Topic: Generator load shedding

User: MNSparky, Location: Minneapolis, MN

Asked on: Monday, September 16, 2024 at 11:18 am EDT
Answered on: Thursday, March 6, 2025 at 2:30 am EST

Question: We just starting selling and installing generators so excuse me if this question seems basic. I have a customer that does not want load shedding. He wants us to put in a 26kw generator to feed his 400amp service. The house is still under construction so I haven't been able to solidify what loads he's going to have so I haven't been able to do a load calc, but I'm going to guess it's going to be more than 26kw.My question is, are we required to put in load shedding or would this be a legal install? I see nothing about it in the NEC. I realize it's not the best idea.We are on the 2023 NEC here.

Okay, let's break this down. You're right, this is a common scenario, and while the NEC doesn't mandate load shedding in this specific situation, there are several key considerations and potential code implications you need to be aware of.

NEC Requirements and Considerations (2023 Edition)



Article 702 (Optional Standby Systems)

Generators installed to provide power during outages fall under Article 702.


702.4 (Capacity and Rating)

This is crucial. It states: "An optional standby system shall have adequate capacity and rating for the supply of all equipment intended to be operated at one time."

This means you need to demonstrate that the 26kW generator can handle the load the customer
intends to run simultaneously.
This is where your load calculation is absolutely necessary. "Intent" is key here. If the customer intends to use all loads at once, the generator must be sized accordingly. 702.5 (Transfer Equipment)

The transfer switch must be listed for the application and compatible with the generator and the electrical system. Make sure it's rated for the full service amperage (400A in this case).

Article 220 (Load Calculations)



Mandatory for determining the proper size of the service and feeders.
Even though it's standby power, you need to apply load calculation principles to determine if the generator is adequate. You need to use the appropriate method (Standard or Optional) based on the dwelling type and complexity of the load.

Why Load Shedding is a Good Idea (Even if Not Mandated)



Generator Overload

Running a generator beyond its rated capacity will shorten its lifespan, potentially damage it, and may void the warranty. Even short-term overloads can cause problems.

Voltage and Frequency Instability

An overloaded generator will struggle to maintain stable voltage and frequency, which can damage sensitive electronics.


Safety

Prolonged overloading can lead to overheating and potentially fire hazards.

Here's a step-by-step approach you should take


Load Calculation is Paramount

You must perform a thorough load calculation. Work with the customer to determine which loads they absolutely want to run during an outage, and which ones they can live without. Get specific: HVAC (how many units, BTU/hr or kW) Water heater (element size in watts) Refrigerator(s) Freezer(s) Lighting (estimated total wattage) Well pump (if applicable, horsepower) Sump pump (if applicable, horsepower) Electric range/oven Electric dryer Small appliances (coffee maker, toaster, microwave - estimate usage) EV charger (if applicable, amperage)2.

Explain the Risks

Clearly communicate the risks of overloading the generator to the customer. Document this communication in writing. Explain that without load shedding, they could damage the generator or be unable to run certain appliances during an outage.3.

Offer Load Shedding as a Solution

Present load shedding as a proactive measure to protect their investment and ensure reliable power. Explain the benefits:
Prevents generator overload Extends generator lifespan Maintains stable voltage and frequency Allows them to run more essential appliances consistently4.

If the Load Calculation Exceeds the Generator Capacity (Highly Likely)

You have a few options:


Upsize the Generator

This is the most straightforward solution, but also the most expensive.

Implement Load Shedding

Use a load shedding module to prioritize critical loads and shed non-essential loads when the generator approaches its capacity.


Reduce the Intended Load

Convince the customer to lower their expectations of what they can run simultaneously. This is often the least desirable option.5.

Document Everything

Keep detailed records of your load calculations, customer communications, and the final system design. This will protect you in case of future issues.

Legality

If the customer insists on a 26kW generator without load shedding, and your load calculation clearly shows that the intended simultaneous load exceeds 26kW, then

you need to decide if you are comfortable installing the system.
While the NEC may not explicitly prohibit it, you could be held liable if the generator is damaged or causes problems due to overloading. Furthermore, some inspectors may not pass such an installation if they deem it inadequate based on a reasonable interpretation of 702.4. The fact that the house is under construction and you haven't fully documented the loads makes your responsibility even higher.

In summary: Focus on a thorough load calculation. Communicate the risks of overloading the generator to the customer. Offer load shedding as a responsible solution. Document everything.* If the calculated load exceeds the generator's capacity, seriously consider up-sizing the generator or refusing the job to mitigate risk of liability.Good luck! Let me know if you have more questions as you go through the process. Flag for review