Topic: 16 MOP device and a 20MOP device for a dehumidifier. Can i use 20 MOP for either?

User: Cartoon1, Location: Florida

Asked on: Monday, September 16, 2024 at 9:07 am EDT
Answered on: Thursday, March 6, 2025 at 2:30 am EST

Question: There is this dehumidifier manufacture that has 2 similar models. They are almost literally the same unit. Except one unit has a 9MCA and the other has a 12MCA. Their MOP is 16A (not sure why 16) for the first one and 20A for the second one. (it says minimum wire size #14 for both of them)I did 20A breaker with a #12. The dehumidifier starts and runs fine with no issues.My question is since we ended up going with the first model. Does this needs to be a 15A breaker now? Am i overthinking this?Thank you,

You're right to be thinking about this! Let's break down the situation and see what's what

Understanding the Terms:
MCA (Minimum Circuit Ampacity)

This is the
minimum size circuit (wire and breaker) the appliance requires for safe and reliable operation. The dehumidifier needs at least this much capacity.

MOP (Maximum Overcurrent Protection)

This is the maximum breaker size you can use to protect the appliance. It's there to prevent damage to the appliance itself in case of a fault.

Analyzing Your Situation


Model with 9MCA and 16A MOP

You bought this one. This dehumidifier needs at least a 9A circuit, but you cannot exceed a 16A breaker for protection.2.

You Installed a 20A Breaker and #12 Wire

This is designed for the second model.3.

Dehumidifier Runs Fine

While it seems to be working now, it's not properly protected according to the manufacturer's specifications.

The Problem



Over-Protection

Your 20A breaker
exceeds the MOP of 16A for the 9MCA dehumidifier. If the dehumidifier malfunctions and draws excessive current below 20A but above 16A, the breaker won't trip, and the dehumidifier could be damaged or potentially cause a fire.

The Solution

Yes, you need to change the breaker to a 15A breaker. A 15A breaker is safer because it is close enough to the 16A MOP but can also deal with the start-up amps.

Important Considerations



Wire Size

#12 wire is rated for 20A, so you're good there. You do not need to change the wiring.*

Code Compliance

Using a breaker larger than the appliance's MOP violates electrical codes, as you are putting the appliance at risk.

In summary:
You are right to be concerned. It's important to have the right breaker size to protect the dehumidifier properly. Swap that 20A breaker for a 15A breaker, and you'll be in good shape with the existing #12 wiring. Flag for review