Topic: Bonding generator to building steel

User: Tannerdebo, Location: Raleigh North Carolina

Asked on: Monday, September 16, 2024 at 12:57 pm EDT
Answered on: Thursday, March 6, 2025 at 2:31 am EST

Question: I am currently wrapping up a fit up job. The building has multiple tenants with their own service disconnects. My suit I didn’t touch the service coming in to our main panel (MDP).We installed a 80kw generator. Which feeds a ATS inside. This is a separately derived system since it’s switching the neutral. I have 2 ground rods and a bonding jumper outside on the generator.On the normal side the MDP feeds a transformer that directly feeds the ATS (480 down to 208). The transformer is bonded to building steel.Last week my inspector failed me for missing my bonding from the generator to the building gec. Which is something I overlooked, it wasn’t drawn on the prints. My inspector said I can hit building steel if I can prove that the service is bonded to the building steel. If I can’t prove it then I have to bring it all the way back to the service disconnect. Unfortunately this is an older building and the grounding is tapped in a trough. And goes into the building somewhere and no one is sure where.I guess what I’m trying to ask is since my ATS is fed directly from a transformer that is bonded to steel would that be my GEC for that system or does it need to go all the way back.If there are codes that would clarify this for me I would appreciate it. I’m working on getting better about understanding the code but the grounding and bonding really trips me up.

Okay, this is a common and sometimes confusing scenario. Let's break it down and look at the applicable code sections.

Understanding Separately Derived Systems (SDS)

Since you have a generator with a switching neutral ATS, it's definitely a Separately Derived System (SDS). This means the generator is treated as its own power source, requiring its own grounding electrode system and bonding.

Key Code Sections NEC 250.30 Grounding Separately Derived AC Systems

This is the core section for understanding SDS grounding.


(A) Grounded Systems

Since your generator likely has a grounded neutral, this section applies. It requires the system grounding conductor (the one that bonds the neutral at the generator) to be connected to a grounding electrode conductor (GEC) that connects to a grounding electrode system.

(2) Grounding Electrode System Installation

This describes the grounding electrode system.


NEC 250.30 (A)(3) Location of Grounding Electrode Connection

This is the crucial section for your situation. It dictates where the GEC connection must be made.

It states that the connection to the grounding electrode must be made at the same point on the separately derived system where the grounding conductor is connected.
It provides an exception that you might be able to utilize NEC 250.68 Grounding Electrode Conductor Connections

This covers how you make your connections to grounding electrodes and building steel.


NEC 250.50 Grounding Electrode System

This section outlines what can be used as a grounding electrode system (building steel, concrete-encased electrode, ground ring, etc.).

Your Specific Scenario & Possible Solutions
1. The Problem

You're required to connect your generator's grounding electrode conductor (GEC) to a suitable grounding electrode system. The inspector wants you to tie into the building's GEC, which you can't easily trace.2.

The Transformer's Role

The fact that the transformer feeding your ATS is bonded to building steel is helpful, but it doesn't automatically make that steel your generator's GEC. The code is specific about the grounding electrode being at the SDS itself.3.

Option 1: Building Steel as the GEC (If you can prove it)
If you can PROVE beyond a reasonable doubt that the building steel is used as the service GEC, you can bond to that steel. You'd need documentation, original electrical plans, or direct visual confirmation of a connection from the service equipment to the steel. Even then, the inspector might be hesitant without solid proof.4. Option 2: Running to the Service Disconnect (The Difficult One) If you can't prove the building steel connection, the inspector is correct: you'd technically need to run a GEC all the way back to the service disconnect. This is likely impractical and expensive.5. Option 3: (MOST LIKELY THE BEST APPROACH) Using the Exception in 250.30(A)(3)

This exception allows you to connect the GEC of your separately derived system to the nearest available of the following: The nearest effectively grounded structural metal member of the structure; or The nearest available water pipe as specified in 250.52(A)(1); or The nearest available point on the building or structure grounding electrode system as specified in 250.50.

This exception is your most likely path forward.
6. How to Proceed (Using the Exception)



Document Everything

Take pictures of your connections, the route of the GEC, and anything you use as a grounding electrode (building steel, water pipe, etc.).

Bond to the Steel

Run an appropriately sized GEC (see 250.66) from the generator's neutral bonding point (where you're bonding the neutral and equipment grounding conductors at the generator) to the nearest accessible, effectively grounded structural metal member of the building
that is part of the building's grounding electrode system. This likely involves using a listed connector suitable for bonding to steel.

Water Pipe (Less Desirable)

If you cannot readily access the building steel, the nearest metallic water pipe bonded to the building’s grounding electrode system is another option.

Consult with the Inspector

Before doing anything, talk to the inspector about this approach. Explain that you're using the exception in 250.30(A)(3). Show them your plan and get their buy-in. This is the most crucial step to avoid further issues.

Important Considerations



GEC Size

The size of your GEC from the generator to the building steel is determined by 250.66, based on the size of the generator's ungrounded conductors.

Continuity

Ensure the building steel you're bonding to is truly continuous and effectively grounded. Look for evidence of it being used as part of the building's grounding electrode system.


Connections

Use listed connectors and proper bonding techniques to ensure low-impedance connections.

Documentation

Keep detailed records of all grounding and bonding connections, including wire sizes, connector types, and locations.


Bonding Jumper at the Generator

Make sure you have a proper bonding jumper (Equipment Grounding Conductor) between the generator's frame and the neutral terminal where you're making the GEC connection.

In summary, your best bet is to utilize the exception in NEC 250.30(A)(3) and bond to the nearest accessible and effectively grounded structural metal member of the building. Consult with the inspector before proceeding, and document everything carefully.