Topic: Breaker tripping when machine turned off.

User: The Murch, Location: Ireland

Asked on: Tuesday, September 17, 2024 at 4:47 am EDT
Answered on: Thursday, March 6, 2025 at 2:33 am EST

Question: Hi All,Recommissioning an old Control Cabinet and retrofitted it with some new control gear. I'm looking to put it back into use, however when i turn off the isolator on the Control Panel, it trips the 16A Breaker for the Socket its plugged into.Checked for Ground Faults and Short-circuits, everything seems to be fine. Isolator is 4 Pole (3Ph + N), Plug wiring looks good.Cabinet has a Siemens Simanics V20 VFD and Logo8 Controls, motor isnt running when powered down so there shouldn't be any inductive kickback. However when I E-Stop the machine before turning off the isolator, which in turn cuts power to the VFD via the branch contactor, the breaker doesn't trip.Trip Switch is a Hager ADM420c B20.Any suggestions?Thanks.

This is a tricky problem, but here's a breakdown of potential causes and troubleshooting steps, based on your observations

Understanding the Problem
Breaker Tripping on Isolator Off

This is the key symptom. It suggests a sudden change in current when the circuit is
opened. This is often indicative of capacitive discharge or a current imbalance.

No Tripping on E-Stop

This is a crucial clue. The E-Stop, by cutting power to the VFD via the contactor, seems to prevent the problem. This strongly points to the VFD or something connected to it as the source of the issue.

No Ground Fault/Short Circuit Found

This eliminates the most obvious causes, but doesn't rule out small leakage currents or transient problems.


New Control Gear

Even new components can be faulty or incorrectly configured.

Possible Causes
1. Capacitive Discharge from VFD



Explanation

VFDs have large capacitors for smoothing DC voltage. When the isolator is turned off, these capacitors discharge quickly. This discharge current, even though brief, can be large enough to trip the breaker, especially if it's a sensitive B-curve.


Why E-Stop Works

When you use the E-Stop, the VFD's internal soft-stop function or control logic might partially discharge the capacitors before the contactor opens the circuit entirely. This reduces the discharge current when the isolator is switched off.

Possible Solutions



Bleed Resistor

Some VFDs have built-in bleed resistors. Verify that these are functioning correctly. If not, or if the VFD doesn't have one, consider adding an external bleed resistor across the DC bus capacitors. This will slowly discharge the capacitors when power is removed.

Consult the VFD manual for the correct resistor value and power rating.
DC Bus Choke

If applicable, a DC bus choke (inductor) in the VFD can help to reduce the inrush current and potential for tripping. Again, refer to the manual.


Pre-Charge Circuit

More complex, but a pre-charge circuit can limit the inrush current to the VFD capacitors when power is applied. Not a typical solution for this issue.2.

Neutral Current Imbalance



Explanation

Even with a balanced three-phase load, there can be some imbalance. Turning off the isolator might momentarily interrupt one phase slightly before the others, creating a surge of current in the neutral.


Possible Solutions



Check Wiring

Carefully re-examine the neutral wiring. Make sure it's adequately sized and properly connected throughout the cabinet and to the supply. Loose connections can exacerbate imbalances.


Consider RCD/RCBO

While you've ruled out a direct ground fault, a small leakage current to ground can contribute to the problem, especially in conjunction with an imbalance. Consider replacing the breaker with an RCBO (Residual Current Breaker with Overcurrent protection) with a low mA tripping current (e.g., 30mA). Important: This is a test and might not be a permanent solution. RCBOs can be nuisance tripped by VFDs.



Power Quality Analyzer

A power quality analyzer can provide detailed information about voltage and current imbalances, harmonics, and other factors that could be contributing to the problem.3.

Inrush Current from Other Components



Explanation

While you mention the motor isn't running, other components like the Logo8 PLC, contactors, or other small power supplies could have inrush currents when power is suddenly removed.

Possible Solutions



Staggered Shutdown (If Possible)

If the control system allows, program the Logo8 to shut down non-essential components before the main contactor is opened.

Inrush Current Limiters

Consider adding inrush current limiters (thermistors or inductors) in series with the power supplies of the Logo8 and other components.4.

Faulty Breaker (Less Likely, But Possible)



Explanation

The breaker itself could be overly sensitive or have a manufacturing defect.

Possible Solutions



Test with Another Breaker

Temporarily (and safely) try a different, known-good 16A B-curve breaker of the same type (Hager ADM420c B20). Important: Only do this if you are qualified and comfortable working with electrical circuits.5.

Harmonics from the VFD



Explanation

VFDs generate harmonics that can distort the current waveform. These harmonics can increase the RMS current and potentially trip the breaker.


Possible Solutions



Line Reactor

Install a line reactor (also called an input choke) on the input side of the VFD. This can reduce harmonics and improve power factor.


EMC Filter

Ensure the VFD has a properly installed EMC filter.

Troubleshooting Steps1.

Double-Check VFD Manual

Absolutely essential. The manual will provide specific information about capacitor discharge characteristics, bleed resistors, recommended line reactors, and EMC filtering.2.

Monitor DC Bus Voltage

If possible, use a multimeter to monitor the DC bus voltage of the VFD immediately after turning off the isolator. See how quickly it discharges. This will help confirm if the capacitors are the primary issue.3.

Isolate Components



Disconnect the Motor

Disconnect the motor from the VFD output. Turn off the isolator and see if the breaker still trips. If it doesn't, the motor or the wiring to the motor
could be contributing.

Disconnect Non-Essential Loads

Disconnect the Logo8 PLC and any other small power supplies. See if the tripping stops.4.

Power Quality Analysis

As mentioned above, a power quality analyzer is the best way to diagnose complex power issues. Rent one or hire an electrician with one.5.

Wiring Integrity

Although you checked for shorts, visually inspect all wiring for damage, especially near terminations. Check for loose connections, corrosion, or insulation breakdown.6.

Test with a Different Breaker

Safely try a different, known-good 16A B-curve breaker.

Safety Precautions

Work De-Energized

Whenever possible, work on the control panel with the power off and locked out.


Qualified Personnel

Only qualified electricians should perform electrical testing and repairs.

Follow Electrical Codes

Adhere to all applicable electrical codes and safety regulations.


Capacitor Discharge

Be aware of the danger of high-voltage capacitors in the VFD. Ensure they are properly discharged before working on the unit.

In Summary:The most likely cause is capacitive discharge from the VFD. Start by checking the VFD manual, monitoring the DC bus voltage, and verifying the bleed resistor. If those don't solve the problem, systematically isolate components and consider the other possibilities listed above. A power quality analyzer can be invaluable for pinpointing the root cause. Flag for review