User: darunedefig, Location: HV, New York
Asked on: Tuesday, September 17, 2024 at 2:34 pm EDT
Answered on: Thursday, March 6, 2025 at 2:34 am EST
Question: Trenched AC wires run from a detached shed/garage/ground mount with solar to a house.Normally before I penetrate a house I would place an AC disconnect on the exterior wall of the house.Following NEC 2017,"225.32 Location. The disconnecting means shall be installedeither inside or outside of the building or structure served orwhere the conductors pass through the building or structure.The disconnecting means shall be at a readily accessible locationnearest the point of entrance of the conductors. For thepurposes of this section, the requirements in 230.6 shall beutilized."I have this one job where the customer is wanting us to penetrate the basement from the trench, run conduit across basement,then penetrate back out to exterior wall, and then place a rapid shutdown disconnect next to the utility meter.Normally I would be installing two disconnects, with one near utility meter and another disconnect prior to the wires from the solar array entering the building.Looking at this forum most of the posts that I saw concerning this are prior to rapid shutdown and prior to 2017.In NEC 2017,2020,or 2023, is there anything in the code that only requires the rapid shutdown device where 225.32 does not apply?Can I get away with the one disconnect by the utility meter?
You're dealing with a tricky situation where multiple codes are interacting. Let's break it down
Understanding the Requirements
225.32 (Disconnecting Means - Other Structures)
This section generally mandates a readily accessible disconnecting means nearest the point of entrance where conductors supply a building or structure from another structure (your shed/garage/ground mount). This is your primary concern.
230.6 (Underground Conductors)
This section, referenced by 225.32, deals with the physical protection and installation of underground conductors. It doesn't change the location requirement for the disconnect.
Rapid Shutdown (RSD)
While not directly impacting 225.32, RSD requirements (690.12 and potentially state/local amendments) influence the location and type of disconnects used, especially in solar PV systems. RSD is a safety requirement, 225.32 is a convenience/safety requirement.
The Problem with Your Customer's Request
Your customer's proposed installation of penetrating the basement, running conduit, and then exiting to the exterior wall significantly violates 225.32. The disconnect is not "nearest the point of entrance." It's adding unnecessary length and complication to the circuit inside the building before the disconnect is reached.
Analysis of the Code and Your Question "Is there anything in the code that only requires the rapid shutdown device where 225.32 does not apply?" No. The RSD requirements and 225.32 are independent requirements. RSD is in addition to, not instead of, 225.32. Think of them as separate layers of safety. One is for personnel working on the solar panels, and the other is for the fire department. "Can I get away with the one disconnect by the utility meter?" Almost certainly not, because it violates the “nearest the point of entrance” requirement of 225.32.
Why Your "Normal" Practice is Correct
Your instinct to install two disconnects is generally correct in this scenario for several reasons:1. Compliance with 225.32
A disconnect before or immediately after entering the house is required by 225.32.
2.
Ease of Maintenance/Emergency
Having a disconnect close to the point of entry allows for easy isolation of the circuit before it enters the house in case of problems or emergencies.3.
RSD Requirements
The second disconnect, placed near the meter/inverter on the exterior, may need to be a Rapid Shutdown device to comply with 690.12 and local amendments. It's often convenient to combine this with the required disconnect from 225.
32.
What to Do1. Educate the Customer
Clearly explain why their proposed installation violates code and introduces unnecessary risks and inefficiencies. Emphasize the importance of having a disconnect at the point of entry for safety and ease of maintenance.2.
Propose an Alternative That Complies
Suggest an installation that places a disconnect (potentially an RSD disconnect) on the exterior wall, nearest to where the conduit enters the basement. The conduit run in the basement is acceptable after* the disconnect.3.
Consult with the AHJ
Before starting any work, discuss the proposed solution with the local Authority Having Jurisdiction (AHJ). They have the final say and can provide clarification on specific interpretations of the code in your area.
In Summary
You cannot bypass the requirements of 225.32 simply because you're installing a Rapid Shutdown system. The "nearest the point of entrance" requirement is critical for safety and code compliance. Stick to your standard practice of installing a disconnect at the point of entry and another near the inverter/meter, ensuring compliance with RSD requirements. Your customer's suggestion is not compliant with NEC 2017, 2020, or 2023. Flag for review