Topic: Running a 24kw Generac with no ATS

User: jraymond, Location: Traverse City, MI

Asked on: Monday, September 16, 2024 at 9:23 am EDT
Answered on: Thursday, March 6, 2025 at 2:30 am EST

Question: Hi everyone. I have a customer that only has a pole barn on his property, no utility power hooked up. He wants to know if he can run the pole barn with a 24kw generator. My question is: can I legally hook up this generator to his panel to feed his pole barn with no automatic transfer switch and he can just turn his generator on and off manually to run his pole barn?

Okay, let's break down the legality and safety considerations of connecting a 24kW generator to your customer's pole barn without an automatic transfer switch.

The Short Answer: Generally No, and Highly Discouraged.

While it might be technically possible in some limited jurisdictions, it's overwhelmingly illegal and unsafe to directly connect a generator to a building's electrical panel without a proper transfer switch. It presents significant safety hazards and code violations.

Here's Why


Backfeeding

This is the biggest and most dangerous issue. Connecting a generator directly to the panel without a transfer switch can send power back into the utility grid. This is called "backfeeding."

Danger to Utility Workers

Backfeeding creates a lethal hazard for utility workers who may be working on the lines, assuming they are de-energized. They could be electrocuted.


Damage to Generator and/or Utility Equipment

The generator is not designed to power the grid. Backfeeding can damage the generator, transformers, and other utility equipment.

Liability

You, as the electrician, and the homeowner would be liable for any injury or damage caused by backfeeding.2.

Code Violations

The National Electrical Code (NEC), which is adopted in most jurisdictions,
requires a transfer switch when connecting a generator to a building's electrical system. Specific sections of the NEC will vary depending on the edition in force in your area, but the requirement for a transfer switch is very standard. The main goal is to prevent interconnection of the generator and utility power.3.

Improper Grounding and Neutral Bonding

A generator used as a separately derived system has specific requirements for grounding and neutral bonding. Connecting it directly to the panel without a transfer switch can create dangerous ground loops or improper grounding, increasing the risk of electric shock.4.

Overloading the Generator

Without proper load management (which a transfer switch can facilitate), the homeowner could easily overload the generator, causing it to shut down, damage equipment, or even start a fire.5.

Manual Switching is Not Reliable

Relying on the homeowner to manually switch off breakers to prevent backfeeding is risky. People make mistakes, and even momentary overlap between generator power and grid power can be disastrous.

Legal Ramifications



Permits and Inspections

Any electrical work connecting a generator to a building requires permits and inspections in almost all jurisdictions. An inspector will absolutely fail an installation without a proper transfer switch.

Liability

If you install this system without a transfer switch and someone is injured or property is damaged, you could face severe legal consequences, including lawsuits and loss of your license.

Acceptable Solutions

The only safe and legal way to connect the generator is with a properly installed transfer switch. Here are the common types:


Manual Transfer Switch

This is the most economical option. It requires the homeowner to manually switch between utility power and generator power. Critically, it physically isolates the generator from the utility grid.

Automatic Transfer Switch (ATS)

This automatically switches between utility power and generator power when a power outage occurs. It provides seamless power and is the safest and most convenient option.

Additional Considerations for a Pole Barn with No Utility Power



Separately Derived System

Since the generator is the only power source, it is considered a "separately derived system." This means it needs to be grounded and bonded according to the NEC requirements for separately derived systems. This is different than a generator that supplements utility power. You need to consult the NEC for the specific requirements.

Load Calculation

Perform a proper load calculation to determine the actual power needs of the pole barn. This will help ensure the 24kW generator is adequately sized.


Fuel Supply

Consider the fuel supply for the generator. Propane or natural gas are often used for standby generators. Make sure the fuel supply is adequate for the anticipated run time.*

Generator Location and Ventilation

The generator needs to be located in a well-ventilated area and protected from the elements. Never operate a generator indoors or in an enclosed space, as this can lead to carbon monoxide poisoning.

Recommendation


Absolutely refuse
to install the generator without a transfer switch. Explain the safety hazards and code violations to your customer.2. Recommend a manual or automatic transfer switch. Discuss the pros and cons of each option with your customer.3. Perform a load calculation to ensure the generator is adequately sized.4. Obtain the necessary permits and inspections.5. Follow all applicable codes and regulations.In summary: Do not compromise on safety. A transfer switch is non-negotiable. Flag for review