vibration and abrasion. Use flexible conduit where necessary.

User Error:
* The biggest risk is probably user error with the generator. Educate the owner thoroughly on how to properly ground the generator every time it's used.This is a challenging project, but with careful planning, proper materials, and a thorough understanding of electrical safety principles, you can create a safe and functional electrical system for your friend's sauna trailer. Always prioritize safety and consult with your local electrical inspector to ensure compliance with all applicable codes and regulations. Good luck! Flag for review

Previous Question Next Question