Question: Hi All,Recommissioning an old Control Cabinet and retrofitted it with some new control gear. I'm looking to put it back into use, however when i turn off the isolator on the Control Panel, it trips the 16A Breaker for the Socket its plugged into.Checked for Ground Faults and Short-circuits, everything seems to be fine. Isolator is 4 Pole (3Ph + N), Plug wiring looks good.Cabinet has a Siemens Simanics V20 VFD and Logo8 Controls, motor isnt running when powered down so there shouldn't be any inductive kickback. However when I E-Stop the machine before turning off the isolator, which in turn cuts power to the VFD via the branch contactor, the breaker doesn't trip.Trip Switch is a Hager ADM420c B20.Any suggestions?Thanks.
This is a tricky problem, but here's a breakdown of potential causes and troubleshooting steps, based on your observations
Understanding the Problem
Breaker Tripping on Isolator Off
This is the key symptom. It suggests a sudden change in current when the circuit is opened. This is often indicative of capacitive discharge or a current imbalance.
No Tripping on E-Stop
This is a crucial clue. The E-Stop, by cutting power to the VFD via the contactor, seems to prevent the problem. This strongly points to the VFD or something connected to it as the source of the issue.
No Ground Fault/Short Circuit Found
This eliminates the most obvious causes, but doesn't rule out small leakage currents or transient problems.
New Control Gear
Even new components can be faulty or incorrectly configured.
Possible Causes1. Capacitive Discharge from VFD
Explanation
VFDs have large capacitors for smoothing DC voltage. When the isolator is turned off, these capacitors discharge quickly. This discharge current, even though brief, can be large enough to trip the breaker, especially if it's a sensitive B-curve.
Why E-Stop Works
When you use the E-Stop, the VFD's internal soft-stop function or control logic might partially discharge the capacitors before the contactor opens the circuit entirely. This reduces the discharge current when the isolator is switched off.
Possible Solutions
Bleed Resistor
Some VFDs have built-in bleed resistors. Verify that these are functioning correctly. If not, or if the VFD doesn't have one, consider adding an external bleed resistor across the DC bus capacitors. This will slowly discharge the capacitors when power is removed.
Consult the VFD manual for the correct resistor value and power rating. DC Bus Choke
If applicable, a DC bus choke (inductor) in the VFD can help to reduce the inrush current and potential for tripping. Again, refer to the manual.
Pre-Charge Circuit
More complex, but a pre-charge circuit can limit the inrush current to the VFD capacitors when power is applied. Not a typical solution for this issue.2.
Neutral Current Imbalance
Explanation
Even with a balanced three-phase load, there can be some imbalance. Turning off the isolator might momentarily interrupt one phase slightly before the others, creating a surge of current in the neutral.
Possible Solutions
Check Wiring
Carefully re-examine the neutral wiring. Make sure it's adequately sized and properly connected throughout the cabinet and to the supply. Loose connections can exacerbate imbalances.
Consider RCD/RCBO
While you've ruled out a direct ground fault, a small leakage current to ground can contribute to the problem, especially in conjunction with an imbalance. Consider replacing the breaker with an RCBO (Residual Current Breaker with Overcurrent protection) with a low mA tripping current (e.g., 30mA). Important: This is a test and might not be a permanent solution. RCBOs can be nuisance tripped by VFDs.
Power Quality Analyzer
A power quality analyzer can provide detailed information about voltage and current imbalances, harmonics, and other factors that could be contributing to the problem.3.
Inrush Current from Other Components
Explanation
While you mention the motor isn't running, other components like the Logo8 PLC, contactors, or other small power supplies could have inrush currents when power is suddenly removed.
Possible Solutions
Staggered Shutdown (If Possible)
If the control system allows, program the Logo8 to shut down non-essential components before the main contactor is opened.
Inrush Current Limiters
Consider adding inrush current limiters (thermistors or inductors) in series with the power supplies of the Logo8 and other components.4.
Faulty Breaker (Less Likely, But Possible)
Explanation
The breaker itself could be overly sensitive or have a manufacturing defect.
Possible Solutions
Test with Another Breaker
Temporarily (and safely) try a different, known-good 16A B-curve breaker of the same type (Hager ADM420c B20). Important: Only do this if you are qualified and comfortable working with electrical circuits.5.
Harmonics from the VFD
Explanation
VFDs generate harmonics that can distort the current waveform. These harmonics can increase the RMS current and potentially trip the breaker.
Possible Solutions
Line Reactor
Install a line reactor (also called an input choke) on the input side of the VFD. This can reduce harmonics and improve power factor.
EMC Filter
Ensure the VFD has a properly installed EMC filter.
Troubleshooting Steps1.
Double-Check VFD Manual
Absolutely essential. The manual will provide specific information about capacitor discharge characteristics, bleed resistors, recommended line reactors, and EMC filtering.2.
Monitor DC Bus Voltage
If possible, use a multimeter to monitor the DC bus voltage of the VFD immediately after turning off the isolator. See how quickly it discharges. This will help confirm if the capacitors are the primary issue.3.
Isolate Components
Disconnect the Motor
Disconnect the motor from the VFD output. Turn off the isolator and see if the breaker still trips. If it doesn't, the motor or the wiring to the motor could be contributing.
Disconnect Non-Essential Loads
Disconnect the Logo8 PLC and any other small power supplies. See if the tripping stops.4.
Power Quality Analysis
As mentioned above, a power quality analyzer is the best way to diagnose complex power issues. Rent one or hire an electrician with one.5.
Wiring Integrity
Although you checked for shorts, visually inspect all wiring for damage, especially near terminations. Check for loose connections, corrosion, or insulation breakdown.6.
Test with a Different Breaker
Safely try a different, known-good 16A B-curve breaker.
Safety Precautions
Work De-Energized
Whenever possible, work on the control panel with the power off and locked out.
Qualified Personnel
Only qualified electricians should perform electrical testing and repairs.
Follow Electrical Codes
Adhere to all applicable electrical codes and safety regulations.
Capacitor Discharge
Be aware of the danger of high-voltage capacitors in the VFD. Ensure they are properly discharged before working on the unit.
In Summary:The most likely cause is capacitive discharge from the VFD. Start by checking the VFD manual, monitoring the DC bus voltage, and verifying the bleed resistor. If those don't solve the problem, systematically isolate components and consider the other possibilities listed above. A power quality analyzer can be invaluable for pinpointing the root cause. Flag for review