Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Are "Demand Factors" in Load Flow Studies Permitted?

User: Ekmast, Location: Wichita, KS

Asked on: Monday, September 16, 2024 at 2:22 pm EDT
Answered on: Thursday, March 6, 2025 at 2:31 am EST

Question: With NFPA 70B stipulating that Load Flow Studies be performed or reviewed every five years, I’ve been researching the requirements for conducting these studies. I’ve reviewed NEC Article 220, IEEE Std 3002.2-2018, IEEE 399-1997 (Chapter 6), and IEEE 141-1993 (Section 2.4).One observation is there seems to be a difference between a demand load study and conducting a load flow study. SKM software treats them as two distinct types of studies. Demand load studies involve loading calculations to determine the load on a system, primarily used for sizing feeders and services. The NEC provides minimal allowance for incorporating “demand factors” in an industrial setting in these studies, with the biggest exception being a 1-year/30-day meter-recorded demand for existing systems (NEC 220.87).Load flow studies, on the other hand, are more comprehensive, focusing on how load impacts the entire system, including factors such as power flow in branch circuits, source loading, voltage magnitude, voltage drop, phase angles, and more. One area of uncertainty for me is whether "demand factors" are permissible in load flow studies. Since maximum demand data is often readily available from the utility, a demand factor could potentially be derived from this for use in the load flow study. However, I’m unsure if there is an allowance for this practice.Some IEEE documents suggest that analyzing different loading levels in an electrical system is indeed permitted. For example, one document notes: “System loading demand should be considered. Both maximum and minimum loading conditions can be useful to determine the system operating limits (i.e., under- and overvoltage conditions).”From our experience, using the connected load in load flow studies almost always results in the entire system appearing to fail. However, when checked or trended with a meter, this is usually not the case.

You've accurately identified the difference between demand load studies and load flow studies and highlighted the key point of contention: the permissibility of demand factors in load flow studies. Let's break down the issue and provide some guidance

Key Differences Recap:
Demand Load Study

Purpose: Primarily for sizing feeders, services, and other equipment. Focus: Calculating the total load based on connected loads and applicable demand factors. NEC's Approach: Conservative, with limited demand factor allowances, especially in industrial settings. Emphasis on ensuring the system can handle worst-case scenarios.

Load Flow Study

Purpose: Analyzing the impact of load on the entire system, including voltage drop, power flow, equipment loading, and system stability. Focus: Understanding the system's operational characteristics under various loading conditions. Flexibility: Allows for analyzing different loading scenarios, including maximum, minimum, and typical operating conditions.

The Core Question: Demand Factors in Load Flow Studies - Is it Permissible?
Yes, it is permissible, and often necessary, to use demand factors (or load diversity factors) in load flow studies, but with significant caveats and considerations



Realistic System Representation

Using connected load
without any demand factors in a load flow study almost always results in a pessimistic and unrealistic view of the system. You are correct that in real-world situations, equipment rarely operates at its maximum rated capacity simultaneously.

Analyzing Different Loading Conditions

As you correctly pointed out with the IEEE quote, load flow studies require the analysis of different operating points. This inherently involves considering load diversity.

IEEE Support

IEEE standards implicitly support the use of demand factors by recommending the analysis of different loading scenarios. They are often used when trying to understand existing system operation.


Data Justification is Crucial

The key is

rigorous justification and documentation
of the demand factors you use. This is where the real work lies. You can't just arbitrarily apply a demand factor without a solid basis.

How to Justify and Apply Demand Factors in Load Flow Studies


Data Collection is Paramount



Utility Data

Your existing utility demand data is a good starting point but may not be detailed enough. The utility data is also a conglomerate of all the loads together which loses granularity of information.


Submetering

Install submeters on critical loads or groups of loads. This is the best way to obtain accurate demand data. Metering can also be used to track harmonics, power factor and other data points.

Equipment Specifications

Consult equipment manuals and manufacturer data sheets to understand typical operating profiles. Some equipment will give you data regarding average load and its deviation.


Process Knowledge

Engage with process engineers and plant personnel to understand how equipment is used in practice. They can provide valuable insights into duty cycles, operational sequences, and periods of peak demand.

Historical Data

Review past maintenance records, production data, and energy consumption reports to identify trends and patterns.


SCADA/PLC Data

Many industrial facilities have SCADA or PLC systems that track equipment status and energy usage. This data can be invaluable for understanding load profiles.2.

Develop Load Profiles

Based on the data you collect, create realistic load profiles for different equipment and groups of equipment. These profiles should reflect the actual usage patterns and duty cycles.3.

Derive Demand Factors

Calculate demand factors based on the ratio of the actual peak demand to the connected load.4.

Apply Diversity Factors (Groups of Loads)

When modeling groups of loads (e.g., an entire production line), you can also apply diversity factors to account for the fact that all equipment in the group is unlikely to operate at its peak simultaneously.5.

Scenario Analysis

Consider multiple loading scenarios in your load flow study:

Peak Demand

The worst-case scenario. Use conservative demand factors, focusing on critical equipment and loads that are likely to operate concurrently.


Typical Demand

The most common operating condition. Use demand factors based on historical data and typical usage patterns.

Minimum Demand

Useful for analyzing voltage rise issues.


Contingency Scenarios

Consider scenarios such as motor starting, transformer in-rush, or equipment outages.6.

Document Assumptions

Meticulously document all assumptions you make about demand factors, diversity factors, and load profiles. Explain the basis for your assumptions and the data you used to support them. This is critical for justifying your results and defending your approach.7.

Validate Results

Compare the results of your load flow study with actual system measurements. This will help you refine your model and improve the accuracy of your predictions.8.

Sensitivity Analysis

Perform sensitivity analysis to understand how the results of your load flow study are affected by changes in demand factors. This will help you identify critical loads and areas of the system that are most sensitive to load variations.

Specific Examples of Demand Factor Justification



Motors

A motor driving a pump may have a nameplate rating of 100 HP, but it may only operate at 60% of its capacity on average. A demand factor of 0.6 could be justified based on operating data. Consider the inrush for motor starting.


Lighting

Even in industrial facilities, not all lights are on at the same time. A demand factor based on occupancy and operational practices could be justified. Consider the type of lights and impact of inrush for HID and LED drivers.

Welding Machines

Welding machines have highly variable loads. Metering data or process knowledge about welding cycles can be used to derive a demand factor.


HVAC

Demand factor should reflect typical conditions.

Important Considerations



Safety Margins

While realistic modeling is important, don't compromise safety. Always maintain adequate safety margins to account for unforeseen circumstances and future load growth.


Coordination Studies

When conducting a coordination study, demand factors may not apply or be relevant.

Worst-Case Scenarios

Ensure that your system can handle worst-case scenarios, such as equipment failures or unexpected increases in demand.


Software Capabilities

Most power system analysis software packages (like SKM, ETAP, EasyPower, etc.) allow you to define different load profiles and demand factors for individual loads or groups of loads. Learn how to effectively use these features.*

NFPA 70B and NEC Compliance

Remember to consider how the demand factors you use impact compliance with NFPA 70B and the NEC. The demand factors in NEC are a minimum, and the results of a Load Flow Study might show that additional capacity is required.

In summary, the use of demand factors in load flow studies is not only permissible but often necessary to obtain a realistic representation of the electrical system. However, it is critical to use demand factors responsibly, with thorough data collection, rigorous justification, and careful documentation. Don't just apply demand factors to make the system pass; use them to create an accurate model that allows you to understand the system's behavior under various operating conditions.
Flag for review