Topic: Mini Split wiring - correct breaker, AWG, and disconnect?

User: Tilopa108, Location: CA

Asked on: Monday, September 16, 2024 at 5:44 pm EDT
Answered on: Thursday, March 6, 2025 at 2:32 am EST

Question: I'm wiring a mini split, and the placard on the outdoor unit lists the following:208/230V 20.0AMINIMUM CIRCUIT AMPACITY 25.0AMax.Fuse 40.0ACan I use a 25A double pole breaker and 10 AWG? Or would that trip the breaker often? I'm confused about the 40A max fuse. Does this mean the max current the system runs at?And what size quick disconnect should I use?The distance to the panel is only about 15 feet.Thanks.

Okay, let's break down these mini-split wiring requirements and figure out the right solution for you. It's essential to get this right for safety and proper operation.

Understanding the Placard



208/230V

This means the unit is designed to operate on either 208-volt or 230-volt power, both common in the US.


20.0A

This is the Rated Load Amps (RLA) of the unit. This is the continuous current the unit is expected to draw while running normally.

MINIMUM CIRCUIT AMPACITY (MCA) 25.0A

This is the
most important number for determining the wire and breaker size. The National Electrical Code (NEC) requires that the circuit be sized to handle at least 125% of the unit's continuous load (RLA), plus any other loads on the same circuit. This calculation is already done for you.

Max. Fuse 40.0A

This is the maximum size fuse or circuit breaker you can use to protect the unit. It's there to prevent damage to the unit in case of a short circuit or other fault. It is not the normal operating current. This is a protective value, not an operational value.

Your Wiring Questions Answered


Can I use a 25A double pole breaker and 10 AWG wire?
Yes, that is the correct combination to use. The MCA is 25.0A, therefore you should use a 25A breaker. 10 AWG copper wire is rated for 30 amps, which is sufficient for a 25A circuit.2. Or would that trip the breaker often? No, a 25A breaker should not trip under normal operation. The MCA already factors in the continuous running load (RLA) and the necessary safety margin. Breakers trip when there's an overload or a short circuit. If it trips repeatedly under normal conditions, it indicates a problem with the unit, the wiring, or the breaker itself.3. I'm confused about the 40A max fuse. Does this mean the max current the system runs at? No. As explained above, the 40A is the maximum overcurrent protection allowed. It's there to protect the equipment in the event of a fault, not to define the normal operating current. You MUST NOT use a breaker larger than 40A. Using a breaker larger than specified could allow a fault to damage the mini-split unit before the breaker trips.

Quick Disconnect Size

You'll need a

60 amp
disconnect switch. Even though the circuit is only 25 amps, disconnect switches are rated for much higher amperages. A 30A disconnect switch is rated for small resistive loads and not rated for motor loads.

Important Considerations and Best Practices



Local Codes

Always check and comply with your local electrical codes. They may have stricter requirements than the NEC.


Grounding

Ensure proper grounding of the outdoor unit according to the manufacturer's instructions and local codes.

Wiring Method

Use the appropriate wiring method (e.g., conduit, cable) as required by local codes. For a short run like 15 feet, using properly secured outdoor-rated cable (like UF-B) inside conduit is a common option.


Professional Installation

If you're not comfortable working with electrical wiring, it's always best to hire a qualified electrician.

Torque

Torque all connections to the manufacturer's specifications using a torque screwdriver or wrench. Loose connections are a major cause of electrical problems.


Voltage Drop

While voltage drop is less of a concern with such a short run, it's good practice to check it, especially on longer runs.

In Summary



Breaker

25A double-pole breaker


Wire

10 AWG copper wire*

Quick Disconnect:
60AFollow these guidelines, consult local codes, and consider professional help if needed to ensure a safe and properly functioning mini-split installation. Flag for review