Question: Got a service call today to a new residence that was finished in 2022.As I’m there working I start noticing several things that stand out .- Several 18 Cubic inch nail on boxes that have as many as 15 #14 conductors not counting EG’s and the device.- AC cable on basement poured walls with one strap at the top plate and one 6” above the 4” square box. Just over 6’ of dangling cable. Top strap is a plastic NM staple in the bottom of the floor joist.-As many as 5 14/2 NM cables in a 3/4” NM connector entering the panel.- Two of the boxes I opened had the equipment grounds twisted with no wire nut or crimp securing them.- #6 bare Cu GEC attached to the exposed rebar ufer with 3 clamps. (Why 3 ????) Min#4 required.These things were in just the utility room.I chuckled when I saw the Final inspection sticker.Approved.Inspectors signature was a scribble not even close to being legible.It’s a shame that the homeowner is getting this type of work on a $400K plus home.
You've walked into a goldmine of code violations! This is beyond just sloppy work; it's negligent and potentially dangerous. Here's a breakdown of the issues and what you should consider doing
Detailed Breakdown of Violations:
Overcrowded Boxes (18 cu in with 15+ #14 Conductors)
This is a severe violation of NEC 314.16. Overcrowding can lead to overheating, insulation damage, and fire hazards. Each conductor counts based on the conductor size. A device also counts.
Unsecured AC Cable
NEC 330.30 and 334.
30. AC cable (armored cable) and NM cable needs to be supported at intervals not exceeding 4 1/2 feet and within 12" of boxes. The fact that you've got over 6 feet of unsupported cable is a blatant violation. The plastic NM staple is also an improper support for AC cable. It is likely the wrong type.
Multiple Cables in a Single Connector
NEC 312.5(C), 314.17(B) generally prohibits multiple cables through a single connector unless the connector is specifically listed for that purpose. Five 14/2 NM cables in a 3/4" connector is almost certainly a violation.
Improper Grounding Connections
NEC 250.8 and 250.
148. Grounding conductors must be connected so electrical continuity is assured. Twisting grounds without a connector or crimp is not a secure, code-compliant connection. This can prevent proper fault clearing.
Undersized GEC (Grounding Electrode Conductor)
NEC 250.66 dictates the size of the GEC based on the size of the service entrance conductors. The rebar Ufer is the grounding electrode, and based on your description, the #6 copper is undersized and violates NEC 250.
66.
Excessive Clamps on Ufer Ground
This isn't necessarily a violation, but it's a clear sign of someone not knowing what they're doing. One or two appropriately sized clamps are sufficient for a proper connection. Three is redundant and suggests a lack of understanding.
Inspection Failure
The signed "approved" sticker highlights a massive failure in the inspection process.
What You Should Do
Document Everything
This is crucial.
Take detailed photographs
Capture everything – the overcrowded boxes (with covers removed), the unsecured cables, the connector with multiple cables, the ground connections, the GEC, and the inspection sticker. Photos are your best evidence.
Write a clear, detailed report
Outline each specific violation, referencing the applicable NEC code sections. Be precise.
Note the location of each violation
Make it easy to find the problems again.2.
Inform the Homeowner
Carefully and professionally explain the issues
Emphasize the safety concerns first and foremost. Explain that the work is not up to code and could pose a fire or electrical shock risk.
Show them the photos and your report
Visual evidence is powerful.
Explain the potential consequences
Discuss the risks of leaving the issues unaddressed (e.g., fire hazard, difficulty selling the house, insurance complications).
Provide options
Hire you to correct the problems
Be upfront about the scope of work and the cost.
Suggest they contact the original electrician and demand corrections
This might be difficult if the original electrician is the one who did the shoddy work.
Advise them to report the issues to the local building department/inspection authority
This is often the most effective way to force corrections and hold the original contractor accountable.3.
Consider Reporting the Violation Yourself
While it's primarily the homeowner's responsibility, you, as a licensed electrician, have a responsibility to report code violations, especially when they pose a safety hazard. This is the moral and ethical course of action. Contact the local building department/inspection authority directly. Explain the situation and provide your documentation. Be prepared to answer questions. Anonymously reporting the violations may also be an option.4.
Your Liability
Do not make any corrections without the homeowner's explicit authorization. Doing so could make you liable for the original electrician's mistakes. If you do make corrections, ensure they are 100% code-compliant. Document your work thoroughly. Cover your own back
Make sure your insurance is up-to-date and covers you for situations like this.
Important Considerations
Homeowner's Insurance
The homeowner should contact their insurance company to inform them of the situation. Depending on the policy, the insurance company may be able to assist in getting the issues corrected.
Contractor Licensing Board
Consider filing a complaint with the state's contractor licensing board against the original electrician. This can lead to disciplinary action and may help the homeowner recover damages.
Legal Counsel
The homeowner may want to consult with an attorney to explore their legal options against the original contractor and potentially the inspector.
In summary, this is a serious situation. Your priority is to inform the homeowner of the dangers and provide them with the information they need to take action. Document everything, and consider reporting the violations to the authorities. You're doing the right thing by addressing this. Flag for review