Topic: Is this tap legal?

User: Tainted, Location: New York

Asked on: Tuesday, September 17, 2024 at 9:02 am EDT
Answered on: Thursday, March 6, 2025 at 2:33 am EST

Question: There are 3 phases that feed the bus bars of a panel as shown in picture below. The left and middle phases are tapped. The right phase is not tapped.Is there anything in the code that prevents us from tapping this bus? I've heard that it might be illegal because it can cause unbalance of the feeders.

You're right to be concerned about the potential imbalance. While there's no explicit code section in the NEC (National Electrical Code) that directly forbids tapping only two of three phases on a busbar, the implications of doing so are heavily addressed and strongly discouraged due to the potential for creating an unbalanced load. This is because there are several factors to consider.Here's a breakdown of the code sections and principles that are relevant: NEC 220.10: General. Branch-circuit, feeder, and service calculations shall include the rating of the voltage, current, and frequency specified on the equipment nameplate. This is the overarching principle: all calculations and installations must consider the equipment's design. Loading only two phases heavily while leaving one lightly loaded can stress the distribution system and the equipment connected to it. NEC 220.42: General Lighting. The unit loads specified in Table 220.42 shall be considered as minimum requirements and shall apply to occupancies specified therein. The NEC requires you to calculate the expected load and ensure the feeder and service are adequately sized to handle it. An unbalanced load can distort the voltage and current waveforms. NEC 220.61: Feeder or Service Neutral Load. The feeder or service neutral load shall be the maximum unbalanced load as determined by this section. This section addresses neutral conductors and how to calculate their load. Unbalanced loads directly impact the neutral conductor, potentially overloading it. NEC 310.15: Ampacity of Conductors. Conductor ampacity must be appropriate for the load, and this includes considering the load balance. Uneven loading can lead to overheating and potential failure.

Why tapping only two phases is generally bad practice


Voltage Imbalance

Uneven loading causes different voltage drops on each phase. This voltage imbalance can damage sensitive equipment, reduce motor efficiency, and cause overheating.2.

Current Imbalance

This leads to higher currents on the loaded phases, potentially exceeding their ampacity or the rating of the busbars themselves.3.

Neutral Overload

In a wye-connected system, the unbalanced load creates a current flow in the neutral conductor. This can overload the neutral, leading to voltage distortion and potential fire hazard.4.

Transformer Overheating

The supply transformer is designed for balanced loads. An unbalanced load can cause overheating in the transformer windings.5.

Power Quality Issues

Voltage and current imbalances degrade power quality, affecting all equipment connected to the system.

How to Address the Issue


Load Balancing

Distribute the load as evenly as possible across all three phases. This is the preferred solution. Rearrange the connections to better distribute the load.2.

Engineering Analysis

Perform a thorough load analysis to determine the actual load on each phase. This will help determine if the existing service and feeders can handle the unbalanced load.3.

Upgrading the Service

If the existing service and feeders are not adequate, you may need to upgrade them to handle the increased load and potential imbalance.4.

Delta-Wye Transformer

Consider using a delta-wye transformer to mitigate the impact of the unbalanced load on the utility grid.5.

Specialized Equipment

Some equipment is designed to handle unbalanced loads. If the load is critical, consider using such equipment.

In Conclusion:


While there isn't a direct "Thou shalt not tap only two phases" rule in the NEC, the implications and requirements related to load calculations, conductor ampacity, voltage balance, and neutral loading effectively make it a highly discouraged and potentially code-violating practice if not addressed properly. A licensed electrical engineer or qualified electrician should perform a load analysis and determine the best course of action to ensure a safe and compliant installation.Before making any changes, consult with a qualified electrical engineer or licensed electrician to evaluate the situation and ensure compliance with all applicable codes and standards. They can perform load calculations, assess the capacity of the existing equipment, and recommend the best solution for your specific situation. This is crucial for ensuring the safety and reliability of the electrical system. Flag for review